    Confused Manuf. recommended filter size REALLY wrong?

    I'm stumped.

    Last year I purchased an older ranch home with solid ducts and a 3-ton AC and gas furnace installed in 2007. The unit sits on a filter box made for 1" deep filters (can be 2" if some tabs are ripped off), sized for 14"x25" filters. Seemed very inadequate so I found the manufacturers online pdf and it recommends a 14x25x1 filter.

    Compared to the advice given in this forum this seems way, WAY wrong. Am I missing something?! How can a manufacturer recommend a filter size thats, what, a whole third or fourth the size of current best practices?



    Manual for Lennox G4OUH-36A-070-15 (1200CFM gas furnace)
    http://www.lennox.com/pdfs/installat..._G40UH_IOM.pdf

    Manual for Lennox C33-38A-2F-3 (1200CFM Coil, Dry .27, Wet .30)
    http://tech.lennoxintl.com/C03e7o14l...7R/505060h.pdf

    On top of that, (bad pics below) the unit sits in a hall closet on a raised platform along with the water heater, where a single return air is just 14x25 hole into said platform cavity to a opening under the closet door into the hall. The studs and floor plate only provide a return opening of a mere 28"w x 9.5"h to the hall.



    I've come up with the following options:

    1) Burn it all to the ground. Cost prohibitive.

    2) At least make the filter box accept 2" filters and cut out some more drywall to the hallway and make a bigger grilled return. Filtered grill doesn't look to be an option with just 9.5 height restriction. All this still leaves the puny 14x25 hole in the platform.

    3) Somehow raise the whole unit and replace the filter box with something bigger. Ducting into the attic is but a few feet so not a lot of wiggle room. I'm very handy, but no experience with HVAC, am I better off having a pro do this and so how much cost am I looking at?

    4) Cut a hole in the hallway wall and side of the unit and side-mount some sort of filter/box/return grill? It's 6.25" from the unit to the closet drywall.

    5) Yell obscenities at it until it fixes itself. Time prohibitive.

    Any advice?

  2. #2
    Join Date
    Jun 2011
    Location
    Houston area
    Posts
    1,493
    Post Likes
    First off I'm getting a bit older and it hurts my neck to look sideways so I rotated the pics for you.

    According to manual that's all you need. It wouldn't hurt to enlarge the opening to the platform (in the hallway) as much as you can. Trying to raise the unit up by yourself is a really really bad idea.

    Attachment 233201 Attachment 233211 Attachment 233221
    The picture in my avatar is of the Houston Ship Channel and was taken from my backyard. I like to sit outside and slap mosquitos while watching countless supertankers, barges and cargo ships of every shape and size carry all sorts of deadly toxins to and fro. It's really beautiful at times.....just don't eat the three eyed fish....

    ¯`·.¸¸ .·´¯`· .¸>÷÷(((°>

    `·.¸¸..· ´¯`·.¸ ¸.·´¯` ·.¸>÷÷(((°>

    .·´¯`· .¸>÷÷(((°>

    LMAOSHMSFOAIDMT

  3. #3
    Join Date
    Dec 2011
    Posts
    10
    Post Likes
    Thread Starter
    Quote Originally Posted by Cooked View Post
    Trying to raise the unit up by yourself is a really really bad idea.
    Alright, I'll take your word for it even though where I'm from "bad idea" implies a dare.

    Thanks for editing the pics for me.

  4. #4
    Join Date
    Aug 2007
    Location
    Northern VA 38 degrees N by 76 degrees W
    Posts
    5,115
    Post Likes
    Quote Originally Posted by fferd View Post
    I'm stumped.

    Last year I purchased an older ranch home with solid ducts and a 3-ton AC and gas furnace installed in 2007. The unit sits on a filter box made for 1" deep filters (can be 2" if some tabs are ripped off), sized for 14"x25" filters. Seemed very inadequate so I found the manufacturers online pdf and it recommends a 14x25x1 filter.

    Compared to the advice given in this forum this seems way, WAY wrong. Am I missing something?! How can a manufacturer recommend a filter size thats, what, a whole third or fourth the size of current best practices?



    Manual for Lennox G4OUH-36A-070-15 (1200CFM gas furnace)
    http://www.lennox.com/pdfs/installat..._G40UH_IOM.pdf

    Manual for Lennox C33-38A-2F-3 (1200CFM Coil, Dry .27, Wet .30)
    http://tech.lennoxintl.com/C03e7o14l...7R/505060h.pdf

    On top of that, (bad pics below) the unit sits in a hall closet on a raised platform along with the water heater, where a single return air is just 14x25 hole into said platform cavity to a opening under the closet door into the hall. The studs and floor plate only provide a return opening of a mere 28"w x 9.5"h to the hall.



    I've come up with the following options:

    1) Burn it all to the ground. Cost prohibitive.

    2) At least make the filter box accept 2" filters and cut out some more drywall to the hallway and make a bigger grilled return. Filtered grill doesn't look to be an option with just 9.5 height restriction. All this still leaves the puny 14x25 hole in the platform.

    3) Somehow raise the whole unit and replace the filter box with something bigger. Ducting into the attic is but a few feet so not a lot of wiggle room. I'm very handy, but no experience with HVAC, am I better off having a pro do this and so how much cost am I looking at?

    4) Cut a hole in the hallway wall and side of the unit and side-mount some sort of filter/box/return grill? It's 6.25" from the unit to the closet drywall.

    5) Yell obscenities at it until it fixes itself. Time prohibitive.

    Any advice?
    Your filter dimension is not the problem, the return air grill is too small.

  5. #5
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Most manufacturers use a filter size that meets or just barely exceeds the 500 FPM rating of the air filter. Yours is 494FPM at 1200 CFM.

  6. #6
    Join Date
    Feb 2006
    Location
    Float'N Vally, MS
    Posts
    3,521
    Post Likes
    There are a lot of things wrong with those pictures.

    If I am not mistaken, that filter box will accept a 3" or maybe a 4" filter.
    You would do yourself a favor by upgrading.
    Life is too short, Behappy!
    TFMM

  7. #7
    Join Date
    Jul 2006
    Location
    Prata di Pordenone Italy
    Posts
    8,069
    Post Likes
    looks like a typical Texas install was probably furnace only when built and ac added later I would remove the slides and install a 2 inch filter. sometimes you can cut more return air vents into wall .I have installed many units similar to what you have

  8. #8
    Join Date
    Dec 2011
    Posts
    10
    Post Likes
    Thread Starter
    Quote Originally Posted by catmanacman View Post
    looks like a typical Texas install was probably furnace only when built and ac added later I would remove the slides and install a 2 inch filter. sometimes you can cut more return air vents into wall .I have installed many units similar to what you have
    Hit it right on the head, it's in Texas and the space was originally made for just a furnace.

    From everyone's advice it's nice to hear nothing too drastic has to change. Still don't quite understand how this 3 ton filter size "needs" is so different from other 3 tons discussed on this site.

  9. #9
    Join Date
    Dec 2011
    Posts
    10
    Post Likes
    Thread Starter
    Quote Originally Posted by behappy View Post
    If I am not mistaken, that filter box will accept a 3" or maybe a 4" filter.
    Unfortunately a 3" (2 5/8" or whatever it really is) won't fit unless it's crushed and jammed in.

  10. #10
    Join Date
    Nov 2000
    Location
    Eastern PA
    Posts
    70,520
    Post Likes
    If nothing else, at least stop using those restrictive 1" pleated filters. Let the system breathe. 1" filters claiming to be better for your health are always going to be potentially damaging to your HVAC system.

    As long as there are no air leaks around the filter or at the connections of the filter rack to the unit, the inexpensive fiberglass filters are best to protect they HVAC system while not restricting air flow.

    There is no air filter that will make any significant difference in the healthiness of your air that will not cause too much restriction for the system without greatly enlarging the free area of air for that filter. Filters are there to protect the HVAC equipment, not so much for human health. If you need/want better filtration for cleaining up the air for health reasons, have a self contained by-pass HEPA filter, properly placed UV lighting or Bi-polar ionization units and outside air system installed.
    Training is important!
    Practical Training is a must!

  11. #11
    Join Date
    Jan 2005
    Location
    Emerald Coast
    Posts
    1,640
    Post Likes
    .
    2A)
    Next filter change pick up the 2" pleated merv 8 filter and make the move,
    simple effective and better than you have at this time.
    ..
    Do not attempt vast projects with
    half vast experience and ideas.
    ...

  12. #12
    Join Date
    Dec 2011
    Posts
    10
    Post Likes
    Thread Starter
    Right, I get the "more Merv isn't better", currently using the cheapest 1" pleated.

    My main concern is if a single 14x25(1" or 2") is anywhere near adequate and if not, just how far can I reasonably go to make the unit breath easier.

  13. #13
    Join Date
    Jan 2005
    Location
    Emerald Coast
    Posts
    1,640
    Post Likes
    .
    See Post #4.

    Your return grille is too small / restrictive.

    Possibly replace that grille with a custom plastic eggcrate grille.
    ..


    It will prevent cats from getting sucked thru.
    Do not attempt vast projects with
    half vast experience and ideas.
    ...

  14. #14
    Join Date
    Dec 2007
    Location
    houston, texas
    Posts
    3,787
    Post Likes
    Quote Originally Posted by superheatsleuth View Post
    .
    See Post #4.

    Your return grille is too small / restrictive.
    That is a problem for sure, but what is that gap in the flue pipe just above the 90?
    I'm not tolerating Political Correctness anymore, from now on it's tell it like it is.

    Veto Pro Pak - The best tool bag you'll ever own






  15. #15
    Join Date
    Jan 2005
    Location
    Emerald Coast
    Posts
    1,640
    Post Likes
    .
    Appears to be a 12" adjustable.
    ..
    Do not attempt vast projects with
    half vast experience and ideas.
    ...

  16. #16
    Join Date
    Jun 2011
    Location
    Houston area
    Posts
    1,493
    Post Likes
    Quote Originally Posted by superheatsleuth View Post

    It will prevent cats from getting sucked thru.
    And who among us would consider that to be a problem?
    The picture in my avatar is of the Houston Ship Channel and was taken from my backyard. I like to sit outside and slap mosquitos while watching countless supertankers, barges and cargo ships of every shape and size carry all sorts of deadly toxins to and fro. It's really beautiful at times.....just don't eat the three eyed fish....

    ¯`·.¸¸ .·´¯`· .¸>÷÷(((°>

    `·.¸¸..· ´¯`·.¸ ¸.·´¯` ·.¸>÷÷(((°>

    .·´¯`· .¸>÷÷(((°>

    LMAOSHMSFOAIDMT

  17. #17
    Join Date
    Dec 2011
    Posts
    10
    Post Likes
    Thread Starter
    Quote Originally Posted by Cooked View Post
    And who among us would consider that to be a problem?
    I'd pay extra for the cat-sucking feature. May need to clean the unit more often, though.

  18. #18
    Join Date
    Nov 2000
    Location
    Eastern PA
    Posts
    70,520
    Post Likes
    Quote Originally Posted by fferd View Post
    Right, I get the "more Merv isn't better", currently using the cheapest 1" pleated.

    My main concern is if a single 14x25(1" or 2") is anywhere near adequate and if not, just how far can I reasonably go to make the unit breath easier.
    1" pleated filters are restrictive, no matter the cost. There isn't really 1" of filter, but rather only a thin layer due to the pleating. Use regular 1" fiberglass or spun plastic filters that actually have 1" of media.
    Training is important!
    Practical Training is a must!

  19. #19
    Join Date
    Feb 2006
    Location
    Float'N Vally, MS
    Posts
    3,521
    Post Likes
    Quote Originally Posted by RoBoTeq View Post
    Use regular 1" fiberglass or spun plastic filters that actually have 1" of media.
    With CATS!
    Life is too short, Behappy!
    TFMM

  20. #20
    Join Date
    Nov 2000
    Location
    Eastern PA
    Posts
    70,520
    Post Likes
    Quote Originally Posted by behappy View Post
    With CATS!
    I don't understand.

    If this is supposed to be a question pertaining to having cats in the house, then what ever cat fur does to a 1" filter with 1" of media is going to be the same for any filter.
    Training is important!
    Practical Training is a must!

Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Tags for this Thread

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •