Thread: Siemens PXCM rev 2.8.6

  1. #1
    Join Date
    Nov 2011
    Posts
    9
    Post Likes

    Siemens PXCM rev 2.8.6

    Hello,
    Had a Siemens PXCM V2.8.2 that took a bath and is no longer operational. It is connected to Insight 3.9.1 on a P2 network with a VAEM. Installed new PXCM V2.8.6 that is licensed for VAEM. I have input all of the same settings as the original and it will not connect with Insight. I can ping it from Insight and when I hyperterminal directly into it and run a fieldpanel log it says that Insight is online but disconnected. Does anyone know if this is a rev level issue? If not, any ideas? Thanks

  2. #2
    Join Date
    Mar 2008
    Location
    Indy
    Posts
    378
    Post Likes
    Check the settings. Don't remember the specifics but IIRC it has something to do with the USB port being the factory default and not the VAEM.

  3. #3
    Join Date
    Aug 2013
    Location
    Halifax, Nova Scotia, Canada
    Posts
    32
    Post Likes
    with that version of insight, you probably need to update you firmwarerev.xml file in insight.

  4. #4
    Join Date
    Oct 2007
    Location
    Arizona DUH
    Posts
    174
    Post Likes
    Did you hand type the license? If so make sure its accurate. It is case sensitive.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Tags for this Thread

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •