maybe this question should be directed to supco but,
anybody using supco's cap tubes..
my question to you,
aft18c1e-iaa-201 copeland compressor.(extended medium).
at (-)10* evap it's rated 1610 btuh.
this is used in a traulsen two door low boy freezer. ULT48-LR.
traulsen tech support as expectedly can not provide HP information that I would need to size a supco cap tube.
I ordered the cap tube from the oem since I didn't want to take chance on this fairly new freezer.
if I were to take a chance I would size it to a 1/2 nominal HP compressor.
How would you go about it and why.
(I don't need a bashing for using supco's caps.I know all that...)
Since this is a fairly new system as you say, then I would assume that the compressor was still the original. Therefore I would go with the HP rating of the compressor. Then use that HP to size the cap tube along with the temp range and refrigerant type.
Since Copeland doesn't list many of their compressor's nominal horsepower ratings anymore, I look for the Copeland condensing unit where the compressor is used and apply that nominal HP rating to the Supco cap tube charts.
The AFT18C1E-IAA is used in the M4FL-0051-IAA condensing unit, so I take that as a 1/2 hp low-temp R404A application.
In this case, the Supco chart then tells me to use 29" of #2.
I really wish they would publish a chart based on evap temps and Btu/hr.
I don't know how to quote your words when you post it in that form.
let me try to remember the points you made.
yes they did give me the cap tube info,but I only keep supco's numbered cap tubes,I don't think they specify what they are,if they do I never noticed,I will check it..
as far as selection of cap tubes by horsepower info I didn't think that's a preferable way to do it to say the least.
i belive it on the back of the box it comes in or on a piece of paper it the box
you can punch that comp number into google and get the specs on it
http://www.emersonclimate.com/images...06DS-194R1.pdf
ive found a little difference in what the manufacturer recomends
and what Supco chart states. Most told me to go with Supco,
If you want to be cynical about i, They say sometimes the
Manufactures Size is Designed to Fail. Better for profits, ya know.
Some say the Supco chart gets real close, sometimes you may
need to cut off a couple inches if your discharge is running a
little hot.
The average person has one testicle, and one ovary.
and another fella gave me this calculator
http://www.danfoss.com/United_Kingdo...ils/DanCap.htm
it uses btu's and temps
The average person has one testicle, and one ovary.
I prefer JB cap tubes. They seem to come in standard sizes(I.D.)that I see alot. Supco seems to have the odd sizes. I keep a 100' roll of JB .036 &
.042 I run into those sizes more than any other. JB also has a descent sizing chart.
I love the smell of phosgene first thing in the morning:
To apply for professional membership click here
Educational forums are open.
If you would like to submit a link or an article or other related info to the EF. click here
Here's a page from the Educational Forums with working link for the Danfoss cap tube program:
http://hvac-talk.com/vbb/showthread.php?t=219602