    Well pump banging pipes on start-up

    Hello. I have a 3-year old building, geo-thermal. Climate-Master heat pumps; 6" well-water extraction and injection wells; plate heat exchangers; and 25% P.G. load side. The problem is occasionally when the well pump starts up, it slams the source piping. The pump motor is on a Q9 drive for soft start. I have decreased the acceleration time from 2 sec. to 15 sec. The drive maxes at 50HZ. and I have good flow through the plate heat exchangers at that outout. This adjustment seemed to help as the noise isn't quite as noticeable now but is still there. There is a Taco sand separator in line with the well water supply ahead of the HX's. Blew it down yesterday. One observation I noted--there is a 6" Watts 774 double check valve in-line where the well supply enters the building, lower floor. My observation was that it is installed vertical flow down. The install instructions say it can be installed horizontal or vertical flow up. The plate HX's are located on the second floor. I want to say that the 774 checks are holding in the off-cycle as I isolated the well off water from the HX's on the second floor and opened a 2" ball valve on the bottom of the separator--no vacuum. Normally, if you were to open that 2" ball valve, there is one heck of a vacuum. So, am I dealing with an air issue here? Should the 774 be positioned properly? I hate to do the latter and then still have the problem. This is an intermittent problem, btw. Any input would be greatly appreciated. Thanks. Oh and I'm in Iowa. Cheers!

  2. #2
    Join Date
    May 2014
    Location
    Bay Area California
    Posts
    43,452
    Post Likes
    Regardless if it is part of the problem or not, that double check should be mounted properly. Or it is potentially not even in the circuit.

    Another option, possibly cheaper depending on your site conditions, is to leave the plumbing pretty much the same but install a double check that is rated for vertical flow down. You would just need to be sure your system can handle that, as there is usually a greater pressure drop across those.

  3. #3
    Join Date
    Aug 2010
    Posts
    4,338
    Post Likes
    You ever seen the video on how to break a bottle by tapping with your hand? Same thing could be happening as the vacuum that builds up collapses. Perhaps you need a vacuum arrester.
    http://www.siouxchief.com/docs/defau...eer-report.pdf

  4. #4
    Join Date
    Apr 2003
    Location
    St. Louis
    Posts
    1,269
    Post Likes
    Did you figger the problem out?

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •