Page 1 of 2 12 LastLast
Results 1 to 13 of 16
  1. #1
    Join Date
    Dec 2003
    Posts
    20
    Post Likes

    What is Subcooling?

    What is subcooling and what affects the range in degrees on the suction side?

    Little confusing in relation to Superheat?


    Tia

    Thanks In Advance

  2. #2
    Join Date
    Aug 2009
    Location
    Riyadh Saudi Arabia
    Posts
    2
    Post Likes
    sub-cooling (liquid line) down---- super-heating (suction line) up

    suggested reading:

    http://www.bacharach-training.com/norm/superheat.htm
    Last edited by grismangki; 08-10-2009 at 03:59 AM.

  3. #3
    Join Date
    Jul 2006
    Posts
    6,628
    Post Likes
    It is the amount of heat removed from a refrigerant after it has already condensed to a liquid.
    You sure are cocky for a starving pilgrim.

  4. #4
    Join Date
    Apr 2006
    Location
    Parma, OH
    Posts
    520
    Post Likes
    See this article for additional information.

    http://contractingbusiness.com/service/cb_imp_44702
    Terry McIver, Content Director, ContractingBusiness.com magazine.

  5. #5
    Join Date
    Aug 2007
    Location
    Winter Haven, FL
    Posts
    4,383
    Post Likes
    Subcooling is when heat is removed from a substance. Superheat is when heat is added.

  6. #6
    Join Date
    Nov 2005
    Location
    Haymarket VA
    Posts
    643
    Post Likes
    Quote Originally Posted by Joe Harper View Post
    Subcooling is when heat is removed from a substance. Superheat is when heat is added.
    Joe got one more vote

  7. #7
    Join Date
    Sep 2009
    Location
    Texas
    Posts
    4
    Post Likes
    Subcooling is done in the condenser, the refrig. enters the condenser tubing as a heated vapor, as it travels through the coils of the condenser the fan removes the heat and at the last few turns of the condenser coils it has removed enough heat to turn the vapor into a liquid refrig. again. To measure the subcooling you need to put temp. probe right before the metering device, typically the only time you need the subcool is if you are running a TXV metering device. Since it regulates the refrig. it controls the superheat and so when you put your gauge on the high side and lets say your temp. is 110/225psig (R-22) and your probe reads 100 then you have a subcool of 10 which is a good subcool. Buckey4ds

  8. #8
    Join Date
    Dec 2004
    Location
    Brooklyn, New York
    Posts
    170
    Post Likes

    Thumbs up

    Subcooling is the new Ice treat from Subway Restaurants. Eat Fresh!!

  9. #9
    Join Date
    Sep 2002
    Posts
    27,376
    Post Likes

    Let's clarify that Joe -

    Subcooling results when heat is removed from a previously condensed substance.

    Superheat results when heat is added to a previously vaporized substance.

    PHM
    --------



    Quote Originally Posted by Joe Harper View Post
    Subcooling is when heat is removed from a substance. Superheat is when heat is added.
    PHM
    --------
    The conventional view serves to protect us from the painful job of thinking.

  10. #10
    Join Date
    Aug 2019
    Location
    Cincinnati Ohio
    Posts
    9
    Post Likes
    I am glad someone posted this question. One of those "I didn't know who to ask." questions. A little too busy running my business most times to thank about it but I am glad i found this!!
    Last edited by Dad; 11-16-2019 at 11:15 AM.

  11. #11
    Join Date
    Mar 2015
    Location
    Medford, N.Y.
    Posts
    6,627
    Post Likes
    Quote Originally Posted by buckey4ds View Post
    Subcooling is done in the condenser, the refrig. enters the condenser tubing as a heated vapor, as it travels through the coils of the condenser the fan removes the heat and at the last few turns of the condenser coils it has removed enough heat to turn the vapor into a liquid refrig. again. To measure the subcooling you need to put temp. probe right before the metering device, typically the only time you need the subcool is if you are running a TXV metering device. Since it regulates the refrig. it controls the superheat and so when you put your gauge on the high side and lets say your temp. is 110/225psig (R-22) and your probe reads 100 then you have a subcool of 10 which is a good subcool. Buckey4ds
    Does that mean ALL other metering devices need not worry about SubCooling?

  12. #12
    Join Date
    May 2014
    Location
    Bay Area California
    Posts
    26,546
    Post Likes
    You do realize you are responding to a post that is ten years old, right?


    Quote Originally Posted by TechmanTerry View Post
    Does that mean ALL other metering devices need not worry about SubCooling?
    I do a triple evac with nitro to remove non condensables.

  13. #13
    Join Date
    Mar 2015
    Location
    Medford, N.Y.
    Posts
    6,627
    Post Likes
    Quote Originally Posted by BBeerme View Post
    You do realize you are responding to a post that is ten years old, right?
    NO! I do now!! LOL,Tks

Page 1 of 2 12 LastLast

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •  
Contracting Business
HPAC Engineering
EC&M
CONTRACTOR