Hi everyboby!! My very first post
According to the Copeland manuals available to me, the net oil pressure ( pump discharge pressure minus suction pressure) must be not less than 9 psi for an effective compressor lubrication. On new compressors, I remember watching the pump discharge pressure go up to 50 - 60 psi (low temp systems), with suction pressures 20´s and below.
As the oil was getting kinda dirty in the sight glass, I changed oil and cleaned up the screen mesh and pump in this low temp compressor. Now, as I put the pump back in service, I read pump discharge pressures in the 30´s with suction pressures in the 10´s. That means about 20 psi of net oil pressure (well above the 9 psi recommended value). Even so, the PENN 545 electronic oil pressure controls keeps shutting down the system. This didn´t happen before I serviced the pump. What´s wrong here?
According to the Copeland manuals available to me, the net oil pressure ( pump discharge pressure minus suction pressure) must be not less than 9 psi for an effective compressor lubrication. On new compressors, I remember watching the pump discharge pressure go up to 50 - 60 psi (low temp systems), with suction pressures 20´s and below.
As the oil was getting kinda dirty in the sight glass, I changed oil and cleaned up the screen mesh and pump in this low temp compressor. Now, as I put the pump back in service, I read pump discharge pressures in the 30´s with suction pressures in the 10´s. That means about 20 psi of net oil pressure (well above the 9 psi recommended value). Even so, the PENN 545 electronic oil pressure controls keeps shutting down the system. This didn´t happen before I serviced the pump. What´s wrong here?