    Use some fiberglass batt..r20 or so because you cannot use the expanding foam for obv fire reasons.Just stuff it in the hole behind the plate that your exhaust pipe runs out.

  2. #22
    Join Date
    Aug 2004
    Location
    S.E. Pa
    Posts
    7,384
    Post Likes

    Exclamation

    Wester, you cannot pack insulation or anything else into stated clearances. That wall firestop assembly was tested with an air space. You pack it and you can burn a house down. I've investigated enough of them to know.

  3. #23
    Join Date
    Apr 2011
    Location
    Ontario
    Posts
    131
    Post Likes
    Sorry i didnt read the post 100 percent on the last install I did there was a 26ga steel box the venting went through before termination outside and we packed some extra space between that and the stud wall with insulation. Sounds like everyone here has suggested high temp silicone to seal it up.

  4. #24
    Join Date
    Aug 2004
    Location
    S.E. Pa
    Posts
    7,384
    Post Likes

    Cool

    You have to read the mfrs listed instructions. Some of these firestops cannot be caulked on the inside and must breathe. Sealing and packing these firestops can be a fire hazard. Each model's instructions is the code.

    HTH

  5. #25
    Join Date
    Jul 2011
    Location
    Toronto
    Posts
    5
    Post Likes
    Quote Originally Posted by Wester399 View Post
    Use some fiberglass batt..r20 or so because you cannot use the expanding foam for obv fire reasons.Just stuff it in the hole behind the plate that your exhaust pipe runs out.
    This is a good example of what not to do. The thimble is supposed to be an air gap for a reason, not an insulated space, regardless of the insulation used. A quick check of any manual (you know...those things that come with every piece of equipment but you've probably never read) or code book will tell you this. Insulating this space turns it into a fire hazard. Every time I installed a piece pf equipment that I had never seen before I always took the time to read the manual...it's always a good starting point for any proper installation.

  6. #26
    Join Date
    Apr 2017
    Location
    Canada, BC
    Posts
    12
    Post Likes
    Well I'm not sure about resurrecting post's from the dead, but here's a summary of a white paper duravent did on exactly this issue which disagrees with some of the prevalent wisdom here.

    https://mcusercontent.com/620b42dd9f...s_20201117.pdf

  7. #27
    Join Date
    Aug 2004
    Location
    S.E. Pa
    Posts
    7,384
    Post Likes
    Thanks for posting this. I will discuss it with the UL Standards Technical Panel and NFPA 211 technical cmte. In the meantime, note Duravent still covered themselves by pushing back to the ANSI Z21.88 listing agency. They claim minimal heat transfer. ANSI looks at overall temp rise and pyrolysis. This cavity would capture a lot of heat and has historically caused fires when packed with insulation. Note, they did not test assemblies that were properly caulked, nor did they address what operational cycles providing heat were needed to mitigate any attic condensation. They made a typo on the ASTM std for noncombustibles- it's E-136.