    5-2-1 hard start kit problem

    Took a look at my relative's 4 ton spit, cool only system (R22 about 8 years old). It's working fine, I was just giving it a once over for them. Someone installed a two wire Kickstart hard start kit at some point, maybe from the initial install. From reading here, it seems most prefer the the 3 wire 5-2-1 kit. So I decided to swap out the Kickstart with a 5-2-1 (new and proper size). Not only did the compressor not start with it, but the the 5-2-1 capacitor got pretty warm (almost hot). I triple checked the wiring (hard to mess up) and it was correct. So I put the Kickstart back in and all is well again. Any ideas on why the 5-2-1 did that? It's raining now, so any further tests will have to wait.

    Note: I did not take any current readings, nor did I try it without any hard start. Since everything had been working fine, I did not see the need. BTW, I replaced the dual run cap last year along with a new contactor (just due to age), so those are fairly new.
    Quick reply to this message Reply  

  2. #2
    Join Date
    May 2010
    Location
    Oxford, UK
    Posts
    346
    Post Likes
    The fact the compressor started ok once the two wire was refitted makes it less likely to be the problem. Most likely is you wired it wrong, then it could be the 5-2-1 is fubar.

    Start caps will get hot, and eventually explode if kept in circuit, either due to miss-wiring, faulty relay, compressor, or voltage problems. Never stand in line with the terminals when they are powered up.
    Quick reply to this message Reply  

  3. #3
    Join Date
    Oct 2013
    Location
    Texas
    Posts
    48
    Post Likes
    Thread Starter
    Quote Originally Posted by monkeyspanners View Post
    Most likely is you wired it wrong, then it could be the 5-2-1 is fubar.
    It's pretty hard to wire it wrong, and I did triple check it.

    The 5-2-1 cap seems to be ok, but the relay could be bad I suppose.
    Quick reply to this message Reply  

  4. #4
    Join Date
    May 2013
    Location
    Rogersville, Tennessee
    Posts
    76
    Post Likes
    Quote Originally Posted by mark_a_l View Post
    It's pretty hard to wire it wrong, and I did triple check it.

    The 5-2-1 cap seems to be ok, but the relay could be bad I suppose.
    5 = CAN = COMMON
    2 = SHE = START
    1 = RUN = RUN
    A GOOD WAY TO REMEMBER
    Quick reply to this message Reply  

  5. #5
    Join Date
    Feb 2009
    Location
    Tallahassee, FL
    Posts
    6,217
    Post Likes
    How did you mount the relay
    Quick reply to this message Reply  

  6. #6
    Join Date
    Oct 2013
    Location
    Texas
    Posts
    48
    Post Likes
    Thread Starter
    Quote Originally Posted by SBKold View Post
    How did you mount the relay
    Upright (mounting hole up) as it was supposed to be.
    Quick reply to this message Reply  

  7. #7
    Join Date
    Nov 2007
    Location
    Tucson, AZ
    Posts
    265
    Post Likes
    was it sideways and the unit was supposed to be up? if the relay is not mounted correctly it can do this.
    Quick reply to this message Reply  

  8. #8
    Join Date
    Oct 2013
    Location
    Texas
    Posts
    48
    Post Likes
    Thread Starter
    Quote Originally Posted by N2fords View Post
    was it sideways and the unit was supposed to be up? if the relay is not mounted correctly it can do this.
    Nope, as noted above it was mounted properly. However, due to space limitations, the old Kickstart relay was mounted at a 45 degree angle, so I moved this one over a bit, but then it was only about an inch directly above the contactor. Is there a minimum distance from that, so that the contactor's magnetic field does not interfere? I've never read anything that cautions against that. <grasping at straws here>
    Quick reply to this message Reply  

  9. #9
    Join Date
    Oct 2010
    Location
    Anderson, South Carolina, United States
    Posts
    21,021
    Post Likes
    It was either wired wrong or a bad start cap out of the box.
    Heating/Cooling Services Inc.
    www.heatingandcoolingservicesinc.com
    Quick reply to this message Reply  

  10. #10
    Join Date
    Oct 2013
    Location
    Texas
    Posts
    48
    Post Likes
    Thread Starter
    Quote Originally Posted by jtrammel View Post
    It was either wired wrong or a bad start cap out of the box.
    Well, it definitely was not wired wrong. Only 3 wires and pretty idiot proof.
    I even made sure they didn't have the wrong wires on the wrong relay terminals before I even started.
    Quick reply to this message Reply  

  11. #11
    Join Date
    Jul 2005
    Posts
    7,834
    Post Likes
    Quote Originally Posted by mark_a_l View Post
    Well, it definitely was not wired wrong. Only 3 wires and pretty idiot proof.
    I even made sure they didn't have the wrong wires on the wrong relay terminals before I even started.
    Only 3 wires, but easy to miswire. Seems to happen a lot judging by the number of threads just like this one.

    Name:  5-2-1 wiring diagram.PNG
Views: 12108
Size:  34.5 KB
    Quick reply to this message Reply  

  12. #12
    Join Date
    Jul 2007
    Location
    Virginia
    Posts
    19,249
    Post Likes
    Did you ohm out the relay?

    I have had a couple 5-2-1 relays that the resistance between 1 and 2 was very high (kΩ-mΩ) right out of the packaging, because of a film on the contacts within the relay.

    After opening up the relay and cleaning the contacts the resistance went back to zero.
    Instead of learning the tricks of the trade, learn the trade.
    Quick reply to this message Reply  

  13. #13
    Join Date
    Oct 2013
    Location
    Texas
    Posts
    48
    Post Likes
    Thread Starter
    Quote Originally Posted by hvacrmedic View Post
    Only 3 wires, but easy to miswire. Seems to happen a lot judging by the number of threads just like this one.
    Oh, I have been known to connect things wrong before. But the very first thing I did when it did not work was triple check (more like 4 or 5 times).


    Quote Originally Posted by rundawg View Post
    Did you ohm out the relay?
    Yep. 1-2 zero ohms. 2-5 10.5K I even checked the black wire end to end as it would not be the first time I saw a connector crimped onto insulation.

    Oh well, like they say - if it aint broke....
    I'll leave what has been working in there, and mess with this 5-2-1 another day.
    Quick reply to this message Reply  

  14. #14
    Join Date
    Jul 2005
    Posts
    7,834
    Post Likes
    Quote Originally Posted by mark_a_l View Post
    Oh, I have been known to connect things wrong before. But the very first thing I did when it did not work was triple check (more like 4 or 5 times).




    Yep. 1-2 zero ohms. 2-5 10.5K I even checked the black wire end to end as it would not be the first time I saw a connector crimped onto insulation.

    Oh well, like they say - if it aint broke....
    I'll leave what has been working in there, and mess with this 5-2-1 another day.
    Maybe they're just junk? There have been several similar accounts posted.

    I use these.
    http://www.rectorseal.com/index.php/...start-compress

    FWIW these are OEM in some Carrier units. Unlike the 5-2-1 type that senses start winding voltage rise, the two-wire Kickstarts sense run capacitor voltage rise. Copeland approves this method in some of their bulletins. I haven't witnessed a single failure of the Kickstart two-wire kits. It's the only one I'll install.
    Quick reply to this message Reply  

  15. #15
    Join Date
    Dec 2012
    Location
    columbus, OH
    Posts
    7,049
    Post Likes
    Possibly not the right cutout voltage rating?
    Quick reply to this message Reply  

  16. #16
    Join Date
    Oct 2013
    Location
    Texas
    Posts
    48
    Post Likes
    Thread Starter
    Quote Originally Posted by hvacrmedic View Post
    Maybe they're just junk? There have been several similar accounts posted.
    You may be right. Funny, I only seemed to read good reviews here about them while browsing threads. But when I looked specifically for problems, I did indeed find those similar accounts.
    Quick reply to this message Reply  

  17. #17
    Join Date
    Aug 2012
    Location
    NE wisconsin
    Posts
    488
    Post Likes
    I saw a video where a tech showed the spike on an oscilloscope with a ptc, two wire kickstart, and a 521 start cap, each showed a boost when cold but only the 521 showed each and every time.

    There is definitely something wrong with the 521 kit you used, an 8 year old compressor should start just with the run capacitor. Did you check the mfd of it, I have seen capacitors at nearly zero still able to start with the kickstart, never seen that with a 521. Just my thoughts on it.
    Quick reply to this message Reply  

  18. #18
    Join Date
    Oct 2013
    Location
    Texas
    Posts
    48
    Post Likes
    Thread Starter
    Quote Originally Posted by philjafo View Post
    Did you check the mfd of it, I have seen capacitors at nearly zero still able to start with the kickstart, never seen that with a 521. Just my thoughts on it.
    As noted in my first post, I replaced the original cap last year. However I did not check it at the time because it was new and I assumed it was good when everything worked fine. I'll probably take another look at things this weekend.
    Quick reply to this message Reply  

  19. #19
    Join Date
    Aug 2012
    Location
    NE wisconsin
    Posts
    488
    Post Likes
    Name:  Warning-Made-in-China.jpg
Views: 2817
Size:  52.2 KB

    Not trying to be a smartas but just because a cap is new doesn't mean its good.
    Quick reply to this message Reply  

  20. #20
    Join Date
    Dec 2005
    Posts
    7,904
    Post Likes
    Quote Originally Posted by philjafo View Post
    Not trying to be a smartas but just because a cap is new doesn't mean its good.
    Yep, and if its made in China you'll be lucky to get even a year out of it.
    Quick reply to this message Reply  

Closed Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •