I have a 2 ton Heat Pump paired with 15kW of electric heating. Manual J shows 10kW total required in the winter. The extra 5kW was installed as emergency heat and for when the outdoor temps drop below design.
My air handler specifies a minimum of 875 cfm for 10kW strips and 1050 cfm for 15kW. Unfortunately, my options with the multi speed fan are 880 cfm or 1385 cfm at 0.5” wc. The high speed definitely makes a lot of noise and I’m concerned about it overloading the ductwork or tripping out the fan on high static (it has never done this yet). It’s also noisy and doesn’t heat evenly at that high speed.
Would it hurt the system to run the full 15kW at the lower 880 cfm? Or is the 1050 cfm suggested a hard minimum? I do not want to make the system cycle on the thermal limit switches (they are 150F-50)
For reference, the air handler is a Goodman ASPT29B14.