Page 1 of 2 12 LastLast
Results 1 to 20 of 21

Thread: Return air drop and static pressure

  1. #1
    Join Date
    Dec 2018
    Posts
    106
    Post Likes

    Return air drop and static pressure

    Hey guys, my home had a airflow specialist come and test the ductwork and make recommendations to the Hvac installer of the home. One recommendation done was to upgrade both supply and return trunks, the supply went from 16x8 and 12x8 to 20x8 and 16x8; the return went from 18x8 and 14x8 to 22x8 and 18x8.

    The return drop stayed 24x8 but the drop is no longer anywhere near the center of the 22x8 return. After this work was performed, the static pressure barely dropped, it went from 0.81 to 0.74” on high setting of a Goodman gmss96 60 btu furnace on a 1650’ 2 story.

    My question is this, would the return drop not being centered be creating a lot of turbulence? Because it’s clear that somethings keeping the static pressure high. Maximum for the furnace is 0.50”.

    Thanks
    Attached Images Attached Images   

  2. #2
    Join Date
    Dec 2007
    Posts
    13,231
    Post Likes
    Looks like you have a huge return and then it is all restricted into the actual drop.

    I am not sure where the increase in size is, but no matter what you increase before the drop, it will still be limited by the drop size.
    Also, the best airflow into that filter would be turning vanes or a radius, NOT that hard 90°!!
    The Food Stamp Program, administered by the U.S. Department of Agriculture, is proud to be distributing the greatest amount of free meals and stamps EVER.
    Meanwhile, the National Park Service, administered by the U.S. Department of the Interior, asks us to "Please Do Not Feed the Animals". Their stated reason for this policy "... the animals become dependent on handouts and will not learn to take care of themselves."
    from an excerpt by Paul Jacob in Sun City, AZ

  3. Likes kdean1 liked this post.
  4. #3
    Join Date
    Dec 2018
    Posts
    106
    Post Likes
    Thread Starter
    The drop is 24x8 so it’s larger than the 22x8 return. I agree and recommended an inner radius with turning vanes to the Hvac people. Do you think the offset drop is an issue? It seems that it may be a problem in my mind.

  5. #4
    Join Date
    Jan 2020
    Location
    Winnipeg Canada
    Posts
    2,507
    Post Likes
    I'd have done a really large transition where the drop comes off the return. Actually scratch that. If I was doing that much work already it would have gotten a much larger drop as well.
    Then with a nice big drop the furnace would be fed lot's of air.
    The funny thing is that for me return ductwork should always be slightly larger than supply. Air moves really well under positive pressure. It doesn't move all that well under negative pressure. So I avoid negative pressure at almost all costs

  6. #5
    Join Date
    Mar 2018
    Location
    Cottonwood, Ca #StateofJefferson
    Posts
    2,187
    Post Likes
    How much of that static is on the return side, how much on the supply? Return measured before or after filter and with filter installed and removed? Supply measured in between furnace and evap coil? Full model number of the furnace and evap coil?

  7. Likes R600a liked this post.
  8. #6
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Should be a radius ell at the furnace, and a transition at the 22x8 duct.

  9. Likes kdean1 liked this post.
  10. #7
    Join Date
    Nov 2006
    Location
    SE Ohio
    Posts
    12,905
    Post Likes
    OP, you have focused on size. Fittings and transitions are every bit as important as size. Your guys have neglected those.
    *********
    https://www.hvac20.com/ High efficiency equipment alone does not provide home comfort and efficiency. HVAC2.0 is a process for finding the real needs of the house and the occupants. Offer the customer a menu of work to address their problems and give them a probability of success.

    Find contractors with specialized training in combustion analysis, residential system performance, air flow, and duct optimization https://www.myhomecomfort.org/

  11. #8
    Join Date
    Dec 2018
    Posts
    106
    Post Likes
    Thread Starter
    0.41” return static on high. 0.20” pressure drop across coil. There’s lots of turbulence between filter and the 90 on the drop.

  12. #9
    Join Date
    Dec 2018
    Posts
    106
    Post Likes
    Thread Starter
    Do you have a photo of what the transition at the 22x8 should look like?

  13. #10
    Join Date
    Dec 2007
    Posts
    13,231
    Post Likes
    Quote Originally Posted by Wild85 View Post
    0.41” return static on high. 0.20” pressure drop across coil. There’s lots of turbulence between filter and the 90 on the drop.
    .41" measurement was taken where, before or after the filter?

    Unless that is a hole in the bottom sticker on the door, I don't see a test hole AFTER the filter.
    The Food Stamp Program, administered by the U.S. Department of Agriculture, is proud to be distributing the greatest amount of free meals and stamps EVER.
    Meanwhile, the National Park Service, administered by the U.S. Department of the Interior, asks us to "Please Do Not Feed the Animals". Their stated reason for this policy "... the animals become dependent on handouts and will not learn to take care of themselves."
    from an excerpt by Paul Jacob in Sun City, AZ

  14. #11
    Join Date
    Dec 2018
    Posts
    106
    Post Likes
    Thread Starter
    Inside the blower compartment on the left side of the 5” filter rack.

  15. #12
    Join Date
    Dec 2018
    Posts
    106
    Post Likes
    Thread Starter
    See photo for return measurement.
    Attached Images Attached Images  

  16. #13
    Join Date
    Dec 2018
    Posts
    106
    Post Likes
    Thread Starter
    Checked static on high again and get 0.755”

  17. #14
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Quote Originally Posted by Wild85 View Post
    Do you have a photo of what the transition at the 22x8 should look like?
    No I don't.

    Imagine a fitting 2x20 at the 22x8 that tapers down to 24x8.

    Also, some just run a 20x25 drop to a radius el.

  18. #15
    Join Date
    Mar 2016
    Location
    Dayton Oh
    Posts
    6,632
    Post Likes
    Like this

    They all cant be perfect
    https://r.tapatalk.com/shareLink/top...ink_source=app


    Sent from my iPhone using Tapatalk

  19. #16
    Join Date
    Mar 2016
    Location
    Dayton Oh
    Posts
    6,632
    Post Likes
    Fittings and transitions are more important than size.

    How a duct changes direction or size can account for the equivalent of 75’ of duct.


    Sent from my iPhone using Tapatalk

  20. #17
    Join Date
    Dec 2018
    Posts
    106
    Post Likes
    Thread Starter
    Once the return drop is fixed properly I assume this will allow better performance on the supply side and allow better pull on the return side? Cause right now I’m at around 650 cfm return on a 925 cfm supply.

  21. #18
    Join Date
    Mar 2018
    Location
    Cottonwood, Ca #StateofJefferson
    Posts
    2,187
    Post Likes
    The blower cant push out what it never brought in so opening up its lungs will help it live a happy, quiet life. It will also drop the blowers electrical draw from where it's running at right now I'm sure, again, helping it lead a long healthy life. You want that return air to be traveling across that filter evenly and at the correct speed so it doesnt just pull the dirt thru the filter and out the other side

  22. #19
    Join Date
    Dec 2004
    Location
    Caledonia WI
    Posts
    1,962
    Post Likes
    At the point that the return drop enters the return trunk you have about 120 feet of equivalent resistance, that’s where the most improvement can be made. Doing something like this will help. Then you can look into other things if you still have a problem.
    Attached Images Attached Images  
    It's not what you're capable of doing that defines you, it's what you do on a daily basis.

  23. #20
    Join Date
    Dec 2018
    Posts
    106
    Post Likes
    Thread Starter
    What would you call this pre made piece?

Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •