    Old Copper Water Supply as Grounding Rod for Residence

    Hi,
    I have older Residential system that is grounded to a 1" copper water line (in addition to the Neutral Service wire) Obviosly before "Bonding". Line passes through about 20' of clay, 2 feet below surface. Copper line no longer connects to water main, so is it essentially a large grounding rod run horizontally. Water table is such that the clay is at least moist if not wet. Has been in place for 50 years now.

    Since it is now disconnected from the county water supply, is it providing enough of a ground for a residence? If not, I presume I need to add new thicker grounding rods 10 feet apart, etc?

    While we have a transformer on the supply pole we are connected to, there does not appear to be a separate copper ground wire down the pole.

    Obviously, installing two ground rods through 10' of clay to build new ground system is no small job. Possible, but royal pain.

    Is the old copper water pipe going to handle a lightning strike to the transformer/pole area?

    Please advise. Thanks!

  2. #2
    Join Date
    Jun 2013
    Posts
    67
    Post Likes
    If in doubt , install a ground rod .

    God bless
    Wyr

  3. #3
    Join Date
    Jul 2014
    Posts
    6
    Post Likes
    While your cold water bond is a sufficient source of ground, NEC 250.53 A 2 requires a supplemental grounding electrode. Hence you need to install a ground rod or other electrode permitted by the NEC article stated above. A ground plate may better suit your needs than a rod electode

  4. Likes DavidDeBord liked this post.
  5. #4
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    21,021
    Post Likes
    I use my hitachi hamerdrill to drive ground rods, it makes light work of it.

  6. #5
    Join Date
    Oct 2014
    Location
    Central Kentucky
    Posts
    32
    Post Likes
    X2 to jtrammel. You can actually buy ground rod driver adapters to chuck in a hammer drill, but they are a little pricey if you only have one or two to do.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •