    Grounding 24 volt transformer

    Hey guys
    I’ve got a 120volts to 24volts transformer ..I need to ground the secondary 24 volts side, but there’s no indication on the transformer or from the manufacturer on which one of the two wires coming out of the secondary side of the 24 volts to ground ..which one of the two wires do i ground on the 24 volt side of the transformer..?

    Thanks

  2. #2
    Join Date
    Nov 2006
    Location
    SE Ohio
    Posts
    12,907
    Post Likes
    Take your pick. The 24V side is the opposite of the common side.

    There have been some posts here about phase(?) on the transformer and relationship to neutral on the line voltage side but I have not encountered a situation that required switching them. Perhaps someone will comment who has experienced it.
    *********
    https://www.hvac20.com/ High efficiency equipment alone does not provide home comfort and efficiency. HVAC2.0 is a process for finding the real needs of the house and the occupants. Offer the customer a menu of work to address their problems and give them a probability of success.

    Find contractors with specialized training in combustion analysis, residential system performance, air flow, and duct optimization https://www.myhomecomfort.org/

  3. #3
    Join Date
    Mar 2016
    Posts
    24
    Post Likes
    Thread Starter
    What do you mean by take your pick...any of the two wires coming of the the secondary side i could ground?

    Thanks

  4. #4
    Join Date
    Nov 2006
    Location
    SE Ohio
    Posts
    12,907
    Post Likes
    yes. Whichever you pick to ground, the other side will be 24V. The 24V side is the one that gets switched, common should be uninterrupted.
    *********
    https://www.hvac20.com/ High efficiency equipment alone does not provide home comfort and efficiency. HVAC2.0 is a process for finding the real needs of the house and the occupants. Offer the customer a menu of work to address their problems and give them a probability of success.

    Find contractors with specialized training in combustion analysis, residential system performance, air flow, and duct optimization https://www.myhomecomfort.org/

  5. #5
    Join Date
    Mar 2016
    Posts
    24
    Post Likes
    Thread Starter
    Thanks ..

  6. #6
    Join Date
    Nov 2006
    Location
    SE Ohio
    Posts
    12,907
    Post Likes
    You're welcome. I hope it solves the issue for you.
    *********
    https://www.hvac20.com/ High efficiency equipment alone does not provide home comfort and efficiency. HVAC2.0 is a process for finding the real needs of the house and the occupants. Offer the customer a menu of work to address their problems and give them a probability of success.

    Find contractors with specialized training in combustion analysis, residential system performance, air flow, and duct optimization https://www.myhomecomfort.org/

  7. #7
    Join Date
    Apr 2010
    Location
    ... sitting in the Hollywood Hawaiian Hotel, listening to the air conditioner hum
    Posts
    1,208
    Post Likes
    Quote Originally Posted by kdean1 View Post
    Take your pick. The 24V side is the opposite of the common side.

    There have been some posts here about phase(?) on the transformer and relationship to neutral on the line voltage side but I have not encountered a situation that required switching them. Perhaps someone will comment who has experienced it.
    Thats a possibility with systems where there are two transformers wired in parallel. Two 24v xfmrs with the secondaries wired in parallel will give 24 volts at the secondary. If they are wired out of phase, the secondary voltages will sum to 48 volts. Similar to measuring from hot to neutral at the panel vs hot to hot.

    The great professors of the art are not immune from the malignancy of matter and the eternal cussedness of inanimate objects.

  8. #8
    Join Date
    Jan 2007
    Location
    Mn the state where absolutey nothing is allowed
    Posts
    2,516
    Post Likes
    polarity= L1 to ground, 120V. neutral to ground, 0 volts
    ground/bonding= ground (EGC) to chassis, 0 volts
    phasing a transformer= L1 to R, 96 volts. Out of phase= L1 to R= 144 volts.
    correct phase= primary voltage minus secondary voltage, out of phase, voltages add together.

    for what is worth.......
    my boss thinks its possible to repeal the laws of physics

  9. Likes BALloyd liked this post.
  10. #9
    Join Date
    Jun 2020
    Location
    BAIRD, TX
    Posts
    1,475
    Post Likes
    Quote Originally Posted by Cisco007 View Post
    Hey guys
    I’ve got a 120volts to 24volts transformer ..I need to ground the secondary 24 volts side, but there’s no indication on the transformer or from the manufacturer on which one of the two wires coming out of the secondary side of the 24 volts to ground ..which one of the two wires do i ground on the 24 volt side of the transformer..?

    Thanks
    The only transformers that were grounded on the secondary side I had to replace because some electrician thought everything needs to be grounded! Don't ground low voltage secondaries! Why would you want to ground L1 or L2?? You do not ground live wires. if the secondary goes to ground it is screwed down to grounded metal. You are confused about the American 120 VAC system that uses a neutral instead of just using 240 VAC system like Europe. We use 120 VAC because A. Edison was in a war with Tesla about electrical distribution. Edison lost because he was completely wrong and wanted to use DC. We run 765,000 VAC in transmission lines to lower amperage and wire size then just drop VAC as necessary thru transformers. Most people die of electrocution from a 120 VAC circuit that has lost a path to ground (neutral).
    " The more I learn the more I realize how much I don't know"

  11. #10
    Join Date
    Apr 2020
    Location
    va
    Posts
    10,300
    Post Likes
    Quote Originally Posted by stumpdigger View Post
    The only transformers that were grounded on the secondary side I had to replace because some electrician thought everything needs to be grounded! Don't ground low voltage secondaries! Why would you want to ground L1 or L2?? You do not ground live wires. if the secondary goes to ground it is screwed down to grounded metal. You are confused about the American 120 VAC system that uses a neutral instead of just using 240 VAC system like Europe. We use 120 VAC because A. Edison was in a war with Tesla about electrical distribution. Edison lost because he was completely wrong and wanted to use DC. We run 765,000 VAC in transmission lines to lower amperage and wire size then just drop VAC as necessary thru transformers. Most people die of electrocution from a 120 VAC circuit that has lost a path to ground (neutral).
    ???????????
    Wire per the vendor diagrams. I have had gas valve open with no safeties because of loose or disconnected 24vt grounds, solid state controls intermittently not function and other fail because of inadequate grounding.

  12. #11
    Join Date
    Jun 2020
    Location
    BAIRD, TX
    Posts
    1,475
    Post Likes
    Quote Originally Posted by ehsx View Post
    ???????????
    Wire per the vendor diagrams. I have had gas valve open with no safeties because of loose or disconnected 24vt grounds, solid state controls intermittently not function and other fail because of inadequate grounding.
    Wondering if I understand. Are you saying a poor chassis ground on a 24 VAC causes your circuits not to funtion properly? Are you sending current through the chassis? Never saw that, circuit boards always worked just fine for me.
    " The more I learn the more I realize how much I don't know"

  13. #12
    Join Date
    May 2014
    Location
    Bay Area California
    Posts
    43,457
    Post Likes
    If this transformer is going on a unit that has heating with flame rectification to sense the flame, polarity of the transformer and which side gets grounded is critical.

    So you always fire off the heating to be sure you don't/won't have a call when it gets cold.
    I do a triple evac with nitro to remove non condensables.

  14. #13
    Join Date
    Jan 2010
    Location
    Sea to Sky
    Posts
    7,033
    Post Likes
    Quote Originally Posted by stumpdigger View Post
    Wondering if I understand. Are you saying a poor chassis ground on a 24 VAC causes your circuits not to funtion properly? Are you sending current through the chassis? Never saw that, circuit boards always worked just fine for me.
    In the United States, for example:

    ◆The National Electrical Code® requires (section 250.20) grounding transformers for AC systems of less than 50 volts if the primary voltage exceeds 150 volts to ground or if the main transformer supplying power to the building is ungrounded.

    ◆Some municipal electrical codes more restrictive than the NEC may require that the secondaries of all transformers that supply 24 VAC be grounded

  15. #14
    Join Date
    Apr 2020
    Location
    va
    Posts
    10,300
    Post Likes
    Quote Originally Posted by stumpdigger View Post
    Wondering if I understand. Are you saying a poor chassis ground on a 24 VAC causes your circuits not to funtion properly? Are you sending current through the chassis? Never saw that, circuit boards always worked just fine for me.
    The 24vt is ac, without grounding it can back feed to grnd and cause, in the case I had the gas valve to energize on a call for heat, bypassing ignition and safeties, old Trane rooftop. The gas valve was the last component in line and had enough voltage to open the valve. Found the xformer grnd hanging behind a relay unconnected. A good way to blow up a building, I could smell gas when I drove up into the parking lot.

    On a number of units with solid state furnace controls and old 2 wire electrical service had to add equipment grounds and would add a surge suppressor for good measure also. Electronic t'stats without ground wires would also cause problems with electronics down stream that did not have ground terminals, same with two wire time delays and electronic controls downstream, intermittent malfunctions.

    On a chiller the mfg tied the 24 vac and 24 vdc commons together on a controller causing intermittent issues and controller failures. Had to grnd the 24 vac separately.

  16. #15
    Join Date
    Jun 2020
    Posts
    10
    Post Likes
    Doesn't the current NEC call for the secondary to be grounded?

  17. #16
    Join Date
    Apr 2020
    Location
    va
    Posts
    10,300
    Post Likes
    Yes, in most all cases.
    NEC "Circuits under 50V may have to be grounded. (sec. 250-5)". "If supply system operates ungrounded, then secondary must be operated grounded regardless of voltage."

    Wiring by mfg has to be certified by an "approved agency" UL, ETL, CUL....

  18. #17
    Join Date
    Jun 2020
    Location
    BAIRD, TX
    Posts
    1,475
    Post Likes
    Quote Originally Posted by BBeerme View Post
    If this transformer is going on a unit that has heating with flame rectification to sense the flame, polarity of the transformer and which side gets grounded is critical.

    So you always fire off the heating to be sure you don't/won't have a call when it gets cold.
    The solid state flame rectifier uses a simple electronic current relay, when it senses current flow from the flame rod to anywhere it proves pilot. If you deliberately ground out the flame rod the relay circuit senses a failure and opens. Clean the rod and pilot hood
    " The more I learn the more I realize how much I don't know"

  19. #18
    Join Date
    Jun 2020
    Location
    BAIRD, TX
    Posts
    1,475
    Post Likes
    Quote Originally Posted by BALloyd View Post
    In the United States, for example:

    ◆The National Electrical Code® requires (section 250.20) grounding transformers for AC systems of less than 50 volts if the primary voltage exceeds 150 volts to ground or if the main transformer supplying power to the building is ungrounded.

    ◆Some municipal electrical codes more restrictive than the NEC may require that the secondaries of all transformers that supply 24 VAC be grounded
    They are speaking of an extra ground on the transformer which is taken care of as it's screwed to the chassis.
    " The more I learn the more I realize how much I don't know"

  20. #19
    Join Date
    Jun 2020
    Location
    BAIRD, TX
    Posts
    1,475
    Post Likes
    Quote Originally Posted by Tom27 View Post
    Doesn't the current NEC call for the secondary to be grounded?
    Special for you , it's grounded at the chassis.
    " The more I learn the more I realize how much I don't know"

  21. #20
    Join Date
    Jun 2020
    Location
    BAIRD, TX
    Posts
    1,475
    Post Likes
    Quote Originally Posted by ehsx View Post
    The 24vt is ac, without grounding it can back feed to grnd and cause, in the case I had the gas valve to energize on a call for heat, bypassing ignition and safeties, old Trane rooftop. The gas valve was the last component in line and had enough voltage to open the valve. Found the xformer grnd hanging behind a relay unconnected. A good way to blow up a building, I could smell gas when I drove up into the parking lot.

    On a number of units with solid state furnace controls and old 2 wire electrical service had to add equipment grounds and would add a surge suppressor for good measure also. Electronic t'stats without ground wires would also cause problems with electronics down stream that did not have ground terminals, same with two wire time delays and electronic controls downstream, intermittent malfunctions.

    On a chiller the mfg tied the 24 vac and 24 vdc commons together on a controller causing intermittent issues and controller failures. Had to grnd the 24 vac separately.
    The transformer comes with two posts, two conductors out of phase at +/- 24 VAC sixty cycles/ second; 60Hz if you prefer. There is no ground, there is no neutral, it's just two hot legs. L1 (red) and L2 (common). If you are having issues with grounded 24 VAC systems it is because you are grounding HOT and/ or COMMON. If some engineer wants to ground some circuit board ect. ,they will do it by means of mounting screws. And please do not mix A/C and D/C CIRCUITS.
    " The more I learn the more I realize how much I don't know"

+ Reply to Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •