Results 1 to 15 of 15

Thread: Trane XR80 Furnace Issue

  1. #1
    Join Date
    Oct 2020
    Posts
    6
    Post Likes

    Trane XR80 Furnace Issue

    Hi. I've got a weird issue with my Trane XR80 furnace.
    I've had two different companies come out to try and
    diagnose the problem without success. One of them is
    very familiar with Trane products.

    So, here is the problem. I've noticed that sometimes
    my furnace will partially come on without the burner
    and blower motor coming on. I hear it turn on
    (exhaust fan maybe?) and go for a bit and then it
    goes off. It will immediately come on again and do
    the same thing. One early morning I noticed it did
    this at least 5 or 6 times. I've even noticed this
    happen when I have my thermostat set for AC!

    The furnace will come on as it should at times and
    properly heat my condo. I'm just afraid this is
    especially taxing on my furnace and may cause it
    to fail in the near future. I was trying to be proactive
    to get this checked out before I really need it this
    winter here in Colorado.

    Anyone have any idea what is going on here?

    Thanks for your time,

    Jon

  2. #2
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,736
    Post Likes
    Unfortunately you haven't found a qualified contractor .............Yet!

    Keep looking, measurements need to be taken, with those they will be pointed in the right direction.

  3. #3
    Join Date
    Sep 2008
    Location
    VA
    Posts
    6,217
    Post Likes
    What did the 2 other contractors repair?
    "The only true wisdom is in knowing you know nothing" Socrates

  4. #4
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,736
    Post Likes
    Quote Originally Posted by mgenius33 View Post
    What did the 2 other contractors repair?
    An Invoice?

  5. Likes VTP99 liked this post.
  6. #5
    Join Date
    Oct 2020
    Posts
    6
    Post Likes
    Thread Starter
    Quote Originally Posted by pecmsg View Post
    An Invoice?
    Thanks for the responses.

    The first guy that came out seemed to think it was the thermostat. He
    suggested I replace that. He didn't charge anything, which I appreciated,
    but I'm not so sure his solution will fix the problem.

    The second guy charged me a $ trip fee. This is what he wrote on the
    receipt (hope it's ok to list what he wrote): Homeowner reported an
    occasional failure to fire. Ran System. Pressure switch closes at .50inwc.
    Inducer is pulling .70 inwc. Flame signal 3.1-3.5 dcmA. Inlet:7.2
    Manifold: 3.6 Drop: 0.7 (think it is 0.7, a little illegible). Ran water heater
    during heat cycle. Inlet pressure went down by .3inwc. No delay in
    flame crossover. No loose wires on the gas valve, pressure switch, inducer
    motor or board. HSI ohms: 16. Showed the homeowner how to look for the
    glow of the HSI. Cycled the system 15 times with no failures. If the issue
    returns the homeowner should pay attention to outdoor conditions/time of
    day so that we can better find the issue. Unfortunately I am unable to
    reproduce the failure at this time.

    When I noticed the issue when it did the "partial run" 5 or 6 times -- the
    temperature was in the late 20s/early 30s with no wind. I believe the
    thermostat was set to 68 and the current temp during these partial runs
    was 67. A few times I have manually increased the thermostat a few
    degrees higher and the blower would come on ok.

    Is any of this information helpful in the diagnosis? I honestly don't know
    what to do other than try and hire some other people to come out.
    Afraid they will be unable to locate the issue too and I will be out more
    money. This second company is highly recommended on Team Dave Logan
    website and Dave Logan endorsed (Denver metro recommended providers).

    Thanks again for any help people can provide.

    Jon
    Last edited by beenthere; 10-20-2020 at 04:10 AM.

  7. #6
    Join Date
    Dec 2007
    Posts
    13,231
    Post Likes
    What thermostat?
    The Food Stamp Program, administered by the U.S. Department of Agriculture, is proud to be distributing the greatest amount of free meals and stamps EVER.
    Meanwhile, the National Park Service, administered by the U.S. Department of the Interior, asks us to "Please Do Not Feed the Animals". Their stated reason for this policy "... the animals become dependent on handouts and will not learn to take care of themselves."
    from an excerpt by Paul Jacob in Sun City, AZ

  8. #7
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Sounds like a Nest thermostat wired up to steal power..

  9. #8
    Join Date
    Sep 2008
    Location
    VA
    Posts
    6,217
    Post Likes
    Tell your tech to get on this site and contact us. I believe there is a common issue with ignition timing sequence failure on this particular model when it gets to be several years old. This is one of those "out of the ordinary" issues. I agree, it can be a pain to diagnose when everything is working properly for 15 cycles. It sounds like the second tech did his job.
    "The only true wisdom is in knowing you know nothing" Socrates

  10. Likes ksefan liked this post.
  11. #9
    Join Date
    Oct 2020
    Posts
    6
    Post Likes
    Thread Starter
    The thermostat I have is the Lux TX9600TSa.

    I had a honeywell (I believe) for a bit and noticed this issue. My Dad had just
    upgraded to a Nest and asked me if I wanted this one, which was not very old.
    I installed it and noticed I was having the same issue, so figured the thermostat
    was not the issue (unless the Lux is malfunctioning).

  12. #10
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    The Lux is battery operated. So I am guessing you don't have a low battery warning showing on it.

  13. #11
    Join Date
    Oct 2020
    Posts
    6
    Post Likes
    Thread Starter
    Quote Originally Posted by mgenius33 View Post
    Tell your tech to get on this site and contact us. I believe there is a common issue with ignition timing sequence failure on this particular model when it gets to be several years old. This is one of those "out of the ordinary" issues. I agree, it can be a pain to diagnose when everything is working properly for 15 cycles. It sounds like the second tech did his job.
    I believe this furnace is about 12 years old, so wonder if it is on its way out. Do you think it is too old? A couple years ago the flame sensor and run capacitor were replaced. Last year a tech replaced the blower motor.

  14. #12
    Join Date
    Oct 2020
    Posts
    6
    Post Likes
    Thread Starter
    Thanks everyone for the replies!

  15. #13
    Join Date
    Oct 2020
    Posts
    6
    Post Likes
    Thread Starter
    Quote Originally Posted by beenthere View Post
    The Lux is battery operated. So I am guessing you don't have a low battery warning showing on it.
    Don't see a low battery warning on it. Put this in a few months ago with new batteries, so should be good for a while.

  16. #14
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,736
    Post Likes
    Quote Originally Posted by avoidablehinder View Post
    I believe this furnace is about 12 years old, so wonder if it is on its way out. Do you think it is too old? A couple years ago the flame sensor and run capacitor were replaced. Last year a tech replaced the blower motor.
    Aren't you the one that's suppose to make that decision!

  17. #15
    Join Date
    Dec 2007
    Posts
    13,231
    Post Likes
    NEST is not considered an upgrade to most on this site and in the trade!!!!

    The Food Stamp Program, administered by the U.S. Department of Agriculture, is proud to be distributing the greatest amount of free meals and stamps EVER.
    Meanwhile, the National Park Service, administered by the U.S. Department of the Interior, asks us to "Please Do Not Feed the Animals". Their stated reason for this policy "... the animals become dependent on handouts and will not learn to take care of themselves."
    from an excerpt by Paul Jacob in Sun City, AZ

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.