    vfd over voltage code

    i have a 40ton vfd automation direct gs34040 vfd. it has been in for 4 years no issues. its a 480 drive. 486/482/482 input voltage. it went in alarm sunday. i looked at today. it alarmed out if it went to 35 hz. i changed accel times and a few other parameters. It is on a dessicant dehumidifier. it mostly runs at 60 ate 486hz 365 days a year unless there is a power blip. it now will ramp up but alarms on decel even though i increased decel times. i was on phone with tech support for hours. They are not sure. it faults on dc bus over voltage . why do i have to change settings after 4 years. the blower is a centrifugal type fan no belts. motor seems smooth amps good. the dc buss is 748 at 60 hz but i calculate it should be 687. when it decels the bus voltage goes down according to screen but still trips out. any ideas.

  2. #2
    Join Date
    Mar 2016
    Location
    Dayton Oh
    Posts
    6,632
    Post Likes
    Can’t remember if mine was dc under or over but it was on a 30 horse motor for a tower fan. Book indicated to Meg the motor which we did and found it to be on its way out.

    Had another one that would blow one fuse of three. IR scan showed it was hot, and slightly higher amps then others. Motor checked out fine. Installed a line reactor and it took care of the situation.
    Looked like a big transformer but all it really does is clean up the electric signal.


    Sent from my iPhone using Tapatalk

  3. #3
    Join Date
    Apr 2020
    Location
    va
    Posts
    10,300
    Post Likes
    Line reactor is listed as an accessory. Do you have it?

    Line reactor:
    Increased reliability and life span of the VFD
    Provide some protection against over-voltage trips
    A cost-effective solution to reduce harmonic distortion
    Provide some buffering against voltage spikes

  4. #4
    Join Date
    Jan 2001
    Location
    Carlisle, Pa
    Posts
    945
    Post Likes
    Thread Starter
    no to reactor

  5. #5
    Join Date
    Mar 2018
    Posts
    138
    Post Likes
    The only time I ran into a DC buss over voltage was when a drive was trying to start an already spinning motor. That drive didn't have a catch option so I had it brake before starting. You can also get that error if the motor is spinning faster than the current drive speed. A building imbalance can cause that on fans.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •