Thread: Head scratcher, Trane RTUJC504c, 50tn condenser

  1. #1
    Join Date
    Apr 2020
    Location
    va
    Posts
    10,300
    Post Likes

    Head scratcher, Trane RTUJC504c, 50tn condenser

    At an industrial site today assisting a tech doing pm's. Seen similar problems, but this is the first with this combo.

    Scroll compressors, two per circuit, microchannel condenser, tube/fin evap, ~100' line set, evap ~30' above cond. History of evap coil leaks due to corrosive environment.

    Issue: connected gauges to suction and liquid lines outside of enclosed condenser.
    All four compressor sump heaters were open.
    Suction ~110-120psi, ssh 10-12*f, fairly stable
    Liquid line ~350- 410 psi 5-10 second swings, subcooling ~ 35*f swinging a couple of *f

    Took 3 steps and about 1 hour to find problem.

    I'll go thru the steps giving about an hour for your input before listing each step and conclusion. If I had a prize I'd give it to the first correct response!

  2. #2
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    14,048
    Post Likes
    over charged a little

  3. #3
    Join Date
    Apr 2020
    Location
    va
    Posts
    10,300
    Post Likes
    Thread Starter
    Quote Originally Posted by Snapperhead View Post
    over charged a little
    Correct on first step.
    Recovered refrigerant to ~ 15*f subcooling. SSH unchanged, Liquid line pressure still swinging ~ 50#.

    Step #2?

  4. #4
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    14,048
    Post Likes
    those micro channels dont take much to get dirty correct ? I'd wash them next

    This unit is used for cooling ... I assume ...

  5. #5
    Join Date
    Apr 2020
    Location
    va
    Posts
    10,300
    Post Likes
    Thread Starter
    Quote Originally Posted by Snapperhead View Post
    those micro channels dont take much to get dirty correct ? I'd wash them next

    This unit is used for cooling ... I assume ...
    Cooling production area where they are making covid mask. Coils only moderately dirty.

  6. #6
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    14,048
    Post Likes
    Low ambient Cond Fan monitor sensing bulb correctly mounted ?

  7. #7
    Join Date
    Apr 2020
    Location
    va
    Posts
    10,300
    Post Likes
    Thread Starter
    Quote Originally Posted by Snapperhead View Post
    Low ambient Cond Fan monitor sensing bulb correctly mounted ?
    about 70*f ambient, 2 of 3 fans steady operation

  8. #8
    Join Date
    Apr 2020
    Location
    va
    Posts
    10,300
    Post Likes
    Thread Starter
    Step #2

    did test for non-condensables, saturated and ambient < 2*f difference, liquid line pressure still swinging

    Step #3?

  9. #9
    Join Date
    Apr 2020
    Location
    va
    Posts
    10,300
    Post Likes
    Thread Starter
    Removed coil panels, put gauge and temp probe on compressor discharge.

    compressor discharge ~ 100# higher than liquid line, swinging > 50#, pegged gauges a couple of times, discharge sh 2-4*f
    temp probe on liquid line fairly steady, but I could feel spurts of spikes in liquid line temp for 1-2 seconds
    noticed oil in compressor sight glass agitated

    Problem solved. Answer?

  10. #10
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    14,048
    Post Likes
    I was thinking from the beginning maybe someone topped off unit with wrong refrigerant , but doubtful

    Is something going on with drier ?

  11. #11
    Join Date
    Apr 2020
    Location
    va
    Posts
    10,300
    Post Likes
    Thread Starter
    Extreme oil overcharge.
    Liquid flooding compressor causing swings in pressure. Microchannel ports restricted by by liquid oil entering causing high pressure and high pressure drop.

    evidence:
    1. normal ssh
    2. usually high evaporator approach & low suction pressure on chillers, only slightly out in this case with ahu
    3. low discharge sh, oil not compressing cools discharge gas
    4. microchannel high pressure drop & high approach

    Corrective action: connect recovery cylinder to liquid connection, bleed liquid into cylinder very slowly while operation, heater band on cylinder, cylinder vapor connection full open to suction, distill oil out.

    Unit has had a history of leaks and repairs.

    Have seen excess oil in all types of systems, but this is the first time I've seen the extreme pressure swings and extreme microchannel pressure differential. Usually very little effect on tube/fin condenser pd or approach.

  12. #12
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    14,048
    Post Likes
    Why would anyone add extra oil to it ?

  13. #13
    Join Date
    Apr 2020
    Location
    va
    Posts
    10,300
    Post Likes
    Thread Starter
    Quote Originally Posted by Snapperhead View Post
    Why would anyone add extra oil to it ?
    Oil heater burnt out, may not have seen oil level after starting with saturated oil
    Split unit factory recommends adding oil on start, may have calculated wrong
    Original compressors so not due to changeouts
    Recovery cylinders may have been contaminated

  14. #14
    Join Date
    Nov 2020
    Posts
    19
    Post Likes
    I have run into this before myself. So were your sight glasses on the sump completely full?

  15. #15
    Join Date
    Apr 2020
    Location
    va
    Posts
    10,300
    Post Likes
    Thread Starter
    Quote Originally Posted by HVACDreams View Post
    I have run into this before myself. So were your sight glasses on the sump completely full?
    NO. Low dsh sh with normal ssh is main indication.

    Used to see it frequently on McQuay ALS and other screw chillers, but without the pressure swings with tube/fin or water cooled condensers. Sight glasses on oil seperators would always be low.

  16. #16
    Join Date
    Apr 2010
    Location
    ... sitting in the Hollywood Hawaiian Hotel, listening to the air conditioner hum
    Posts
    1,208
    Post Likes
    I'm intrigued by your makeshift oil separator. It makes perfect sense, but I would have never thought of doing that.

    I'm not familiar with that particular unit, was there no way to drain the oil from the sump? Most units that I've worked on that have oil sight glasses will also have some sort of port there where one could remove oil. Is this method preferable in some way? I guess you don't lose any refrigerant at all this way, as opposed to blowing refrigerant saturated oil into a bucket.

    But for units without a SG, I'll remember this topic if I ever see something like this. Now that I think about it, I have a 30GXN that's been acting up, maybe I can play around with that.

    The great professors of the art are not immune from the malignancy of matter and the eternal cussedness of inanimate objects.

  17. #17
    Join Date
    Apr 2020
    Location
    va
    Posts
    10,300
    Post Likes
    Thread Starter
    Epa does not allow oil at pressures over 5psi to drain to open containers. Most scrolls do not have oil drains. Flooded evaps take the longest to recover the oil...

  18. #18
    Join Date
    Dec 2004
    Location
    Chicago area
    Posts
    19,137
    Post Likes
    Oil saturated refrigerant is a pretty common problem. I find it most after compressors have been changed on packaged units. Most dont take the time to measure the oil out of the old compressor. I usually do, and remove that amount from the new.

    Ive used the method EHSX described a few times for running systems.

    Had one jag off add 5 gallons of oil to the wrong circuit on a machine.


    Sent from my iPhone using Tapatalk

  19. #19
    Join Date
    Apr 2020
    Location
    va
    Posts
    10,300
    Post Likes
    Thread Starter
    I was training manager for Dunham Bush 90’s. Used to say there would never be an oil shortage if everyone had a DB screw, typically always had excess oil, removed 5 to as much as 45 gals from systems in the field. Most of the time no one claimed to know where it came from.

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •