JCI - Max Amount of NS Sensors
Brain fart here. How many NS sensors are allowed on one device again? In this case a PCG2611 using NS8000 sensors. A max of four rings a bell...
-
-
-
-
I’ve done 5 plenty of times with the older ones.
Also there is a max of 8 now with the newer models.
Note: SA bus applications are limited to a power load of 210 mA. The best practice when configuring an SA bus is to limit the total available operating power consumption to 120 mA or less. This power level allows you to connect a BTCVT Wireless Commissioning Converter temporarily or a DIS1710 Local Controller Display to the bus for commissioning, adjusting, and monitoring.
Sent from my iPad using Tapatalk
-