    Quote Originally Posted by jbhenergy View Post
    Couple things.

    4. Your duct work works off pressure. Magically find a bigger motor to move more air and all your going to do is create more pressure in that duct. To the point where the blower won’t be able to move anything more because it is not strong enough to work against that pressure.

    5. Expect the motor to die in 2-4 years. Had a job the duct pressure was 1.3 and it’s supposed to be .5. After 4 motors in 8 years they finally caught on and had it fixed properly.

    Sent from my iPhone using Tapatalk
    There must be a balance of motor rpm / hp and blower wheel blade angles to avoid the high pressure stall?

  2. #22
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    23,573
    Post Likes
    Quote Originally Posted by toofreakinghot View Post
    I would like to put a higher rpm motor on, but if required could dial it down if needed using say the red wire..

    The ducting in this house is bigger than a 747 pressurization system that has to pressurize an aluminum tube with 300 passengers. There is no way on earth this cannot take more flow. The only limiting factor being the fan to produce it.
    If the ducts were bulging like balloons I could understand but I would need a jet engine for that!
    But is it run properly? Air velocity decreases every inch of the run. The longer the run, the duct work needs to decrease in size to keep the velocity up. If you had 2 runs of duct run side by side 100' each and had the same size blower for each. One run of duct was 8" for the entire 100' run. The 2nd run started at 8", reduced to 6" after 33ft and then reduced to 4" after 66ft. The velocity exiting the 4" duct would be greater than that of the 8" duct.
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING

  3. Likes kdean1, VTP99 liked this post.
  4. #23
    Join Date
    Mar 2016
    Location
    Dayton Oh
    Posts
    6,632
    Post Likes
    sooooo you're an engineer?

    do you have a setback on the thermostat???? when you go to work the stat runs up to 75 and when you come home you are wanting it to be 70???

    some of you're comments lead me to believe you have some knowledge so let me ASSuMe... you mentioned a 747 so lets run with that okay. How many engineering hours do you think went into the design of the air delivery system? I dont have a clue really. But could it be 100 hours? "lets try this design it works in the computer model. perfect, get in field and there is a light bulb in the way. lets start over." etc etc. Something tells me an aircraft is engineered to the number of stitches on the seat cushions.

    now tell me, how many hours went into the engineering of the duct system of your house? if you said 0, you are correct. it was likely drawn on the extra mcdonalds napkin that was in the lunch bag.

    yes im sure there is something out there that can do as you wish. but it is gonna cost a lot of money to have implemented in your existing system, and it will be very loud. kinda like a 747. you really wanna sleep in the house and every time the ac kicks on it wakes you up from the extreme noise? Ill pass.

  5. Likes kdean1 liked this post.
  6. #24
    Join Date
    Jan 2010
    Location
    Sea to Sky
    Posts
    7,033
    Post Likes
    Not to mention if the ductwork is not sealed well it could be leaking up to 30 percent of the supplied air out.
    Quote Originally Posted by ksefan View Post
    If the system is designed to cool the house to 75° when it is 100° outside, it might not ever get to 70°. Maybe there is other issues like a loose piece of duct insulation reducing airflow or a weak capacitor. It might not be a bad idea to have the system looked over by a professional.
    Sent from my SM-G965W using Tapatalk

  7. #25
    Join Date
    Aug 2022
    Posts
    19
    Post Likes
    Thread Starter
    Quote Originally Posted by jbhenergy View Post
    do you have a setback on the thermostat???? when you go to work the stat runs up to 75 and when you come home you are wanting it to be 70???
    I don't think that is unreasonable is it? I have always done the same around the world as it makes no sense cost or lifecycle wise to run and cycle the system if Im not home. you do not do that in any other setup, car, hotel, aircraft etc.

    A decent system can always reduce the temp back down in an acceptable time, it is the minimum cost systems that the penny pinching builders are using I suspect is the problem.
    Im just trying to figure out what I can salvage and what I can improve to make the system more than capable rather than barely capable.

  8. #26
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,749
    Post Likes
    You’ve been given several reasons why your ideas will not work but you are not listening to the suggestions.

  9. Likes kdean1, Scoff liked this post.
  10. #27
    Join Date
    Nov 2006
    Location
    SE Ohio
    Posts
    12,907
    Post Likes
    Quote Originally Posted by pecmsg View Post
    You’ve been given several reasons why your ideas will not work but you are not listening to the suggestions.


    He knows better than us and he'll prove even if it kills his system.
    *********
    https://www.hvac20.com/ High efficiency equipment alone does not provide home comfort and efficiency. HVAC2.0 is a process for finding the real needs of the house and the occupants. Offer the customer a menu of work to address their problems and give them a probability of success.

    Find contractors with specialized training in combustion analysis, residential system performance, air flow, and duct optimization https://www.myhomecomfort.org/

  11. #28
    Join Date
    Jun 2014
    Location
    Dover, DE
    Posts
    13,684
    Post Likes
    Quote Originally Posted by toofreakinghot View Post
    I don't think that is unreasonable is it? I have always done the same around the world as it makes no sense cost or lifecycle wise to run and cycle the system if Im not home. you do not do that in any other setup, car, hotel, aircraft etc.

    A decent system can always reduce the temp back down in an acceptable time, it is the minimum cost systems that the penny pinching builders are using I suspect is the problem.
    Im just trying to figure out what I can salvage and what I can improve to make the system more than capable rather than barely capable.
    No, that is not how you should look at it.
    The system isn’t going to pull the house down 5° in 30 minutes when it’s 100° outside. Your going to use all the power you saved with the setback plus some for pull down.
    Plus, you should not expect a consistent temp across 2 floors with a single unzoned system. Without some involved balancing. Just 2 very different environments to deal with.
    As the temperature gets hot, leave the setpoint alone. Let the unit maintain rather then play catch-up during the hottest part of the day.
    “I haven’t failed. I’ve just found 10,000 ways that won’t work.” - Thomas Edison

    “It’s not whether you get knocked down, it’s whether you get up.” - Vince Lombardi

    "In this house we obey the laws of thermodynamics" - Homer Simpson

    Local 486 Instructor & Service Technician

  12. #29
    Join Date
    Aug 2022
    Posts
    19
    Post Likes
    Thread Starter
    Quote Originally Posted by pecmsg View Post
    You’ve been given several reasons why your ideas will not work but you are not listening to the suggestions.
    Appreciate all the input.
    Back to the original question.. Is it possible to switch out either the squirrel wheel with more blade area or the motor for a higher rpm without any mods to the electrical or circuitboard?

  13. #30
    Join Date
    Aug 2009
    Location
    Beatrice, NE
    Posts
    22,117
    Post Likes
    You want more air put in fittings at the plenum with lower equivalent footage.

    I see plenum fittings at 120' EL all the time, replace it with fittings of 10 EL huge difference. also better fittings on the return drop make a huge difference. The amount of air a duct will move is based on TEL (total equivalent length). Dropping a few hundred feet right off the unit increases air flow as it has less restriction, less turbulence.

    Your way will increase operating costs, wear out equipment faster and lower indoor air quality.

  14. Likes toofreakinghot liked this post.
  15. #31
    Join Date
    Jun 2014
    Location
    Dover, DE
    Posts
    13,684
    Post Likes
    Quote Originally Posted by toofreakinghot View Post
    Appreciate all the input.
    Back to the original question.. Is it possible to switch out either the squirrel wheel with more blade area or the motor for a higher rpm without any mods to the electrical or circuitboard?
    No
    “I haven’t failed. I’ve just found 10,000 ways that won’t work.” - Thomas Edison

    “It’s not whether you get knocked down, it’s whether you get up.” - Vince Lombardi

    "In this house we obey the laws of thermodynamics" - Homer Simpson

    Local 486 Instructor & Service Technician

  16. Dislikes toofreakinghot disliked this post.
  17. #32
    Join Date
    Aug 2022
    Posts
    19
    Post Likes
    Thread Starter
    Quote Originally Posted by BNME8EZ View Post
    You want more air put in fittings at the plenum with lower equivalent footage.

    I see plenum fittings at 120' EL all the time, replace it with fittings of 10 EL huge difference. also better fittings on the return drop make a huge difference.
    Where do you recommend to change the fittings? I only really have access in the basement and at the outlet vents themselves as everything else is built into the walls and hardwood floors.

  18. #33
    Join Date
    Mar 2016
    Location
    Dayton Oh
    Posts
    6,632
    Post Likes
    Quote Originally Posted by toofreakinghot View Post
    Appreciate all the input.
    Back to the original question.. Is it possible to switch out either the squirrel wheel with more blade area or the motor for a higher rpm without any mods to the electrical or circuitboard?
    Sure. Have your service tech install you a 2k constant torque motor, set that bad boy for 2000 cfm.
    Watch it not resolve your issue, and in 2 years expect that motor to be dead from running high static and get ready to pay 2500 for a new motor with inflation adjustments.

    And then come back here and report.


    Sent from my iPhone using Tapatalk

  19. Likes kdean1, Scoff liked this post.
    Dislikes toofreakinghot disliked this post.
  20. #34
    Join Date
    Mar 2016
    Location
    Dayton Oh
    Posts
    6,632
    Post Likes

    Turbo Blower

    Quote Originally Posted by toofreakinghot View Post
    I don't think that is unreasonable is it? I have always done the same around the world as it makes no sense cost or lifecycle wise to run and cycle the system if Im not home. you do not do that in any other setup, car, hotel, aircraft etc.

    A decent system can always reduce the temp back down in an acceptable time, it is the minimum cost systems that the penny pinching builders are using I suspect is the problem.
    Im just trying to figure out what I can salvage and what I can improve to make the system more than capable rather than barely capable.
    In the heat of the summer no your unit is not designed to do a hot pull down.

    Here is the short version of system size selection:

    In dayton Ohio my outside design temp is 90*. So I use 90* outside temp in my software. So I run the math of the house and it says I need a 3 ton unit. What that means, is at 90* outside temperature, my house will only MAINTAIN my indoor design temp. At 90* oat my system WILL NOT drop the indoor temp.

    If it’s 85* outside I can drop the temp. But anything 90 and over, if the system is designed per standards, it will not drop.

    Sooooo, when the morning news says it is going to be above average temp today, do not set the thermostat to 75. Leave it at 70

    Clear as mud right


    Sent from my iPhone using Tapatalk

  21. #35
    Join Date
    Jan 2010
    Posts
    45,373
    Post Likes
    The point you're missing on setbacks is the surfaces and surface area within the space. Different materials hold heat longer than others.

  22. #36
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,749
    Post Likes
    YOU can do anything you’d like.

  23. #37
    Join Date
    Aug 2022
    Posts
    19
    Post Likes
    Thread Starter
    Quote Originally Posted by jbhenergy View Post
    In the heat of the summer no your unit is not designed to do a hot pull down.

    Here is the short version of system size selection:

    In dayton Ohio my outside design temp is 90*. So I use 90* outside temp in my software. So I run the math of the house and it says I need a 3 ton unit. What that means, is at 90* outside temperature, my house will only MAINTAIN my indoor design temp. At 90* oat my system WILL NOT drop the indoor temp.

    If it’s 85* outside I can drop the temp. But anything 90 and over, if the system is designed per standards, it will not drop.

    Sooooo, when the morning news says it is going to be above average temp today, do not set the thermostat to 75. Leave it at 70

    Clear as mud right


    Sent from my iPhone using Tapatalk
    So the design is all wrong from the start? Why on earth would anyone want something that could only maintain a temp. How can one ensure that a system is sufficient to reduce as well as maintain? Replace the whole system?

  24. #38
    Join Date
    Aug 2009
    Location
    Beatrice, NE
    Posts
    22,117
    Post Likes
    Quote Originally Posted by toofreakinghot View Post
    Where do you recommend to change the fittings? I only really have access in the basement and at the outlet vents themselves as everything else is built into the walls and hardwood floors.
    Reread the post, it tells you. You are going to need a good duct person to understand what fittings need to go and which can stay. They will be able to better tell where your problem lies than I who have not seen it.

  25. Likes toofreakinghot liked this post.
  26. #39
    Join Date
    Jun 2014
    Location
    Dover, DE
    Posts
    13,684
    Post Likes
    Quote Originally Posted by toofreakinghot View Post
    So the design is all wrong from the start? Why on earth would anyone want something that could only maintain a temp. How can one ensure that a system is sufficient to reduce as well as maintain? Replace the whole system?
    Most systems aren’t a throttle. They are fixed speed.
    Why would you want to have something that would give you a 20 minute pull down at 100° OA? It would make the system unlivable when it was 80° out.
    Even 2 stage units only give you 2 options.
    “I haven’t failed. I’ve just found 10,000 ways that won’t work.” - Thomas Edison

    “It’s not whether you get knocked down, it’s whether you get up.” - Vince Lombardi

    "In this house we obey the laws of thermodynamics" - Homer Simpson

    Local 486 Instructor & Service Technician

  27. #40
    Join Date
    Dec 2002
    Location
    Houston,Texas
    Posts
    23,010
    Post Likes
    Quote Originally Posted by toofreakinghot View Post
    A leaf blower manages to blow a lot through a small tube!
    I would just take out the blower assembly, and mount a leaf blower in there.
    __________________________________________________ _______________________
    “Experience is a hard teacher because she gives the test first, the lesson afterwards" ~ Vernon Law

    "It's what you learn after you know it all that counts." ~ John Wooden

    "When the teachers become unteachable we're all in trouble" ~ Mr. Bill

    "Remember "Pro" is only a name, it's not always a mindset determined to do everything correctly" ~ Mr. Bill




  28. Likes BALloyd, jbhenergy, VTP99, HVAC_Marc liked this post.
Page 2 of 3 FirstFirst 123 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •