    New old furnace for the the garage

    The furnace and coil are not new, but the price was right. Did the entire duct system and attic finish as part of the project.

    AC yet to be installed - its cold out now.









    The relays are for my thermostat selector set up. I have a upstairs and downstairs thermostat to control the temp where I will be working. Each thermostat has a toggle switch nearby to force control from the thermostat I want.


    Sent from my iPhone using Tapatalk

  2. Likes Restaurant Mech, Lahrs, dieseldude liked this post.
  3. #2
    Join Date
    Dec 2004
    Location
    Chicago area
    Posts
    19,137
    Post Likes
    Thread Starter


    Supply elbow


    Sent from my iPhone using Tapatalk

  4. Likes GoCougs, UltraCool liked this post.
  5. #3
    Join Date
    Jan 2008
    Location
    New Jersey
    Posts
    464
    Post Likes
    Nice work, that is too nice to hide behind walls!

    Sent from my ASUS_P00J using Tapatalk

  6. Likes heatingman, STEVEusaPA liked this post.
  7. #4
    Join Date
    Dec 2002
    Location
    SouthEast NC ICW & Piedmont Foothills
    Posts
    8,494
    Post Likes
    Is conduit code requirement or personal preference?
    It`s better to be silent and thought the fool; than speak and remove all doubt.

  8. #5
    Join Date
    Feb 2016
    Location
    Louisburg Kansas
    Posts
    5,824
    Post Likes
    I can't think of anything to say but WHOOOOOOOOOWWWWWWWWWWWWWWWW!!!!!!!!!!!!!!!!!!!!!!! !!!!!!!!!!!!!!!!!
    No man can be both ignorant and free.
    Thomas Jefferson

  9. Likes heatingman liked this post.
  10. #6
    Join Date
    Dec 2004
    Location
    Chicago area
    Posts
    19,137
    Post Likes
    Thread Starter
    Quote Originally Posted by dandyme View Post
    Is conduit code requirement or personal preference?
    Personal preference. It is code in most of the Chicago Area, where I live and work, but the county were this home is, NM cable is allowed.

    But I prefer conduit on any installation I do, whether its required or not. I even run the low voltage in conduit most of the time.

    Its just easier down the road if a circuit needs to be added, or wire up sized for a bigger load. I also think it looks more professional.

    Sent from my SM-G930V using Tapatalk

  11. #7
    Join Date
    Dec 2004
    Location
    Chicago area
    Posts
    19,137
    Post Likes
    Thread Starter
    Also, I dont have a Pittsburg machine, so those are all hand done on the brake.

    Sent from my SM-G930V using Tapatalk

  12. #8
    Join Date
    Dec 2004
    Location
    Chicago area
    Posts
    19,137
    Post Likes
    Thread Starter
    Quote Originally Posted by dandyme View Post
    Is conduit code requirement or personal preference?




    This is the side without the ductwork, but I did pretty much the mirror image on the side with the ductwork.

    I think I ran about 200 ft of conduit in there.

    Could not decide if I wanted low outlets or high ones, so I did both.


    Sent from my iPhone using Tapatalk

  13. #9
    Join Date
    Jan 2010
    Posts
    45,372
    Post Likes
    I just can't put my finger on how the hell the a/c is going to work 🤔

  14. Likes heatingman, Gary Warren Jr liked this post.
  15. #10
    Join Date
    Dec 2004
    Location
    Chicago area
    Posts
    19,137
    Post Likes
    Thread Starter
    Just finished the trim plates for the flue and the supply into the storage area.




    Sent from my iPhone using Tapatalk

  16. Likes mo-flo liked this post.
  17. #11
    Join Date
    Jan 2010
    Posts
    45,372
    Post Likes
    Seriously though I know you'll get that resolved 😉
    Looks good shows your skills of this craft well.
    I think I remember your thread on making those square to round transitions but started getting a headache on the math.
    Go figure I now need some for a current project I'm doing. 22" and can't find any locally readily available.
    What's your turnaround time ? 😃

  18. Likes heatingman liked this post.
  19. #12
    Join Date
    Dec 2004
    Location
    Chicago area
    Posts
    19,137
    Post Likes
    Thread Starter
    Quote Originally Posted by VTP99 View Post
    Seriously though I know you'll get that resolved
    Looks good shows your skills of this craft well.
    I think I remember your thread on making those square to round transitions but started getting a headache on the math.
    Go figure I now need some for a current project I'm doing. 22" and can't find any locally readily available.
    What's your turnaround time ?
    I think I spent a little more then an hour making the square to round. Once I figured it out that is. Surely you could have one made at a fab shop. We have tinners at work, some may know how to make fittings, but they just call it all in to a fab shop.


    Sent from my iPhone using Tapatalk

  20. Likes VTP99 liked this post.
  21. #13
    Join Date
    Apr 2020
    Location
    Garner NC
    Posts
    10,834
    Post Likes
    you have some nice detail work behind it, good to see!.. it does not look far too out of design specs for something on the fly....

    a couple of questions though
    1) is heat going to work properly,i have seen that piping style for a 90% furnace..thats an 80% that i am aware of. so the exhaust opening has to be above the heat exchanger....that exhaust is on the bottom...
    2) the AH could have been easily laid down on its side with the coil on the left before the wall opening..with the exhaust going straight up..any reason you decided not to do it?

    3)if the fan is working currently..what is your static pressure .it would have been nice to see an inside insulated SA casket instead of the 90 with reduction after the turning vanes then going larger...are you going to wrap it all in FSK r-8 insulation, or going to take it apart and sleeve r-8 round flex insulation over it?

    4) I was always taught to keep the refrigeration coil on the return side,its easier to service and clean it, plus the heat can warp/distort the fins... is there a reason your coil is on the supply side especially with a gas furnace?

    5) if i remember correctly that AH can be converted to flip the blower to also help you with its design...if you do decide to change it

  22. Likes Gary Warren Jr liked this post.
  23. #14
    Join Date
    Sep 2007
    Location
    State College, PA
    Posts
    5,579
    Post Likes
    That is some awesome work!

    Don't see much metal ducting around here anymore.
    Can someone please explain to me -
    Why is there never enough time to do it right the first time, but plenty of time to do it twice?


    Please view site rules: http://hvac-talk.com/vbb/showthread.php?t=1241

    Apply for Pro Membership: http://hvac-talk.com/vbb/showthread.php?t=116113

  24. Likes heatingman liked this post.
  25. #15
    Join Date
    Dec 2004
    Location
    Chicago area
    Posts
    19,137
    Post Likes
    Thread Starter

    New old furnace for the the garage

    Quote Originally Posted by Unlimited1 View Post
    you have some nice detail work behind it, good to see!.. it does not look far too out of design specs for something on the fly....

    a couple of questions though
    1) is heat going to work properly,i have seen that piping style for a 90% furnace..thats an 80% that i am aware of. so the exhaust opening has to be above the heat exchanger....that exhaust is on the bottom...
    2) the AH could have been easily laid down on its side with the coil on the left before the wall opening..with the exhaust going straight up..any reason you decided not to do it?

    3)if the fan is working currently..what is your static pressure .it would have been nice to see an inside insulated SA casket instead of the 90 with reduction after the turning vanes then going larger...are you going to wrap it all in FSK r-8 insulation, or going to take it apart and sleeve r-8 round flex insulation over it?

    4) I was always taught to keep the refrigeration coil on the return side,its easier to service and clean it, plus the heat can warp/distort the fins... is there a reason your coil is on the supply side especially with a gas furnace?

    5) if i remember correctly that AH can be converted to flip the blower to also help you with its design...if you do decide to change it
    1 ) Furnace is multi-poise - any flow direction you want - upflow, downflow, left or right. Then you just rotate the flue elbow inside the furnace. Carrier 48CTA

    I assume thats what your talking about.

    Or that the flue goes horizontally before upward?

    2) furnace is upright for 2 reasons - The freebie evap coil is not made for horizontal, and 2 - horizontal layout would have wasted more floor space. The furnace is located in what will be a finished space (office/bonus space) I had thought about putting the furnace horizontal in the kneewall space, but the overall length of furnace, coil, supply and return plenum would have taken up over 1/2 the width of the garage, causing at least 1/2 the supply air having to double back the other direction, which would have wasted even more space and materials.

    3) Have not tested the static pressure. there is not a reduction after the supply elbow, but rather built into it. The design is essentially a standard return drop elbow - with turning vanes to help ease the air through fitting.

    If I had more height to work with, I would done it differently.

    4) evaporator coils always go on the outlet side of a gas heating furnace. Pretty sure thats in every manual. While RTU’s are often counter to that, they also have chronic HX failures because of it. If the evap coil was on the return side of the heater, you’ll be condensing water on the fireside of the HX.

    5) cant flip the blower, but the entire furnace can be rotated.


    Sent from my iPhone using Tapatalk

  26. #16
    Join Date
    Jan 2008
    Location
    LEHIGH VALLEY, PA
    Posts
    858
    Post Likes
    He is from Chicago , code there , I do some work at my daughters house there , everything in steel conduit .

  27. #17
    Join Date
    May 2004
    Location
    Salt Lake City/Tooele
    Posts
    9,679
    Post Likes
    That is a beautiful thing. There is just one thing I am wondering and that is the idea to conceal the din rail mounted relays in the return air? Why not installed in the furnace or in a hinged electrical control enclosure maybe a 12x12, etc. That is the geek in me, I like pretty control panels...Merry Xmas and great job!

  28. Likes heatingman, Gary Warren Jr liked this post.
  29. #18
    Join Date
    Dec 2004
    Location
    Chicago area
    Posts
    19,137
    Post Likes
    Thread Starter
    Quote Originally Posted by slctech View Post
    That is a beautiful thing. There is just one thing I am wondering and that is the idea to conceal the din rail mounted relays in the return air? Why not installed in the furnace or in a hinged electrical control enclosure maybe a 12x12, etc. That is the geek in me, I like pretty control panels...Merry Xmas and great job!
    Figured it would be easier to remove and clean the blower if the relays where not mounted there. If I had an enclosure I probably would have used one. But the filter door hinges open, so its sort of like a built in enclosure.


    Sent from my iPhone using Tapatalk

  30. #19
    Join Date
    May 2014
    Location
    Bay Area California
    Posts
    43,457
    Post Likes
    Nice work Mr. Heating Man !!
    I do a triple evac with nitro to remove non condensables.

  31. Likes heatingman liked this post.
  32. #20
    Join Date
    Apr 2020
    Location
    Garner NC
    Posts
    10,834
    Post Likes
    Quote Originally Posted by heatingman View Post
    1 ) Furnace is multi-poise - any flow direction you want - upflow, downflow, left or right. Then you just rotate the flue elbow inside the furnace. Carrier 48CTA

    I assume thats what your talking about.

    Or that the flue goes horizontally before upward?

    2) furnace is upright for 2 reasons - The freebie evap coil is not made for horizontal, and 2 - horizontal layout would have wasted more floor space. The furnace is located in what will be a finished space (office/bonus space) I had thought about putting the furnace horizontal in the kneewall space, but the overall length of furnace, coil, supply and return plenum would have taken up over 1/2 the width of the garage, causing at least 1/2 the supply air having to double back the other direction, which would have wasted even more space and materials.

    3) Have not tested the static pressure. there is not a reduction after the supply elbow, but rather built into it. The design is essentially a standard return drop elbow - with turning vanes to help ease the air through fitting.

    If I had more height to work with, I would done it differently.

    4) evaporator coils always go on the outlet side of a gas heating furnace. Pretty sure thats in every manual. While RTU’s are often counter to that, they also have chronic HX failures because of it. If the evap coil was on the return side of the heater, you’ll be condensing water on the fireside of the HX.

    5) cant flip the blower, but the entire furnace can be rotated.


    Sent from my iPhone using Tapatalk
    thank you for answering..

    its has been a very long time since i ever installed an 80%, a very long time....all newer ones for the last 12 years with 90% have the coil inside opposite of the furnace being an all in one unit... the ones that was not , design spec was 12" before the return, because all was horizontal install (with anti vibration hanging from the diagonal 2x10's) ...everything else is heat pumps by popular choice

    i have seen a few 90% with the evap coil directly above it with no way to properly clean the inside of the coil as maintenance...

    the package units HE have a bad design as the primary tubes dont pitch back to drain the condensate that causes it to rot internally, but i will see light seam rot first....I am in a much warmer climate so most heat exchanges last 7-10 years....

    the smooth tube bend heat exchanger last much longer than the ripple bend ones where i find the most amount of pinholes because the metal is stretched thin at those points
    Last edited by Unlimited1; 12-25-2020 at 10:08 PM.

+ Reply to Thread
Page 1 of 3 123 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •