    Eaton SVX9000 stuck on minimum speed

    I'm seeing the darndest thing. When the drive is off, the "frequency reference" monitor shows that the VFD is receiving the analog signal from the Siemens panel. But as soon as the drive is commanded on, it is stuck on minimum speed, and shows the minimum as the frequency reference, regardless of the signal sent to it. The motor current is well below the limit, the acceleration time is normal. I tried replacing the OPTA9 I/O board, but the new one acts the same way. I'm thinking of replacing the VFD; but it is a strange way for it to fail, and I worry there is some parameter I am missing. Has anyone ever seen this before?

  2. #2
    Join Date
    Mar 2018
    Location
    South East US
    Posts
    261
    Post Likes
    Pretty normal for VFDs to have minimum speeds programmed into them and or the controls to have minimums set too.
    I usually find the lowest speed we can reliably get out current switch to close and program it into the VFD so we know when it is running or not and isn’t too low of a speed to close the contact.
    Also testing and balancing may adjust them so that minimum air/water flows are achieved..and other reasons.
    It’s likely done so on purpose. But may be worth while to see if it’s the controls telling it to do it or the vfd, maybe something is overridden in the controls.


    Sent from my iPhone using Tapatalk

  3. #3
    Join Date
    Aug 2016
    Location
    Arlington, VA
    Posts
    13
    Post Likes
    Thread Starter
    This VFD drives a pump, and without ramping up to speed it does not make the differential pressure set-point. There is also an equivalent VFD/pump set-up that doesn't behave the same way. And I can verify with a meter that the controller is sending the speed signal, and it is received at the I/O board.

  4. #4
    Join Date
    Mar 2009
    Location
    Several Miles from Sane
    Posts
    2,660
    Post Likes
    Jake,
    Look at he programming of the DI's. It sounds like you have one setup as "Preset Speed" rather that something like "Forward Enable"
    If sense were so common everyone would have it !
    You cannot protect the Stupid from themselves !
    "Experience is the ability to recognize a mistake Before you make it again!" (Stolen Quote)

  5. Dislikes forcryinoutloud disliked this post.
  6. #5
    Join Date
    Aug 2016
    Location
    Arlington, VA
    Posts
    13
    Post Likes
    Thread Starter
    Cagey57,

    That was it!! She's humming now. Thanks so much for the tip.

  7. Likes Cagey57, MaxBurn liked this post.
+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •