    Microchannel coils

    I am at a facility which I’m guessing has 75% copper tube and fin (old school) coils and the rest of the 25% newer stuff being microchannel.

    We are experiencing a disproportionate amount of microchannel coil leaks compared to traditional coils.

    I’m aware of “U-bend leaks... and rubs... but on about 40 coil leaks, these microchannel coils are leaking in the middle, the factory header connections, etc.

    A few of our replaced microchannel coils have been leaking again, within weeks to months, probably 4 of them.

    Some of these are on chillers, some on AAON systems, some on walk in refrigerators and freezers, some on DX systems, some on VAV systems... the whole gambit.


    So, has anyone else had such bad luck with the new coils, or is it just me?

  2. #2
    Join Date
    Jan 2005
    Location
    Emerald Coast
    Posts
    1,640
    Post Likes
    .
    Sadly yes. It's a career opportunity.
    ..
    Do not attempt vast projects with
    half vast experience and ideas.
    ...

  3. Likes R600a liked this post.
  4. #3
    Join Date
    May 2018
    Location
    Central Florida
    Posts
    227
    Post Likes
    Thread Starter
    Got ya
    Last edited by 3.14; 12-15-2020 at 06:31 PM. Reason: Hmmm

  5. #4
    Join Date
    Apr 2010
    Location
    ... sitting in the Hollywood Hawaiian Hotel, listening to the air conditioner hum
    Posts
    1,208
    Post Likes
    Unless its something like a puncture wound on the outside that's easily seen and accessed, most MC coil leaks cannot be repaired. With those, you get some fins out of the way, clean it real good, and solder over with Muggy or Aluxcor or something similar. But almost anything else like a random spot in the middle at the top or if there are leaks at the copper to aluminum transition, is not likely to work.

    One I did about 5 years ago, the installers had put a hail guard screw right through the large thick tube that serves as the coil manifold. I thought that would be easy to solder over that hole. It turned out to be pretty difficult to get that huge piece of aluminum hot enough to work with.

    The great professors of the art are not immune from the malignancy of matter and the eternal cussedness of inanimate objects.

  6. #5
    Join Date
    May 2018
    Location
    Central Florida
    Posts
    227
    Post Likes
    Thread Starter
    Might have more to do with it being aluminum, than microchannel.

  7. #6
    Join Date
    Jan 2012
    Location
    Missouri, USA
    Posts
    3,963
    Post Likes
    Are they all tranes or daikin?

  8. #7
    Join Date
    May 2018
    Location
    Central Florida
    Posts
    227
    Post Likes
    Thread Starter
    No, all different varieties!

  9. #8
    Join Date
    Mar 2015
    Location
    Medford, N.Y.
    Posts
    10,203
    Post Likes
    Split systems on a pumpdown?

  10. #9
    Join Date
    Apr 2010
    Location
    ... sitting in the Hollywood Hawaiian Hotel, listening to the air conditioner hum
    Posts
    1,208
    Post Likes
    Quote Originally Posted by 3.14 View Post
    Might have more to do with it being aluminum, than microchannel.
    Correct, I assumed that was implied. I personally have never seen a MC coil that wasn't aluminum. Doesn't mean they couldn't exist, I guess.

    The great professors of the art are not immune from the malignancy of matter and the eternal cussedness of inanimate objects.

  11. #10
    Join Date
    Jan 2020
    Location
    Winnipeg Canada
    Posts
    2,507
    Post Likes
    The question is how are these coils being cleaned? And what's the air quality like?
    I've had trouble with some that had old school cleaning solvents used on.
    And I've also had trouble with some that were a few blocks from a foundry....

  12. #11
    Join Date
    May 2018
    Location
    Central Florida
    Posts
    227
    Post Likes
    Thread Starter
    Yes all the walk ins are split systems that pump down with no controller call.

  13. #12
    Join Date
    Apr 2020
    Location
    va
    Posts
    10,300
    Post Likes
    Verify the pumpdown capacity is at least 10% greater than the refrigerant charge. Check your liquid line solenoid location.
    Pumpdown capacity varies with the header & channel size. Some units cannot be pumped down and just use a drop out solenoid.


    Most of these coils come from China, with a good bit of mfg facility quality difference.

  14. #13
    Join Date
    Apr 2003
    Location
    Maple Grove, MN
    Posts
    5,136
    Post Likes
    Quote Originally Posted by ehsx View Post
    Verify the pumpdown capacity is at least 10% greater than the refrigerant charge. Check your liquid line solenoid location.
    Pumpdown capacity varies with the header & channel size. Some units cannot be pumped down and just use a drop out solenoid.


    Most of these coils come from China, with a good bit of mfg facility quality difference.
    I highly doubt over-charging has anything to do with pin-hole leaks. Have you ever worked on an outdoor refrigeration condenser? They are made to be pumped down, no matter if they have a micro channel coil or not, although I admit they are easy to over charge.

    Now to your theory about junk coming from China, you might be on to something. I assumed that most were made in the USA, but now that I think about it, they are something that would be easy to jam into a shipping container and float over here.

    Does anyone know if anyone actually manufactures micro-channel coils in the USA, or are they all really coming from China?
    If at First You Don't Succeed, Skydiving Is Not for You.

  15. #14
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,736
    Post Likes
    On the larger coils rigging is critical. Little to no Twisting, bending, racking during install.
    Smaller coils, 1 - 5 HP I've only seen 1 bad coil on a heatcraft condenser. (Installed by others)

  16. #15
    Join Date
    Apr 2020
    Location
    va
    Posts
    10,300
    Post Likes
    Quote Originally Posted by ammoniadog View Post
    I highly doubt over-charging has anything to do with pin-hole leaks. Have you ever worked on an outdoor refrigeration condenser? They are made to be pumped down, no matter if they have a micro channel coil or not, although I admit they are easy to over charge.

    Now to your theory about junk coming from China, you might be on to something. I assumed that most were made in the USA, but now that I think about it, they are something that would be easy to jam into a shipping container and float over here.

    Does anyone know if anyone actually manufactures micro-channel coils in the USA, or are they all really coming from China?
    Speaking from experience, commercial & chiller, mfg testing, design, warranty assessments, etc; pumpdown can be a major issue. Pin holes were not mentioned in the original post. Warranty Failures were reduced by ~80% when mfg switched Chinese providers.

  17. #16
    Join Date
    Apr 2020
    Location
    va
    Posts
    10,300
    Post Likes
    Mfg mandated coils within x distance of coast had epoxy coatings and recommended for locations with high moisture or corrosive atmosphere.
    Coil mounting/ isolation can also cause leaks due to vibration & corrosion.

  18. #17
    Join Date
    Jan 2010
    Posts
    45,372
    Post Likes
    .
    Attached Images Attached Images

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •