    Installed as close to the metering device to capture any debris that is from install or from west and tear. Also rust protection, replaced 4 just this past month with filter driers leaking due to rust.

  2. #42
    Join Date
    Mar 2015
    Location
    Medford, N.Y.
    Posts
    10,203
    Post Likes
    If the old system was r22 and had MO/AB oil and maybe had a slow burnout, then crap is everywhere in the system, like , in the LL, the evap coil, & the suction line. Then the new comp has POE, then the POE scrubs and cleans the 65' or 15" LL and ALL of that crap in the LL get introduced to the metering device. So tell me again ,where should the new C-303-HH or C-163-HH LLFD get installed? And the new SLFD catches the crap from the evap and SL. So, tell me again ,who does not use a SLFD? And the reason for NOT USING a SLFD? Oh the job was a "quoted price" job ,oh I see.

  3. Likes R600a liked this post.
  4. #43
    Join Date
    Jun 2022
    Location
    Central western Florida
    Posts
    39
    Post Likes
    Yes Coolwhip. Installing outside by the condenser is asking for them to rust and leak. In Florida sprinklers always seem to be by condenser. Water filter drier every day. With today’s refrigerant prices a leaking drier relocated to inside is a pricy job I’d rather install them in attic or garage and not have to face customer with a leak. Reclaim water is used as well here High in chlorine I’ve seen 4 year old driers rotted out

  5. #44
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    40,252
    Post Likes
    Quote Originally Posted by I know a little View Post
    Yes Coolwhip. Installing outside by the condenser is asking for them to rust and leak. In Florida sprinklers always seem to be by condenser. Water filter drier every day. With today’s refrigerant prices a leaking drier relocated to inside is a pricy job I’d rather install them in attic or garage and not have to face customer with a leak. Reclaim water is used as well here High in chlorine I’ve seen 4 year old driers rotted out
    So you’d rather go into that 140* attic to change it?

    If you paint them they won’t rust!

  6. Likes Red850kid liked this post.
  7. #45
    R600a's Avatar
    R600a is online now Professional Member*/Membership Committee
    Join Date
    Jul 2019
    Location
    Hanging out with the mice behind the fridge talking bad about the roaches in the oven.
    Posts
    22,221
    Post Likes
    Just needs a little paint.
    "Is this before or after you fired the parts cannon at it?" - senior tech
    I'm tired of these mediocre "semi flammable" refrigerants. If we're going to do it let's do it right.
    Unless we change direction we are likely to end up where we are going.
    "It's not new, it's better than new!" Maru.

  8. #46
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    40,252
    Post Likes
    Quote Originally Posted by R600a View Post
    Just needs a little paint.
    That’s what 7 - 10 years!

    Even in my salt air environment.

    BTW. Where’s the oil?

  9. Likes R600a liked this post.
  10. #47
    Join Date
    Jan 2010
    Posts
    33,472
    Post Likes
    He prefers latex 😃

  11. #48
    R600a's Avatar
    R600a is online now Professional Member*/Membership Committee
    Join Date
    Jul 2019
    Location
    Hanging out with the mice behind the fridge talking bad about the roaches in the oven.
    Posts
    22,221
    Post Likes
    Quote Originally Posted by pecmsg View Post
    That’s what 7 - 10 years!

    Even in my salt air environment.

    BTW. Where’s the oil?
    It wasn't leaking. It was 95% restricted. I expect it was well over 20 years old.
    "Is this before or after you fired the parts cannon at it?" - senior tech
    I'm tired of these mediocre "semi flammable" refrigerants. If we're going to do it let's do it right.
    Unless we change direction we are likely to end up where we are going.
    "It's not new, it's better than new!" Maru.

  12. #49
    Join Date
    Jan 2010
    Posts
    33,472
    Post Likes
    You sure it wasn't 94% 🤔

  13. #50
    R600a's Avatar
    R600a is online now Professional Member*/Membership Committee
    Join Date
    Jul 2019
    Location
    Hanging out with the mice behind the fridge talking bad about the roaches in the oven.
    Posts
    22,221
    Post Likes
    Quote Originally Posted by VTP99 View Post
    You sure it wasn't 94%
    Yep I measured with my puffometer I could tell it was 95% by how far my cheeks puffed out when I attempted to blow through it.
    "Is this before or after you fired the parts cannon at it?" - senior tech
    I'm tired of these mediocre "semi flammable" refrigerants. If we're going to do it let's do it right.
    Unless we change direction we are likely to end up where we are going.
    "It's not new, it's better than new!" Maru.

  14. Likes ksefan, doc havoc, jbhenergy liked this post.
  15. #51
    Join Date
    Jun 2022
    Location
    Central western Florida
    Posts
    39
    Post Likes
    Yes I’d rather go up in attic. Better than facing a customer with a big bill when you know there was a better way You better have some good paint to deal with the chlorine in reclaimed water. Replaced a rusted out muffler on a six year old unit today that was sprayed with reclaim from sprinkler. I’ll post a pic when I figure out how
    Attached Images Attached Images   

  16. #52
    Join Date
    Jun 2022
    Location
    Central western Florida
    Posts
    39
    Post Likes
    All right I guess I do know how. Drier was up in garage on this one Nice and clean

  17. #53
    Join Date
    Jun 2022
    Location
    Central western Florida
    Posts
    39
    Post Likes
    I have seen homeowners paint some kind of tar or undercoating on them and it seems to work but what a mess

  18. #54
    Join Date
    Jun 2019
    Posts
    1,398
    Post Likes
    Quote Originally Posted by hvacrmedic View Post
    A small pressure drop in the LL doesn't affect performance. Systems using POE oil REQUIRE a filter drier.
    so how comes that mini splits do not require one

  19. Likes R600a liked this post.
  20. #55
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    40,252
    Post Likes
    Quote Originally Posted by gustavhorna View Post
    so how comes that mini splits do not require one
    One job of the filter drier is to protect the X-Valve from debris. With minis the valve is located in the outdoor unit.

  21. #56
    Join Date
    Jan 2010
    Posts
    33,472
    Post Likes
    Also typically mini's are SAE connections so no brazing = no contamination 😉

  22. Likes R600a liked this post.
  23. #57
    R600a's Avatar
    R600a is online now Professional Member*/Membership Committee
    Join Date
    Jul 2019
    Location
    Hanging out with the mice behind the fridge talking bad about the roaches in the oven.
    Posts
    22,221
    Post Likes
    Quote Originally Posted by VTP99 View Post
    Also typically mini's are SAE connections so no brazing = no contamination
    Minis only get installed in a perfect world of course.
    "Is this before or after you fired the parts cannon at it?" - senior tech
    I'm tired of these mediocre "semi flammable" refrigerants. If we're going to do it let's do it right.
    Unless we change direction we are likely to end up where we are going.
    "It's not new, it's better than new!" Maru.

  24. #58
    Join Date
    Jan 2010
    Posts
    33,472
    Post Likes
    Yes by perfect tech's of course 😃

  25. Likes R600a liked this post.
  26. #59
    Join Date
    Jul 2005
    Posts
    7,278
    Post Likes
    Quote Originally Posted by gustavhorna View Post
    so how comes that mini splits do not require one
    Planned obsolescence.

  27. #60
    Join Date
    Jun 2019
    Posts
    1,398
    Post Likes
    Quote Originally Posted by pecmsg View Post
    One job of the filter drier is to protect the X-Valve from debris. With minis the valve is located in the outdoor unit.
    he was saying POE oil REQUIRES filter drier.... not what other functions it also has