    Angry Trane RTAA

    Am I the only one who shakes my head when I have to pull a sensor to check accuracy? Why doesn't Trane use wells for the sensors?

  2. #2
    Join Date
    Aug 2006
    Location
    Ohio
    Posts
    2,759
    Post Likes
    Quote Originally Posted by seathop View Post
    Am I the only one who shakes my head when I have to pull a sensor to check accuracy? Why doesn't Trane use wells for the sensors?
    I service quite a few RTAAs and RTWAs.

    I want to pull my hair out every time I have to check or change a sensor.

    I have taken more "Trane oil baths" than I can count.
    UA LU189

  3. #3
    Join Date
    Mar 2004
    Location
    ottawa canada
    Posts
    4,011
    Post Likes
    Am I the only one who shakes my head when I have to pull a sensor to check accuracy? Why doesn't Trane use wells for the sensors?


    Thats what that fancy chart in the IOM is for , you know the one that compares resistance to temperature ??????????
    The toy chest is officially full ... I got a new toy..... 2007 Aston Martin V8 Vantage and yes it still gives me goosebumps
    You bend em" I"ll mend em" !!!!!!!
    I"m not a service tech, I’m retired ….I used to be a thermodynamic transfer analyst & strategic system sustainability specialist
    In the new big shop , greasin', oilin' . tweakin' n shinin' !!

  4. #4
    Join Date
    Sep 2005
    Location
    Pa
    Posts
    305
    Post Likes
    Thread Starter
    Reading the fancy chart is easy, how do you get an accurate temp. reading of the sensor, especially if its submerged in glycol in the chiller barrel or inside the suction line ect. sensors whos inputs dictate chiller operation must be accurate, thats why they recommend changing them in pairs!! To compare two sensors that are in two different locations, I don't know a better way to do it but to remove them to see if they read the same ambient air temp. What am I missing?
    Last edited by seathop; 12-19-2010 at 07:15 PM. Reason: Additional information

  5. #5
    Join Date
    Mar 2004
    Location
    ottawa canada
    Posts
    4,011
    Post Likes
    In the 14yrs that I have been working on the RTAA I have never seen a sensor off by a small amount . They are always way off , like out to lunch off , because the sensor has either shorted , grounded or is open . if you have a good infared or strap on sensor themometer or if its a refrigerant sensor use your gauges and work it backwards you shouldnt need to pull the sensor other than to replace it .
    The toy chest is officially full ... I got a new toy..... 2007 Aston Martin V8 Vantage and yes it still gives me goosebumps
    You bend em" I"ll mend em" !!!!!!!
    I"m not a service tech, I’m retired ….I used to be a thermodynamic transfer analyst & strategic system sustainability specialist
    In the new big shop , greasin', oilin' . tweakin' n shinin' !!

  6. #6
    Join Date
    Dec 2010
    Location
    On a Peninsula in NE NC
    Posts
    1,904
    Post Likes
    Quote Originally Posted by graham View Post
    In the 14yrs that I have been working on the RTAA I have never seen a sensor off by a small amount . They are always way off , like out to lunch off , because the sensor has either shorted , grounded or is open . if you have a good infared or strap on sensor themometer or if its a refrigerant sensor use your gauges and work it backwards you shouldnt need to pull the sensor other than to replace it .
    Same here, never seen one off by a little, alway's way outa range. I have also never had an issue changing one. Pull it down to 2-3psig and good to go. I only had an issue with 1 water side sensor that the water valves were so rotted out they did not work. I took a bath on that for sure.

  7. #7
    Join Date
    Dec 2010
    Location
    Brisbane, Australia
    Posts
    11
    Post Likes

    Trane RTAA

    Thermistor sensors such as Trane use in RTAA's can go out of range, especially the ones that are in cold spots such as leaving CHW: they suck in moisture sometimes which reduces the resitance and increases the temperature reading. I have only spent about six years on these things but agree with Graham: you shouldn't need to pull them out. You have two circuits: compare them. If your leaving chilled water is out you'll see that when you compare it to ent. CHW; you'll also likely get diags coming up telling you so. The RTAA is a great machine: don't knock them!

  8. #8
    Join Date
    Jan 2011
    Location
    Pacific Northwest
    Posts
    20
    Post Likes
    RTAA is a good machine, I agree with above that they are usually way off if they are off at all and you shouldn't need to pull the sensors to check them.

  9. #9
    Join Date
    Jan 2004
    Location
    Oregon
    Posts
    2,096
    Post Likes
    I have maybe changed a dozen in 18 years at Trane.

  10. #10
    Join Date
    Jan 2005
    Location
    Houston TX
    Posts
    1,041
    Post Likes

    Sensor errors

    I've also been heavily involved with RTAA.RTHA,RTHB and RTWA sensors and if they are way off it is easy to detect by using the charts. You may also have the alarm status letting you know whats going on with the temperature sensor. As a procedure during annuals if the sensor accuracy looks questionable (entering water a few degrees cooler then my thermometer comes out) the resistance of the sensor is checked. Another major problem I have come across is when a sensor (pair) has been changed the new cables are cut and then wire nutted to the existing terminations. I prefer to use the entire new sensor and remove the all the old wire along with the sensor, route the new cable as I'm removing the old and make a new termination in the amp plug on the control board. It really isn't that hard to do.-GEO
    Once in a while everything falls into place and I am able to move forward, most of the time it just falls all over the place and I can't go anywhere-GEO

  11. #11
    Join Date
    Mar 2004
    Location
    ottawa canada
    Posts
    4,011
    Post Likes
    Another major problem I have come across is when a sensor (pair) has been changed the new cables are cut and then wire nutted to the existing terminations. I prefer to use the entire new sensor and remove the all the old wire along with the sensor, route the new cable as I'm removing the old and make a new termination in the amp plug on the control board. It really isn't that hard to do.-GEO


    Thats the way its supposed to be done but there are a lot of hacks and lazy @&?holes out there that think they know better !!!!!!!!!!!!!!!!!!
    And its guys like us that do it right that have to fix their #@?$ work !!!!!
    The toy chest is officially full ... I got a new toy..... 2007 Aston Martin V8 Vantage and yes it still gives me goosebumps
    You bend em" I"ll mend em" !!!!!!!
    I"m not a service tech, I’m retired ….I used to be a thermodynamic transfer analyst & strategic system sustainability specialist
    In the new big shop , greasin', oilin' . tweakin' n shinin' !!

  12. #12
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    8,082
    Post Likes
    Quote Originally Posted by ga1279 View Post
    ...As a procedure during annuals if the sensor accuracy looks questionable (entering water a few degrees cooler then my thermometer comes out) the resistance of the sensor is checked...
    i, too, used to check the resistance on suspect sensors, but i never found one that was inaccurate at the control panel! the resistance ALWAYS matched the chart and the resistance chart ALWAYS matched the control panel...but the resistance RARELY matched the actual!
    "Right" is not the same as "Wise".

    Don't step on my favorite part of the Constitution just to point out your favorite part.

    Just because you can measure it, doesn't mean it is important. Just because you can't measure it, doesn't mean it isn't important.

  13. #13
    Join Date
    Dec 2009
    Location
    Southern US
    Posts
    504
    Post Likes
    Just replaced a saturated condensor sensor last week and I have to agree with graham.

    Pulled the old wiring out and rewire tied back to the control board. I have seen a few with those blue wirenuts at the sensors and I just cannot remember ever seeing a new unit show up that way.

    Maybe its a little overkill but I cut out the old ties and use the mounts for the new ties. I just like the equipment to be neat and clean.
    I'm good at making things cold...You can ask my first two wives!

  14. #14
    Join Date
    Oct 2004
    Location
    Metro ATL
    Posts
    474
    Post Likes
    The biggest problem I have with these sensors are the wiring connections on the board. I hate those connectors. A poor connection here will give you strange readings.

  15. #15
    Join Date
    Jan 2005
    Location
    Houston TX
    Posts
    1,041
    Post Likes

    Sensor leads

    Graham, Jayguy and Jemawalton: I know what the bulletins and service books say about sensor change, but I would rather have a solid insulated wire from the end of the sensor to terminate at the proper module. The termination isn't really that hard to do, I use a small c-clamp vise and mount the MTA in there and I use the rounded lead from an old Fluke test lead and it will pop it right in there correctly. Then again you could be real fancy and spend the money for the AMP tool, but unfortunately I can't afford it as little as I replace them. I have had several that the blue or orange wire nuts had gotten corroded inside and increase the resistance and made a good sensor look bad, thus the reason I follow the procedure I outlined. I like running them the same length as the original. Except for the larger units that have the junction box at mid point along with the condenser fans. There is generally enough wire to go from the evaporator liquid point to the module. I have also seen those beads not positioned correctly and causing a variance on the reading. I like to leave the machine better then it was when I got there. -GEO
    Once in a while everything falls into place and I am able to move forward, most of the time it just falls all over the place and I can't go anywhere-GEO

  16. #16
    Join Date
    Apr 2011
    Location
    Southern Indiana
    Posts
    482
    Post Likes
    Quote Originally Posted by Healey Nut View Post
    Am I the only one who shakes my head when I have to pull a sensor to check accuracy? Why doesn't Trane use wells for the sensors?


    Thats what that fancy chart in the IOM is for , you know the one that compares resistance to temperature ??????????
    What page is that chart on? Do you have that IOM?

  17. #17
    Join Date
    Jul 2018
    Location
    Kazakhstan
    Posts
    43
    Post Likes
    RLC-SVD03A-EN manual pages 15-18, RTAA-SB-5 service bulletin pages 19-23.
    RLC-SVD03A - http://www.graycoolingman.com/upload...-svd03a-en.pdf

  18. #18
    Join Date
    Nov 2014
    Location
    Abu Dhabi, United Arab Emirates, United Arab Emirates
    Posts
    1
    Post Likes
    Hi sir can you told me the size of oil drain valve of oil separator of RTAA 328

  19. #19
    Join Date
    Nov 2011
    Location
    CO
    Posts
    17,439
    Post Likes
    Quote Originally Posted by Haris Shahid View Post
    Hi sir can you told me the size of oil drain valve of oil separator of RTAA 328

    instead of reviving a 10 year old thread with a topic that is completely unrelated to your question, start a new thread for your issue. you will have a better chance of getting an answer.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •