HVAC-Talk: Heating, Air & Refrigeration Discussion banner

York YT Dead on arrival

3.4K views 8 replies 5 participants last post by  toptech  
#1 ·
Model YTH1A1E2-CRJ
Comp Model YDTL-120
Serial# GHJM 200244

Control Enclosure
Panel#371-02264-105
Panel Diagram(which i dont have) 035-15994-000
Serial # 01079H800

This chiller is down. optiview screen dark. I just printed off the 160.55 M-1
manual.
I have no other documentation for this chiller/wiring diagrams etc.
The micro has a solid green LED lit.
I only have had to trouble shoot starter issues with this loud bugger.
Any experiences would be helpful
Thank you
 
Save
#2 ·
got power anywhere else?
 
Save
#3 ·
With no documentation I did a few things to get started.
Power supply outputs were 5vdc \12 vdc
I unplugged each input and output on the micro and tried to reboot. no success.
i have since printed off the optiview manual(160.55M-1)and scoured this site for more info.
I need to pay close attention to the actual power supply voltages.
I also need a wiring diagram for this panel.
with a green led im assuming the LCD should be lit up.
 
Save
#6 ·
Agree take it to the Pro Forum.
 
Save
#9 ·
turned out to be a bad J1 plug connection on the main board from the power supply.
used a tip cleaner plugged here back in and away she went.
cycled power off a dozen times, came back up without fail.
had the office order a new plug.
thanks to all
 
Save
You have insufficient privileges to reply here.