    Nitrogen leak test walk in freezer

    I'm new to refrigeration and trying to learn as much as I can. One question I have is when it comes to nitrogen leak testing a walk in freezer. During this process does the liquid line solenoid need to be manually opened?

  2. #2
    Join Date
    Oct 2011
    Location
    Harrisburg, NC
    Posts
    2,034
    Post Likes
    Quote Originally Posted by harrisal21 View Post
    I'm new to refrigeration and trying to learn as much as I can. One question I have is when it comes to nitrogen leak testing a walk in freezer. During this process does the liquid line solenoid need to be manually opened?
    Yes, either by a manual stem or solenoid magnet.

    Same goes for evacuation.


    Sent from my iPhone using Tapatalk

    I can't fix it if it won't stay broke..

  3. #3
    Join Date
    Jan 2010
    Posts
    45,370
    Post Likes
    That would depend on your points of access.

  4. #4
    Join Date
    Oct 2011
    Location
    Harrisburg, NC
    Posts
    2,034
    Post Likes
    Quote Originally Posted by VTP99 View Post
    That would depend on your points of access.
    As I just had an argument with a guy that tried a shortcut... the OP only asked if it should be manually opened. I’d say yes, every time.

    That way he always thinks about it.

    If he has a port on the other side of the solenoid he can use and decides not to manually open the solenoid, that is his choice.

    But as he is learning, and only asked if it should be opened. Then yes.


    Sent from my iPhone using Tapatalk

    I can't fix it if it won't stay broke..

  5. Likes VTP99 liked this post.
  6. #5
    Join Date
    Jul 2012
    Location
    WA
    Posts
    3,250
    Post Likes
    I will typically leave it open for purging, pressure testing, and evacuation. It does not need to be open for pressure testing or evacuation if you use the suction and liquid service ports at the condensing unit.

  7. Likes VTP99 liked this post.
  8. #6
    Join Date
    Jan 2010
    Posts
    45,370
    Post Likes
    Well technically he could apply electric to it which wouldn't really be manual in the sense of the word.
    The solinoid could also be located at different locations.
    But I agree a novice should make certain it's not creating a restriction obstructing flow if needing to pass through it.

  9. #7
    Join Date
    Nov 2009
    Location
    Richmond, working under tarps
    Posts
    1,051
    Post Likes
    if you dump N2 into the high side while looking at low side pressure, you can prove the solenoid holds and so does the dis valves in the compressor

    then you once you are good there, you can dump into the low side, with a magnet or like

  10. Likes mnbvcxz liked this post.
  11. #8
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,726
    Post Likes
    Pull a control wire to disable the compressor. Energize the solenoid.

  12. #9
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,726
    Post Likes
    Quote Originally Posted by harrisal21 View Post
    I'm new to refrigeration and trying to learn as much as I can. One question I have is when it comes to nitrogen leak testing a walk in freezer. During this process does the liquid line solenoid need to be manually opened?
    You've got the post count

    Apply for Pro status!

  13. #10
    Join Date
    Oct 2004
    Posts
    597
    Post Likes
    Watch out for the test pressure on Heatcraft products that have transducers. You can either keep it under the safe pressure or unscrew it. They show funky pressures after being hit with to high of a nitrogen test. Don’t ask me how I know

  14. Likes WT70, zymometer liked this post.
  15. #11
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    14,048
    Post Likes
    You can also create leaks on semi hemis ....

  16. Likes rkious, WT70 liked this post.
  17. #12
    Join Date
    Nov 2009
    Location
    Richmond, working under tarps
    Posts
    1,051
    Post Likes
    Quote Originally Posted by rkious View Post
    Watch out for the test pressure on Heatcraft products that have transducers. You can either keep it under the safe pressure or unscrew it. They show funky pressures after being hit with to high of a nitrogen test. Don’t ask me how I know
    evap data plate should have the design pressure clearly stated

    if the xducer cannot handle it, that is a mauf issue

    i am not familiar with what they are using, i have used many pt-x from emerson, without issues

  18. #13
    Join Date
    Oct 2011
    Location
    Harrisburg, NC
    Posts
    2,034
    Post Likes
    Quote Originally Posted by indy2000 View Post

    if the xducer cannot handle it, that is a mauf issue
    Got to take em off for vacuum anyway, so why not be safe and take them off while nitro testing?

    And it depends on what range the suction transducer is good for. If it’s a 0-100 transducer, hitting it with 200psig of nitrogen might mess it up.

    But again. Transducers are not built (as a general rule) for deep vacuum. So remove them if doing any pressure testing/vacuums. Then you don’t have to worry if it will hold the nitrogen or not.


    Sent from my iPhone using Tapatalk

    I can't fix it if it won't stay broke..

  19. #14
    Join Date
    Jan 2010
    Location
    Sea to Sky
    Posts
    7,033
    Post Likes
    They should all be on isolation valves on a proper install anyway.

    Sent from my SM-G965W using Tapatalk

  20. #15
    Join Date
    Nov 2009
    Location
    Richmond, working under tarps
    Posts
    1,051
    Post Likes
    Quote Originally Posted by BadDaddy420 View Post
    Got to take em off for vacuum anyway, so why not be safe and take them off while nitro testing?

    And it depends on what range the suction transducer is good for. If it’s a 0-100 transducer, hitting it with 200psig of nitrogen might mess it up.

    But again. Transducers are not built (as a general rule) for deep vacuum. So remove them if doing any pressure testing/vacuums. Then you don’t have to worry if it will hold the nitrogen or not.


    Sent from my iPhone using Tapatalk


    I have not heard that anywhere, talking with engineers at emerson or alike............


    here is a little spec sheet

    https://climate.emerson.com/document...us-1734302.pdf


    I always leave them on for pressure testing and evacuation, if they dont pass that, back they go to the supplier....

    I dont know, maybe a close to a 1000 of them, i have done..........

  21. #16
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,726
    Post Likes
    Just looked at a LP transducer.
    Rating 0 - 18 BAR
    Converted 0 -261 PSI
    Don’t see an issue!

  22. #17
    Join Date
    Nov 2020
    Location
    Finland
    Posts
    10
    Post Likes
    Not necessary if you're lazy and you have a scent about the leaking part I.E hole in the condenser coil.

  23. #18
    Join Date
    Nov 2009
    Location
    Richmond, working under tarps
    Posts
    1,051
    Post Likes
    Quote Originally Posted by pecmsg View Post
    Just looked at a LP transducer.
    Rating 0 - 18 BAR
    Converted 0 -261 PSI
    Don’t see an issue!
    i think that is operating signal

    design pressures, i like burst, are way higher

  24. #19
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,726
    Post Likes
    Exactly!

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •