Thread: My cooling towers are overflowing and need help

  1. #1
    Join Date
    Dec 2020
    Posts
    4
    Post Likes

    Exclamation My cooling towers are overflowing and need help

    I am from the UK and have 4 x cooling towers which overflow only when the pump turns off.
    I have isolated the make up to ensure that it is not a float valve issue, and i have also isolated the flow to the top of the towers to ensure the water doesnt 'backfill into the system should there be a failed NRV.
    me and my colleague drained down the towers to 2 inches below the overflow and once again when the pumps shut off they overflow.

    Could someone please steer me in the right direction?

    KR
    Shane

  2. #2
    Join Date
    Feb 2008
    Location
    Dubai
    Posts
    901
    Post Likes
    maybe the undersized equalizer line caused the overflowing. equalize line to be sized 15% more capacity of single tower flow rate. please check and update

  3. #3
    Join Date
    Apr 2020
    Location
    va
    Posts
    10,300
    Post Likes
    New or existing older job?
    How much of the condenser water piping is higher than the tower basin? Type tower, model? Iso?

  4. #4
    Join Date
    Dec 2020
    Posts
    3
    Post Likes
    Also check your chemicle treatment lines. I have had siphon effect thru the lines after pump is off and it would literally empty the supply to tower into basin after about 30 minutes.

  5. #5
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,739
    Post Likes
    Quote Originally Posted by RyanWAIDB7778 View Post
    Also check your chemicle treatment lines. I have had siphon effect thru the lines after pump is off and it would literally empty the supply to tower into basin after about 30 minutes.
    3/8" or even 1/2" chemical feed lines are going to take quite a while to move several hundreds of gals of water!

  6. #6
    Join Date
    Dec 2020
    Posts
    3
    Post Likes

    Tower

    Quote Originally Posted by pecmsg View Post
    3/8" or even 1/2" chemical feed lines are going to take quite a while to move several hundreds of gals of water!
    Didn't know how fast it was leaking back. Triple duty not checking? Or you're supply piping is above your tower inlet

  7. #7
    Join Date
    Mar 2017
    Location
    Arizona
    Posts
    277
    Post Likes
    I would look at the check valves


    Sent from my iPhone using Tapatalk

  8. Likes Unlimited1, pecmsg liked this post.
  9. #8
    Join Date
    Dec 2020
    Posts
    4
    Post Likes
    Thread Starter
    Quote Originally Posted by Chillertech4 View Post
    I would look at the check valves


    Sent from my iPhone using Tapatalk
    I isolated the main flow going over the top of the towers to 'simulate' a valve shutting as the pumps went off, the ponds still overflowed, not sure where the additional water would be coming from?

  10. #9
    Join Date
    Dec 2020
    Posts
    4
    Post Likes
    Thread Starter
    Quote Originally Posted by ehsx View Post
    New or existing older job?
    How much of the condenser water piping is higher than the tower basin? Type tower, model? Iso?
    The cooling towers are existing and probably over 15 years old, i have no O&M or schematics for the condenser water circuit, the Towers are EVAPCO LPT but i do not have the model number.
    In regards to the piping, the only pipes that are higher than the basin are the flow pipes going the spray nozzles, i initially thought it may be a failed check valve but to simulate this i isolated the flow valve just as my colleague turned the pumps off. and it still overflowed

  11. #10
    Join Date
    Dec 2020
    Posts
    4
    Post Likes
    Thread Starter
    Quote Originally Posted by RyanWAIDB7778 View Post
    Didn't know how fast it was leaking back. Triple duty not checking? Or you're supply piping is above your tower inlet
    The overflow ( 2") literally gushes out whenever the pumps shut off, our dosing system is located in the basement

  12. #11
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,739
    Post Likes
    Check valve in or out of the pump is leaking by.

  13. #12
    Join Date
    Feb 2016
    Location
    Louisburg Kansas
    Posts
    5,824
    Post Likes
    It's starting to sound like the your makeup water control is putting too much water in the basin. With the system running how high is the water level in the basin?
    No man can be both ignorant and free.
    Thomas Jefferson

  14. #13
    Join Date
    Aug 2019
    Location
    LA
    Posts
    170
    Post Likes
    There is a running level for towers listed in their manuals. Usually A buildings running level is too high to hold hot box water After shut down. Piping also can contribute if a long horizontal run also drains in to tower at shut down.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Tags for this Thread

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •