    Vaccum problem's

    This is going to sound stupid been doing this almost 30 yrs went and changed a compressor.
    pressurized up to 155 pounds checked for leaks sprayed each joint. Did not lose pressure
    installed core tools did hi side and low side. removed core tools thinking they were leaking but i guess not still the same thing And yes I broke with nitrogen
    put on vacuum for just over an hour small system got down to 325 microns.
    but it would not hold a vacuum new hoses Fieldpeice mr45.
    The system still had a full charge upon recovery.
    Any idea's
    Thanks

  2. #2
    Join Date
    May 2004
    Location
    Salt Lake City/Tooele
    Posts
    9,679
    Post Likes
    Vacuuming through your gauges?

  3. #3
    Join Date
    Mar 2018
    Location
    Virginia
    Posts
    5,120
    Post Likes
    Redock your hoses to your manifold with the crt attached and vacuum the entire rig? Does it hold?

    Sent from my SM-G960U using Tapatalk
    "I think Quantum tunneling would work great... "

    "Call a technician for God's sake. Or we'll see you on the news or the Dark Side of the Moon."

  4. #4
    Join Date
    Dec 2018
    Location
    Californa
    Posts
    2
    Post Likes
    Thread Starter
    Quote Originally Posted by slctech View Post
    Vacuuming through your gauges?
    First time yes 2nd time no still the same thing using all fieldpiece two different manifold's

  5. #5
    Join Date
    Nov 2020
    Location
    Spokane, WA
    Posts
    18
    Post Likes
    In my experience you are not going to vacuum down to 325 microns if you have any sort of a leak, there has must be something with in the system still effecting the vacuum? If equipment is proven accurate. Then it may be the system. What does the vacuum rise to?

  6. #6
    Join Date
    Jan 2020
    Location
    Winnipeg Canada
    Posts
    2,507
    Post Likes
    Possible moisture in system? Have you tried the old triple evac to see if it'll hold the microns?
    Other suggestion is nylog on fittings and not using manifold

  7. #7
    Join Date
    Dec 2004
    Location
    Chicago area
    Posts
    19,137
    Post Likes
    Schrader without a cap? Like a unused port on evap?


    Sent from my iPhone using Tapatalk

  8. Likes R600a liked this post.
  9. #8
    Join Date
    Nov 2020
    Location
    Denver, Colorado
    Posts
    21
    Post Likes
    Out of curiosity, did you end up losing the whole vacuum? Or did it break a certain point where you called it? I agree with a couple other comments about the possibility of there bein moisture in the system. The other possibility is there being a leak within whatever you are using as a micron gauge. I don't pull through manifolds anymore due to me having to waste time looking for a leak that was never actually there, and it being my hoses. Or the possibility of the micron gauge being dirty inside the manifolds.

  10. #9
    Join Date
    Jan 2019
    Location
    Vero Beach, Florida
    Posts
    827
    Post Likes
    If you pulled to 325microns you don’t have any leaks.

    When was the last time you changed your pump oil? Is your micron gauge clean?

  11. #10
    Join Date
    May 2014
    Location
    Bay Area California
    Posts
    43,452
    Post Likes
    What did the microns rise up to and how long did it take to get there?


    Quote Originally Posted by AVR2018 View Post
    This is going to sound stupid been doing this almost 30 yrs went and changed a compressor.
    pressurized up to 155 pounds checked for leaks sprayed each joint. Did not lose pressure
    installed core tools did hi side and low side. removed core tools thinking they were leaking but i guess not still the same thing And yes I broke with nitrogen
    put on vacuum for just over an hour small system got down to 325 microns.
    but it would not hold a vacuum
    new hoses Fieldpeice mr45.
    The system still had a full charge upon recovery.
    Any idea's
    Thanks
    I do a triple evac with nitro to remove non condensables.

  12. #11
    Join Date
    Sep 2020
    Location
    midwest
    Posts
    203
    Post Likes
    RIP OP

  13. #12
    Join Date
    Jan 2019
    Location
    Vero Beach, Florida
    Posts
    827
    Post Likes
    Quote Originally Posted by YOUNG FROSTY View Post
    RIP OP
    ??

  14. #13
    Join Date
    Oct 2011
    Location
    Chicagoland Area
    Posts
    23,572
    Post Likes
    Quote Originally Posted by Deathpunch0311 View Post
    If you pulled to 325microns you don’t have any leaks.

    When was the last time you changed your pump oil? Is your micron gauge clean?
    and if you have a 2 stage pump and all you're doing is draining the oil, you're only removing 2/3 of the oil.
    Officially, Down for the count

    YOU HAVE TO GET OFF YOUR ASS TO GET ON YOUR FEET

    I know enough to know, I don't know enough
    Why is it that those who complain the most contribute the least?
    MONEY CAN'T BUY HAPPINESS. POVERTY CAN'T BUY ANYTHING

  15. #14
    Hurst11 is offline Professional Member/Membership Committee
    Join Date
    May 2020
    Location
    Haskell Oklahoma
    Posts
    1,529
    Post Likes
    I’m gonna say oil in the evaporator or condenser and as it’s in vacuum a small amount of refrigerant bubbles out and it’s reflected in your micron reading. It’s hard to pull and keep an extremely deep vacuum on an existing system.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •