Assuming that you have Tracer Summit... you can add or replace a Lontalk (COMM5) device.
The best thing to do is go through the procedure in the manual Every Tracer Summit installation includes a PDF copy of their programming manual. This is about 800 pages and can be found by going to:
C:\Program Files|Tracer Summit|Docs
You want the Programming book and look on page 107... here is a snippet from the manual...
Adding a New UCM to an Existing Comm5 Link (BMTX or High Capacity BMTW)
To add a new UCM to an existing Comm5 link:
1. Start your installation at the new UCM. Configure and verify operation
of the new device in stand-alone mode, without the communication
link connected, using the Rover service tool.
If this device was previously installed, push the service pin for 15 seconds
until the red service LED flashes.
2. Connect the UCM to the communication link on the BCU. Move termination
resistors, if necessary.
3. At the PC workstation select Setup from the Tracer Summit main
menu and open Site Configuration.
4. From the Devices tab, click the Create UCM button. Then follow the
procedure for “Creating Comm5 UCMs Objects for BMTX or High
Capacity BMTW” on page 95. If you created the UCMs during the initial
installation, you can skip this step.
5. On the Devices tab, click the Assign Neuron ID button to open the
Assign Neuron ID dialog box.
When the Assign Neuron ID dialog box opens, all command buttons
are unavailable while the PC workstation determines whether
Comm5 activity is occurring in the BCU. When there is Comm5 activ-
Note:
Do not begin working on the link with the Rover service tool
until you have verified that all devices are communicating with
the BCU.
Note:
When you add a device to an existing link, you will not be able
to preserve bindings between any of the new devices that are
added. You will, however, be able to preserve existing bindings.
If additional bindings are required, create them using the
Rover service tool or Rover in Tracer Summit software, after
the device has been added. Then remove the Rover service tool
from the link and follow this procedure.
Note:
Unassigned UCMs show up in the UCMs list on the Devices
tab with the default name and no Neuron ID assigned.
Comm5 Links
108 BMTX-SVP01B-EN
ity, a progress bar displays in the Comm5 Status group in the upper
right-hand corner of the dialog box. When all activity ends, the command
buttons are available again.
6. Click the Discover Neuron IDs button. In this phase of discovery, the
BCU discovers devices on the link and builds a list that appears in
the Neuron IDs Unassigned to UCM Objects. Confirmation that the
BCU found devices also appears in the Comm5 Object and Neuron ID
Summary on the left side of the dialog box.
7. From the UCM Type drop-down list in the Assign Neuron ID dialog
box, select the appropriate UCM type.
8. From the Unassigned UCM Object Name drop-down list, select an
Unassigned UCM Object Name to give an unassigned Neuron ID to.
9. If you do not want to use the Neuron ID location label as the UCM
object name, clear the Assign Location Label checkbox.
10. In the Neuron IDs Unassigned to UCM Objects list, select the Neuron
ID that you want associated with the UCM object displayed in the
Unassigned UCM Object Name field.
11. Click the Assign button to give the Neuron ID to the unassigned UCM
object and move it to the Neuron ID Assigned to UCM Objects list
12. Repeat the process if there are more UCM objects to assign.
13. Click OK to return to the Devices tab. Notice that the UCM objects in
Selected Device list now have Neuron IDs assigned to them.
14. Click Save and close Site Configuration.
You can see communication established with your newly installed
devices by looking at the UCM editors. (If power is lost to the BCU
before communication is established, the devices will have to be reinstalled.)
Adding New UCMs to an Existing Comm5 Link (Standard Capacity BMTW)
1. Start your installation at the new Comm5 device. Configure and verify
operation of the new device in stand-alone mode, without the communication
3. When you have completed the installation of the new units on the
link, push the service pin on all of the units. This broadcasts the Neuron
ID of the new devices on the link. The BCU will discover only the
Note:
the BCU.