Thread: Compressor super heat problem 0*f super heat

  1. #1
    Join Date
    May 2005
    Posts
    1,771
    Post Likes

    Compressor super heat problem 0*f super heat

    System ran it’s self out of Freon, I repaired the leak and added 134a back in to a full sight glass
    Case is a open deli case (hussman) old..

    Was setting super heat, started at a 17*f suction temp and a suction psi of 17psi

    Closed the txt until it was closed, compressor super heat didn’t change...I can’t take the super heat at the
    Txv.

    If the txt failed would if fail open or closed?? I had 80psi head and 17psi suction
    Let's give nukes a chance.

  2. #2
    Join Date
    Mar 2018
    Location
    Virginia
    Posts
    5,120
    Post Likes

    Compressor super heat problem 0*f super heat

    When you closed the txv all the way what did your pressures do?

    Also what’s the condition of the evap coil and is it clean?
    "I think Quantum tunneling would work great... "

    "Call a technician for God's sake. Or we'll see you on the news or the Dark Side of the Moon."

  3. #3
    Join Date
    May 2005
    Posts
    1,771
    Post Likes
    Thread Starter
    PSI never changed I can’t see the evap..there’s 6” between the top of

    the unit and the ceiling

    The suction temp never went to anything but 17* I need like 38*
    Let's give nukes a chance.

  4. #4
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,726
    Post Likes
    Open case check air flow.
    As far as not adjusting change the power head.

  5. Likes stumpdigger liked this post.
  6. #5
    Join Date
    May 2005
    Posts
    1,771
    Post Likes
    Thread Starter
    Have you seen how tight the head is on one off these?? I know the threads move when you tighten them
    I don’t have much room, i closed the valve And

    it still puts out Freon.. the seat may be bad
    Let's give nukes a chance.

  7. #6
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,726
    Post Likes
    You need to pump it down.

  8. #7
    Join Date
    May 2005
    Posts
    1,771
    Post Likes
    Thread Starter
    I know...
    Let's give nukes a chance.

  9. #8
    Join Date
    Jan 2010
    Location
    Sea to Sky
    Posts
    7,033
    Post Likes
    Does it have a heat exchanger piped in somewhere?

    Sent from my SM-G965W using Tapatalk

  10. Likes icemeister liked this post.
  11. #9
    Join Date
    May 2005
    Posts
    1,771
    Post Likes
    Thread Starter
    Yes I think so, it’s under the shelving..

    I have manually shut the txv down and there’s no change in the suction line temp, it’s too low

    I’m in calif, and leaving at 4am to get to my vendor to buy a new txv..a 3 1/2 hour drive..one way
    Let's give nukes a chance.

  12. #10
    Join Date
    Jan 2010
    Location
    Sea to Sky
    Posts
    7,033
    Post Likes
    If you have a heat exchanger and it fails, liquid refrigerant will go straight back into the compressor without going through the txv or evaporator.

    Sent from my SM-G965W using Tapatalk

  13. Likes icemeister, stumpdigger liked this post.
  14. #11
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    14,048
    Post Likes
    Im not sure that I would go after that TXV .... I cant ever remember a TXV that metered out of control , but ive seen plenty that didnt flow enough

    And whats up with 80 psi head ?

    I would ramp that head up to 160 psi and see what suction and SH does

    Turn off 1 of the cond fans , or if that unit only has 1 then cycle it by hand

    Im just wondering if the head pressure control has failed

    Im also trying to imagine a Heat Exchanger with a big enough leak to cause this ... has anyone seen a HX crack that big ?

  15. #12
    Join Date
    May 2005
    Posts
    1,771
    Post Likes
    Thread Starter
    Yes When I was a boy, I seen a exchanger that had leaked across..and I’m thinking it may of been this case I’m
    Working on right now, I didn’t go get the txv, BALloyd made the suggestion and I’m waiting for 9am to roll around.

    This unit has a headmaster control, so the fans run all the time, I will try disconnecting the fan, I placed a piece of cardboard
    In front of the coil, covered a 3rd of it and it had no affect, I also think I added way too much Freon to clear the sight glass

    The question that I cant find an answer to is can you manually shut the flow of Freon off by closing the txv manually..my suction temp 1 foot from the compressor stays
    At 17*f no matter where the txv is set
    Let's give nukes a chance.

  16. #13
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    14,048
    Post Likes
    Pump it down and torch receiver

  17. #14
    Join Date
    May 2005
    Posts
    1,771
    Post Likes
    Thread Starter
    Not following??
    Let's give nukes a chance.

  18. #15
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    14,048
    Post Likes
    Quote Originally Posted by primmers View Post
    I placed a piece of cardboard In front of the coil, covered a 3rd of it and it had no affect
    if its really chilly outside that will do very little , you have to cover the whole coil

    Whats ambient ? When its below 40 , Feel the inlet of the coil and see if its hot , It should be cold .... the Receiver should be nice and warm because the master is directing the gas to it

  19. #16
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    14,048
    Post Likes
    Quote Originally Posted by primmers View Post
    Not following??
    you think you may have added too much refrigerant ? so check the level by torching it

    Have you done this method ?

  20. #17
    Join Date
    May 2005
    Posts
    1,771
    Post Likes
    Thread Starter
    Ah, Ok..
    Ambient was 52*

    I’ll check it this morning two hours before they open.
    Let's give nukes a chance.

  21. #18
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    14,048
    Post Likes
    50 degrees it might be bypassing pretty well too ( if its working correctly ) alot will be shoved into the Receiver while "some" will be sent to the coil

    You have to get in there and be touchy feely ...

  22. Likes primmers liked this post.
  23. #19
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    14,048
    Post Likes
    So when you have this 0 deg SH is the suction line frosting up ? Is the compressor sounding like it has popcorn inside ?

  24. #20
    Join Date
    May 2005
    Posts
    1,771
    Post Likes
    Thread Starter
    Noeverything looks and sounds good except the 46* box temp and the 0* superheat at the compressor
    Let's give nukes a chance.

+ Reply to Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •