    desuperheater fitting for water heater tanks

    Where is the heck can I find these, they screw right in where the drain for the water heater is, has a chunk of 1/2 copper that goes inside the 3/4, then has an inlet/outlet and drain. Some of you may know what Im talking about. For Geo systems...

    Local parts guys have no idea what Im talking about. Also, these things plug up pretty quick dont they...
    You picked a fine time to leave me loose wheel...

    http://rapalaguy.spaces.live.com/

  2. #2
    Join Date
    Apr 2007
    Location
    Portland, OR
    Posts
    92
    Post Likes
    They plug up REAL quick. Every time. Stopped using them.

  3. #3
    Join Date
    Jun 2002
    Location
    Bemidji, Mn
    Posts
    3,573
    Post Likes
    Thread Starter
    Thats what I was thinking, the water has very little clearance. I "made" one since I wasnt able to find one, it works!
    You picked a fine time to leave me loose wheel...

    http://rapalaguy.spaces.live.com/

  4. #4
    Join Date
    Sep 2008
    Location
    Central Florida
    Posts
    40
    Post Likes
    You are referring to what's known as a "coaxial fitting". As hvacguy said, if you have very hard water in your area they will get clogged up easily.

  5. #5
    Join Date
    Jun 2009
    Location
    New Haven,MO
    Posts
    34
    Post Likes
    Have to agree the coaxial method just leeds to maintenance problems if the water has any impurities. We quit piping that way a few years ago. Our manufacturer still shows piping it coaxial in there literature.

  6. #6
    Join Date
    Sep 2008
    Location
    Central Florida
    Posts
    40
    Post Likes
    The best thing to do is buy a larger solar tank. Look for tanks designed for open loop solar applications. They will have 5 ports on the top and 3 dip tubes. You usually get more mileage out of a bigger tank when hooked up to a desuperheater because you can store the heat longer and not depend on the electric resistance elements in the heater so much. Disconnect the lower element to so that it's not firing when the desuperheater is working.

  7. #7
    Join Date
    Dec 2011
    Location
    USA
    Posts
    67
    Post Likes
    Talk to the parts supply house about a water cooled condenser. It will hold up well with lime build up for a few years.

  8. #8
    Join Date
    Sep 2008
    Location
    Central Florida
    Posts
    40
    Post Likes
    The main issue with them liming up is that when they draw water through a coaxial fitting at the bottom of the tank they picku sediment in the bottom of the tank. This sediment then clogs the desuperheaters smaller water passages. This is not an issue when hooked up to a tank with 2 extra dip tubes that are cut 6" from the tank bottom.

    Its pretty sillly to hook them up to a standard water heater from both an efficiency and reliability point of view.

  9. #9
    Join Date
    May 2012
    Posts
    26
    Post Likes
    we use the t&P port on the top with a 3/4 brass nipple to a brass tee, then pull the drain out ant use a 3/4 brass nipple and tee there too it has never given us problems

  10. #10
    Join Date
    Oct 2012
    Location
    New Hampshire
    Posts
    18
    Post Likes
    We no longer use coaxial fittings as well. I'm not sure what water heater you are using or if this will help but here's a photo of the desuperheater piping using a Vaughn.



    Ill also try to drum up some different diagrams that could assist you in a different method of piping without need of a coaxial.

  11. #11
    Join Date
    Feb 2009
    Location
    Portland OR
    Posts
    2,620
    Post Likes
    We always use a 50 gallon desuperheater storage tank before going into the water tank and have had no issues with this so far and from what I can tell is the most efficient. Plus we dont' need to use that silly 4 way fitting that plugs up, we just push the water back in through the drain at the bottom and pull out of the cold water inlet in the top.

    Then again, in Oregon we are required by law to hire a plumber and pull a permit for anything beyond two nipples and two 18" water flex lines so my plumber brings the fittings he needs.
    Attached Images Attached Images  
    Check out my YouTube channel - http://www.youtube.com/user/skyheating1 We have customer testimonials, product reviews and more!
    Like us on FACEBOOK if you like our advice here!

  12. #12
    Join Date
    Oct 2012
    Location
    New Hampshire
    Posts
    18
    Post Likes
    Quote Originally Posted by SkyHeating View Post
    Then again, in Oregon we are required by law to hire a plumber and pull a permit for anything beyond two nipples and two 18" water flex lines so my plumber brings the fittings he needs.
    Same issue with plumbing in Mass, then head over the border to here in NH and were allowed to do the piping ourselves.

  13. #13
    Join Date
    Aug 2010
    Location
    iowa
    Posts
    47
    Post Likes
    We pull off of the cold water inlet, pipe it to the desuperheater, and then pipe it back to the bottom of the waterheater using a 3/4inch brass T with a boiler drain on the opposite side.

  14. #14
    Join Date
    Feb 2016
    Posts
    1
    Post Likes

    Hmm Hot Water Generator taking heat from my Hot Water Tank?

    Hello

    I live in Ontario Canada. (hopefully that's a good start to my thread HA HA)

    I researched on this forum about HWG (hot water generators) and the proper plumbing into a single electric hot water tank.

    I purchased a 10 year old home with a 2005 model Climate Master GSV 060 (5 ton) geothermal unit with HWG. I have owned the home for 2 months and noticed a SUBSTANTIAL amount of electricity consumption. Last month (30 days) 3528 Kw/h. Yep, in Ontario Canada $0.21 per Kw (tax included) equates to $740.00 for the 30 day period. Yeah WOW.

    So, we have no gas what so ever in our area. Geothermal Closed Loop system. Yesterday I conducted an experiment to shut down my hot water tank for 6 hours. It is a 80 Gallon REHEEM unit. I have no bunker (secondary tank). My energy consumption dropped in 1/2 for this period compared to the last 60 days. Here is my concern, I think my HWG is plumbed incorrectly to the HWT. I wanted to enter a picture but cannot figure out how so I will try to explain it. Two lines run from the HWG. (in / out). These two orange lines run into a four way T on the bottom of the tank. One is a drain, the other goes into the tank. Does this not create a vacuum drawing the pre-heated hot water from the tank back into the HWG of the geothermal unit?

    Another little note: on the hot output (on top of the tank) is a circulation pump which circulates the hot water throughout the large home to acquire on demand hot water at the faucets. It's 1/25 HP less than 25W.

    Any specialists that can help me on this would be VERY appreciated. I was told I cannot just close the valves on the bottom of the tank because the HWG pump needs constant circulation. Although, could I just disable the HWG pump and then turn off the valves if in fact this is why all my energy is being drawn from the Hot Water Tank?

    Please help!

  15. #15
    Join Date
    Dec 2012
    Location
    Lancaster County, Pennsylvania
    Posts
    101
    Post Likes
    Quote Originally Posted by parabrush View Post
    Hello <snip>

    I researched on this forum about HWG (hot water generators) and the proper plumbing into a single electric hot water tank.

    I purchased a 10 year old home with a 2005 model Climate Master GSV 060 (5 ton) geothermal unit with HWG. <snip>

    <snip> Two lines run from the HWG. (in / out). These two orange lines run into a four way T on the bottom of the tank. One is a drain, the other goes into the tank. Does this not create a vacuum drawing the pre-heated hot water from the tank back into the HWG of the geothermal unit?

    Another little note: on the hot output (on top of the tank) is a circulation pump which circulates the hot water throughout the large home to acquire on demand hot water at the faucets. It's 1/25 HP less than 25W.

    Any specialists that can help me on this would be VERY appreciated. I was told I cannot just close the valves on the bottom of the tank because the HWG pump needs constant circulation. Although, could I just disable the HWG pump and then turn off the valves if in fact this is why all my energy is being drawn from the Hot Water Tank?

    Please help!
    First off, if the HWG in/out lines go to two of the 4 ports on a 4-way cross at the bottom of the tank it would just be a short circuit and very little would be done to help your domestic hot water. Doesn't go through the tank at all. If that domestic circulation pump is plumbed in down at that 4-way I would need to see a diagram and I could be barking up the wrong tree. I also don't like a HWG without a "bunker" tank. The electric elements are going to hold the temperature and you gain very little to nothing unless you have a HW demand while the geo is running. And that requires them to be plumbed in correctly!

    The inlet to your HWG should be plumbed to a Tee at the cold inlet to your domestic HW tank. ClimateMaster wants the outlet to go into a Tee installed at the tank drain fitting. Since we have always installed our geothermal systems with a non-electrified water heater (bunker) ahead of the electric water heater, instead of the Tee at the drain fitting (hate the tripper it makes) I remove the lower element and return the output of the HWG into that opening. Drain runs cold even with the geo system operating but it looks a bit odd to the uninitiated with a hole cut into the bottom element cover and a pipe going in.

    To me, HWGs don't make much sense when the system is running for heating. They make the most sense in AC. You better have a really hefty ground loop with a lot of capacity designed for both space and domestic water heating. Around here the HWG isn't often taken into account when designing the ground loop.

    Hope that helps.

    EPM

  16. #16
    Join Date
    Jun 2013
    Location
    NORTHERN
    Posts
    1,262
    Post Likes
    these aforementioned 4-way T's for recirc in HW tank drain ports, - in one port have fowled in nearly every one of seen installed since the 1980's.

    The PEX tube installers' flood-baths in folks homes are less pretty than where plugged at the 4-way.
    Process cooling: NO COMPRESSORS- just simply Earth-Coupled since 1996
    ... still needs to be hybridized with Earth-loop GTX for energy transfer/ chillin' /or thawin'

    Perhaps you need a 22f Chiller/HW-Heat-Reclaim: buy a GEO-T Heat Pump (GTHP with Heat-Recovery)
    http://www.energystar.gov/index.cfm?...mal_heat_pumps

    http://www.hydro-temp.com/products.html and Bosch/Carrier/WF DHW while Cooling/Chilling

  17. #17
    Join Date
    Jun 2013
    Location
    NORTHERN
    Posts
    1,262
    Post Likes
    PEX has not held up to the convected HW able to hit 170f RARELY when a circ pump is off and a GHP desuperheater is below a cold fluid in a tank, forcing slow , sometimes over-heated pressurized hot water to pop-off the PEX at the inlet to the GHP ( reversed heat migration, likely during restricted air flow/ blower-failing to wipe off heat/ etc).
    Process cooling: NO COMPRESSORS- just simply Earth-Coupled since 1996
    ... still needs to be hybridized with Earth-loop GTX for energy transfer/ chillin' /or thawin'

    Perhaps you need a 22f Chiller/HW-Heat-Reclaim: buy a GEO-T Heat Pump (GTHP with Heat-Recovery)
    http://www.energystar.gov/index.cfm?...mal_heat_pumps

    http://www.hydro-temp.com/products.html and Bosch/Carrier/WF DHW while Cooling/Chilling

  18. #18
    Join Date
    Nov 2016
    Location
    Huntsville, Alabama
    Posts
    952
    Post Likes
    @ Hawkeyehvac Just curious based on my solar hot water experience why you wouldn't draw cold water from the bottom of the water heater, heat it in the desuperheater and then return it to the top of the tank where the warm water is? Stratification is your friend.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •