    Quote Originally Posted by beenthere View Post
    That won't tell you the total capacity. Only the sensible. So its not nearly accurate on a fresh air system.
    IF GPM of chilled water is same , what would be change in energy cost with reduced CFM across cooling coil?

  2. #42
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Quote Originally Posted by Raghurajsawhney View Post
    IF GPM of chilled water is same , what would be change in energy cost with reduced CFM across cooling coil?
    How much did the chilled water delta through the coil change.

  3. #43
    Join Date
    Jan 2021
    Posts
    9
    Post Likes
    Quote Originally Posted by beenthere View Post
    How much did the chilled water delta through the coil change.
    Delta T is 6C

  4. #44
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    If the chilled water delta remains the same at both CFMs, then there is no energy savings.

  5. #45
    Join Date
    Jan 2021
    Posts
    9
    Post Likes

    Calculations

    Quote Originally Posted by beenthere View Post
    If the chilled water delta remains the same at both CFMs, then there is no energy savings.
    In an Chilled water Air Handling unit

    Situation 1

    Supply air temp to coil = 35C
    CFM = 5000
    Supply air to Space 23 C at 5000 CFM

    Chilled water Supply 4C
    GPM 20

    Chilled water return 8 C

    Situation 2

    Supply air temp to coil = 35C
    CFM = 3000
    Supply air to Space 23 C at 3000 CFM

    Chilled water Supply 4C
    GPM 20

    Chilled water return NA

    Question : 1. with decrease in CFM will there be change in Delta T of chilled water? And by how much approx.
    2. What could be energy consumed in KWH in Situation 1 and Situation 2

    Kindly share your thoughts. I am working on an energy saving project and would appreciate if you can help.

    Thanks

  6. #46
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Unless I punched a number in wrong. Your first example shows a sensible air temp of 118,000 BTUs. But your chilled water only shows a 70,000 BTU change.

    Need realistic numbers.

  7. Likes heatingman liked this post.
  8. #47
    Join Date
    Dec 2004
    Location
    Chicago area
    Posts
    19,137
    Post Likes
    Quote Originally Posted by Raghurajsawhney View Post
    In an Chilled water Air Handling unit

    Situation 1

    Supply air temp to coil = 35C
    CFM = 5000
    Supply air to Space 23 C at 5000 CFM

    Chilled water Supply 4C
    GPM 20

    Chilled water return 8 C

    Situation 2

    Supply air temp to coil = 35C
    CFM = 3000
    Supply air to Space 23 C at 3000 CFM

    Chilled water Supply 4C
    GPM 20

    Chilled water return NA

    Question : 1. with decrease in CFM will there be change in Delta T of chilled water? And by how much approx.
    2. What could be energy consumed in KWH in Situation 1 and Situation 2

    Kindly share your thoughts. I am working on an energy saving project and would appreciate if you can help.

    Thanks
    There will be virtually no energy savings. Might be some, but very minimal. And as was pointed out, you need real life numbers, or a good computer model to know.

    As you slow the fan, you will remove more moisture from the air. Unless the water temp is above the dew point of the air. And also you will increase the delta on the air side.

    Delta on the water side would barely change.

    The fan slowing pending on how its done can save electricity that way.

    But on the chilled water side, you’d save more buy reducing flow on that end. This is the more typical approach. Control the water volume to meet desired space or air conditions. Fan speed typically manipulated for either dehumidification enhancement, building pressure requirements, or duct pressure requirements.


    Sent from my iPhone using Tapatalk

  9. #48
    Join Date
    Jan 2021
    Posts
    9
    Post Likes
    Quote Originally Posted by beenthere View Post
    Unless I punched a number in wrong. Your first example shows a sensible air temp of 118,000 BTUs. But your chilled water only shows a 70,000 BTU change.

    Need realistic numbers.
    I have just provided figures to depict a situation . Not any realistic figures. The delta T can be higher . you can do your calculations with change in chilled water BTU proportional to delta T change in Air

    what is the formula/s to do such calculations.

+ Reply to Thread
Page 3 of 3 FirstFirst 123

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •