Thread: Superheat

  1. #1
    Join Date
    Oct 2010
    Location
    Rocklin, CA.
    Posts
    4
    Post Likes

    Superheat

    Will superheat go up or down on a capillary tube system, when the evaporator stays at a steady heat load and the condenser is suddenly cooled by a spray of water and why?

  2. #2
    Join Date
    Jan 2004
    Location
    PA
    Posts
    77,677
    Post Likes
    It will go up.

    Because the amount of refrigerant being fed to the evap will be less.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  3. #3
    Join Date
    Feb 2007
    Posts
    1,002
    Post Likes
    Beenthere, I was under the impression (perhaps wrongly) that a captube is a fixed orifice device. If so, how is less refrigerant delivered?

  4. #4
    Join Date
    Jan 2004
    Location
    PA
    Posts
    77,677
    Post Likes
    They require X pressure difference across them to maintain the flow rate.

    As the condensers pressure drops, the PD across the cap tube drops. feeding less refrigerant through the cap tube.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  5. #5
    Join Date
    Feb 2009
    Location
    Tallahassee, FL
    Posts
    6,217
    Post Likes
    Picture a garden hose sprayer nozzle set at one particular flow rate.

    What is the spray flow like at 80 psi?

    And compare that to 40 psi.

  6. #6
    Join Date
    Feb 2007
    Posts
    1,002
    Post Likes
    THANKS

  7. #7
    Join Date
    Oct 2010
    Location
    Rocklin, CA.
    Posts
    4
    Post Likes
    Thread Starter

    cornfused

    Thanks guys for your reply, best wishes.

  8. #8
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,677
    Post Likes
    Wouldn't the suction drop off almost as rapidly as the head pressure?



  9. #9
    Join Date
    Feb 2009
    Location
    Tallahassee, FL
    Posts
    6,217
    Post Likes
    Quote Originally Posted by jpsmith1cm View Post
    Wouldn't the suction drop off almost as rapidly as the head pressure?
    was that rhetorical? Yes it does with a piston system....maybe not so much with TXV.

  10. #10
    Join Date
    Sep 2008
    Location
    Western PA
    Posts
    26,677
    Post Likes
    The OP's question was about a cap tube system. Effectively a fixed metering device.

    Not entirely rhetorical, just trying to evoke thought.

    BT said that flow rate drops as head pressure drops, but the suction pressure is going to drop, too, so does the flow rate really change significantly?



  11. #11
    Join Date
    Feb 2009
    Location
    Tallahassee, FL
    Posts
    6,217
    Post Likes
    He asked if superheat would increase and that is a definate Yes.

    I also see your point to get us thinking the logical way while working with fixed bore systems.

    Both sides act together equally.

  12. #12
    Join Date
    Jan 2004
    Location
    PA
    Posts
    77,677
    Post Likes
    Quote Originally Posted by jpsmith1cm View Post
    The OP's question was about a cap tube system. Effectively a fixed metering device.

    Not entirely rhetorical, just trying to evoke thought.

    BT said that flow rate drops as head pressure drops, but the suction pressure is going to drop, too, so does the flow rate really change significantly?
    Yes it does.

    The vapor pressure dropping, means the compressor is not able to draw as much refrigerant back. So flow rate has/does drop significantly. Which is why the SH increases.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  13. #13
    Join Date
    Mar 2007
    Location
    In the Conservatory with a Lead Pipe
    Posts
    15,679
    Post Likes
    Quote Originally Posted by jpsmith1cm View Post
    The OP's question was about a cap tube system. Effectively a fixed metering device.

    Not entirely rhetorical, just trying to evoke thought.

    BT said that flow rate drops as head pressure drops, but the suction pressure is going to drop, too, so does the flow rate really change significantly?
    Yes its fixed AND yes its a metering device. Not simple at all IMO
    A cap tube running refrigerant is in no way like a hose with water.
    The flow rate will increase with more subcooling but is counteracted by the lower pressure in the system. There are two phases of refrigerant at a point in a cap tube and flow is slowed at this point. If I had to guess if the SH will change really depends how the system is designed. One system maybe another maybe not.