    1 and 3 PH resistance motor/compressor testing to ground

    Embarrassing rookie question, but proud to be asking in order to become a better tech:

    On single phase motors, either my hot or neutral leg, when measured to a solid ground, should read an infinite resistance if the winding is good, correct? Any reading of a resistance (0 ohms to anything less than 0L) would indicate a grounded or broken winding?

    The same principle applies to three phase motors, the only difference being adding a third leg to check, correct?

    Nothing changes when measuring resistance to ground on compressors, correct?

    A sincere thank you to anyone who answers this!

  2. #2
    Join Date
    Oct 2011
    Location
    Harrisburg, NC
    Posts
    2,034
    Post Likes
    On a 3 phase motor, all 3 legs should ohm put the same. As they are all (L1/L2/Ll3) connected at one end, all three winding lengths and gauge are the same. Seems most 3 phase compressors I ohm are 1.0-1.5 ohms.

    On a single phase compressor, you have a common, a start, and a run. The start and run are both connected to common. So start to run should equal common to start plus common to run.


    Sent from my iPhone using Tapatalk

    I can't fix it if it won't stay broke..

  3. #3
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,726
    Post Likes
    A little reading

    Motors are Motors:
    Attached Images Attached Images

  4. #4
    Join Date
    Oct 2020
    Posts
    4
    Post Likes
    Thread Starter
    Just for clarification Big Daddy, you are speaking about your ohm readings between the legs, but not each leg to ground, correct? I definitely understand that, but am curious about leg to ground readings in order to determine if a winding has grounded.

    Thanks for the great resource, pecmsg. I am printing it now so I can quickly reference it in the future. I wish they had spoke about reading resistances in it too, but FASCO did cover a lot of cool factoids.

  5. #5
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,726
    Post Likes
    You should NEVER have any resistance to ground in any electric motor, single or 3 phase!

  6. #6
    Join Date
    Nov 2011
    Location
    CO
    Posts
    17,430
    Post Likes
    If your meter reads into the mega ohm range. It will show resistance to ground.

    I use 1,000 ohms per volt. So a 480 volt motor should be above 480,000 ohms (48M). But that is just a rule of thumb, and isn't always true. I've had motors in the 20-30M range, and still be good. Liquid refrigerant in compressors will lower the readings.

  7. #7
    Join Date
    Mar 2015
    Location
    Medford, N.Y.
    Posts
    10,203
    Post Likes
    Quote Originally Posted by BadDaddy420 View Post
    On a 3 phase motor, all 3 legs should ohm put the same. As they are all (L1/L2/Ll3) connected at one end, all three winding lengths and gauge are the same. Seems most 3 phase compressors I ohm are 1.0-1.5 ohms.

    On a single phase compressor, you have a common, a start, and a run. The start and run are both connected to common. So start to run should equal common to start plus common to run.


    Sent from my iPhone using Tapatalk
    A Copeland Scott T compressor has one leg (of 3)resistance diff from the other 2 legs.

  8. #8
    Join Date
    Oct 2011
    Location
    Harrisburg, NC
    Posts
    2,034
    Post Likes
    Quote Originally Posted by TechmanTerry View Post
    A Copeland Scott T compressor has one leg (of 3)resistance diff from the other 2 legs.
    I gotta look that up. Thanks.

    And I was earlier talking winding ohms. Not to ground.


    Sent from my iPhone using Tapatalk

    I can't fix it if it won't stay broke..

  9. #9
    Join Date
    Nov 2011
    Location
    CO
    Posts
    17,430
    Post Likes
    Do a search in pros commercial, we had a discussion a year or so ago, and someone posted the copeland literature on them.

  10. #10
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    8,082
    Post Likes
    Quote Originally Posted by 71CHOPS View Post
    ...I use 1,000 ohms per volt. So a 480 volt motor should be above 480,000 ohms (48M)...
    I think you meant 0.48M.
    "Right" is not the same as "Wise".

    Don't step on my favorite part of the Constitution just to point out your favorite part.

    Just because you can measure it, doesn't mean it is important. Just because you can't measure it, doesn't mean it isn't important.

  11. #11
    Join Date
    Mar 2015
    Location
    Medford, N.Y.
    Posts
    10,203
    Post Likes
    Quote Originally Posted by BadDaddy420 View Post
    I gotta look that up. Thanks.

    And I was earlier talking winding ohms. Not to ground.


    Sent from my iPhone using Tapatalk
    Yup,on the winding ohms.

  12. #12
    Join Date
    Jul 2007
    Location
    Virginia
    Posts
    19,249
    Post Likes
    Quote Originally Posted by BadDaddy420 View Post
    I gotta look that up. Thanks.
    I saved you the work and emailed you a couple pdf's.

    Check your inbox.
    Instead of learning the tricks of the trade, learn the trade.

  13. #13
    Join Date
    Oct 2020
    Posts
    4
    Post Likes
    Thread Starter
    Any chance you could send those pdf's this way too, rundawg?

  14. #14
    Join Date
    Jul 2007
    Location
    Virginia
    Posts
    19,249
    Post Likes
    Quote Originally Posted by HVACNaabe View Post
    Any chance you could send those pdf's this way too, rundawg?
    That would require you to put an email address in your profile, or sending me an email (address is in my profile).

    I don't post technical info in this "OPEN" forum.
    Instead of learning the tricks of the trade, learn the trade.

  15. #15
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,726
    Post Likes
    Quote Originally Posted by rundawg View Post
    That would require you to put an email address in your profile, or sending me an email (address is in my profile).

    I don't post technical info in this "OPEN" forum.
    Ooops

  16. #16
    Join Date
    Jun 2001
    Location
    San Diego, CA
    Posts
    1,265
    Post Likes
    leg to leg - the smaller the motor, the higher the resistance. You might see 50ohms on a small Cframe fridge motor, 15ohms on a 1/6hp blower, and barely 1 ohm on a 50hp premium.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •