    Trane Rollout Switch Inducer Issue

    S9X2's different sizes all installed horizontally with very short runs to concentric intake/exhaust. Units are failing on rollout switch trip (manual switch E04). Problem only happens in low fire. Checked hx vacuum in low fire and got -0.9 IWC. Don't know what it should be, but it definitely should be higher than that. Pressure switch that runs to condensate drain is listed as -1.0 IWC, and unit did fail once and throw that code (E09). Trane came out and replaced a few items on the first unit with no success, then finally fixed it by "adjusting the board to increase inducer speed in low fire." Looks like they will have to come do it again. Frustrating part is the issue takes about 20 minutes of running in low fire to present itself. I feel like with 2 out of the five units in this new building showing the failure after one month of service it may occur in the other three as well.

    Question: Has anyone else run into this and is their a bulletin on how to speed up the inducer without going through Trane?
    "If you've eliminated all other possibilities whatever remains must be the truth."

  2. #2
    Join Date
    Jan 2008
    Location
    LEHIGH VALLEY, PA
    Posts
    858
    Post Likes
    Disconnect the low speed connection of the inducer motor, wire high and low fire signal to the high speed connection of the inducer . So what ever the call inducer runs in high speed ?.

  3. #3
    Join Date
    Nov 2004
    Location
    Northern Calif
    Posts
    1,005
    Post Likes
    Double check the flue runs, make sure they meet minimum requirements, I would jump w1 and w2 together, get the installation company involved.
    I'm not young enough, to know everything...

  4. #4
    Join Date
    Feb 2013
    Location
    Lamar, SC
    Posts
    848
    Post Likes
    Thread Starter
    "Disconnect the low speed connection of the inducer motor, wire high and low fire signal to the high speed connection of the inducer . So what ever the call inducer runs in high speed ?."
    I would never alter a furnace like that, too much liability for me. I wouldn't want to do what Trane did to the first one without some literature from the manufacturer to back it up.

    "Double check the flue runs, make sure they meet minimum requirements, I would jump w1 and w2 together, get the installation company involved."
    My company installed it, LOL. The lead quit right about the time I started. The install is not even close to perfect, but it doesn't have any issues that should cause this. Flue looks good and install has been gone over with a fine tooth comb by two Trane techs, trying to find a way to blame the install. Consensus was inadequate draft on low fire from everyone involved and speeding up the inducer was the solution. These units are too smart to jump w1 and w2, I think they use other inputs as well to decide what level they will heat on.
    "If you've eliminated all other possibilities whatever remains must be the truth."

  5. #5
    Join Date
    Nov 2004
    Location
    Northern Calif
    Posts
    1,005
    Post Likes
    Have you pulled one of the draft inducer assembly’s yet? Possible bad seal on chamber or factory debris? Just throwing out some ideas, as you’ve exhausted most of the obvious things.
    I'm not young enough, to know everything...

  6. #6
    Join Date
    Mar 2018
    Location
    Canada
    Posts
    257
    Post Likes
    Is condensate getting backed up in the combustion hx and associated parts? I would check the pitch of the intake/exhaust and drainage. How is the airflow through the air-side of the system?

  7. #7
    Join Date
    Feb 2013
    Location
    Lamar, SC
    Posts
    848
    Post Likes
    Thread Starter
    I appreciate the ideas, but troubleshooting is complete, the issue has been found and it has already been corrected on one unit. I just wanted to know if it was something I could perform myself, or something Trane is keeping to themselves.
    "If you've eliminated all other possibilities whatever remains must be the truth."

  8. #8
    Join Date
    Jul 2007
    Location
    Virginia
    Posts
    19,249
    Post Likes
    Quote Originally Posted by jmsmars1 View Post
    Trane came out and replaced a few items on the first unit with no success, then finally fixed it by "adjusting the board to increase inducer speed in low fire."
    Quote Originally Posted by jmsmars1 View Post
    I just wanted to know if it was something I could perform myself, or something Trane is keeping to themselves.
    I am not aware of any "Service Bulletin's" on this issue, but there may a "Confidential Service Alert" that I am not aware of.

    Can't you contact the Trane Rep who came out and ask what he did that is an acceptable practice for other units you come across?

    If you find out what he did, please post the procedure in the "PRO" forum.
    Instead of learning the tricks of the trade, learn the trade.

  9. #9
    Join Date
    Feb 2013
    Location
    Lamar, SC
    Posts
    848
    Post Likes
    Thread Starter
    Quote Originally Posted by rundawg View Post
    I am not aware of any "Service Bulletin's" on this issue, but there may a "Confidential Service Alert" that I am not aware of.

    Can't you contact the Trane Rep who came out and ask what he did that is an acceptable practice for other units you come across?

    If you find out what he did, please post the procedure in the "PRO" forum.
    Information doesn't flow that freely around here. I didn't even know the first unit had been fixed until I was sent out to look at the second one and called in the diagnosis that it was doing the same thing. My boss told me they went into the board and did something to speed it up. I asked how they did that since it looks like a simple two-speed shaded pole motor and he said he did not know, just that is what they said. I asked the dispatcher to see what they would say and do not expect a reply. Like I said communication is crap around here.
    "If you've eliminated all other possibilities whatever remains must be the truth."

  10. #10
    Join Date
    Dec 2005
    Location
    Cincinnati, Oh
    Posts
    11,829
    Post Likes
    Did they perhaps reduce from a 3in to 2in horizontally?

  11. #11
    Join Date
    Feb 2013
    Location
    Lamar, SC
    Posts
    848
    Post Likes
    Thread Starter
    Quote Originally Posted by hvacvegas View Post
    Did they perhaps reduce from a 3in to 2in horizontally?
    2in furnace to 3inch concentric, installed by the book. About 7 feet actual, 20 feet equivalent.
    "If you've eliminated all other possibilities whatever remains must be the truth."

  12. #12
    Join Date
    Aug 2009
    Location
    Beatrice, NE
    Posts
    22,115
    Post Likes
    Dig into the install manual and look close at the vent instructions. A couple things come to mind. One is they always say don't mix sizes. I wouldn't think that would include the termination but it may. But the other part where that concentric could play a part is there was an issue with not enough restriction on the intake especially on single pipe systems. It was required to add several feet of pipe and at least 2 90's. That sounds like more restriction than you have with the 3" concentric & 7' of pipe.

  13. #13
    Join Date
    Dec 2005
    Location
    Cincinnati, Oh
    Posts
    11,829
    Post Likes
    Quote Originally Posted by jmsmars1 View Post
    2in furnace to 3inch concentric, installed by the book. About 7 feet actual, 20 feet equivalent.
    How is the reducer that goes from 3in to 2 in oriented.
    Is the reducer concentric or ecentric

  14. #14
    Join Date
    Feb 2013
    Location
    Lamar, SC
    Posts
    848
    Post Likes
    Thread Starter
    Quote Originally Posted by BNME8EZ View Post
    Dig into the install manual and look close at the vent instructions. A couple things come to mind. One is they always say don't mix sizes. I wouldn't think that would include the termination but it may. But the other part where that concentric could play a part is there was an issue with not enough restriction on the intake especially on single pipe systems. It was required to add several feet of pipe and at least 2 90's. That sounds like more restriction than you have with the 3" concentric & 7' of pipe.
    It does have a few 90s and exceeds the 15 equivalent requirement in the install manual.
    "If you've eliminated all other possibilities whatever remains must be the truth."

  15. #15
    Join Date
    Feb 2013
    Location
    Lamar, SC
    Posts
    848
    Post Likes
    Thread Starter
    Quote Originally Posted by hvacvegas View Post
    How is the reducer that goes from 3in to 2 in oriented.
    Is the reducer concentric or ecentric
    eccentric horizontal about 2 feet from the furnace. cannot remember if it is flat on top or bottom. I know the manual mentions it should be a certain way and without going back I cannot say right now if it is or isn't.
    "If you've eliminated all other possibilities whatever remains must be the truth."

  16. #16
    Join Date
    Dec 2005
    Location
    Cincinnati, Oh
    Posts
    11,829
    Post Likes
    Quote Originally Posted by jmsmars1 View Post
    eccentric horizontal about 2 feet from the furnace. cannot remember if it is flat on top or bottom. I know the manual mentions it should be a certain way and without going back I cannot say right now if it is or isn't.
    If it's the wrong way you get waves in the condensate that's stuck in the flue and can cause issues. Should be flat on bottom.

  17. #17
    Join Date
    Feb 2013
    Location
    Lamar, SC
    Posts
    848
    Post Likes
    Thread Starter
    Quote Originally Posted by hvacvegas View Post
    If it's the wrong way you get waves in the condensate that's stuck in the flue and can cause issues. Should be flat on bottom.
    If I ever get sent back out there I will take a look at it, thanks for the tip.
    "If you've eliminated all other possibilities whatever remains must be the truth."

  18. #18
    Join Date
    Jun 2001
    Location
    San Diego, CA
    Posts
    1,265
    Post Likes
    opening of concentric installed into the direction of the prevailing winds? I can't recall an issue like this in the past. just throwing an idea out there

  19. #19
    Join Date
    Feb 2013
    Location
    Lamar, SC
    Posts
    848
    Post Likes
    Thread Starter
    Quote Originally Posted by gbfromsd View Post
    opening of concentric installed into the direction of the prevailing winds? I can't recall an issue like this in the past. just throwing an idea out there
    vertical
    "If you've eliminated all other possibilities whatever remains must be the truth."

  20. #20
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    14,048
    Post Likes
    there has to be some sort of Altitude adjustement they messed with

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •