    ZIEHL ABEGG condenser motor troubleshooting procedure

    Motor trips 4 amp breaker when 460V power is applied.

    Model FN063-ZIQ.GL.V7P3/154972






  2. #2
    Join Date
    Nov 2004
    Location
    Northern Calif
    Posts
    142
    Post Likes
    That looks like a single unit, control and motor ?...the old ones were separate, test the motor leads ohms should be equal.
    "He who knows the least, knows it the loudest"
    I'm not young enough, to know everything...

  3. #3
    Join Date
    Nov 2004
    Location
    up in the hizzy
    Posts
    3,665
    Post Likes
    Toasted it, was that a Hoffman or Rittal ?
    There is not better place for the working men than the union! 100% UA the only HVAC union!

  4. #4
    Join Date
    Feb 2005
    Location
    Florida
    Posts
    1,423
    Post Likes
    Thread Starter
    Quote Originally Posted by valdelocc View Post
    Toasted it, was that a Hoffman or Rittal ?
    Neither, but both condenser motors were bad.

  5. #5
    Join Date
    Apr 2007
    Location
    New Brunswick, Canada
    Posts
    343
    Post Likes
    As mentioned above, check the motor leads for equal resistance. I would also Meg them to ground as well.
    If the windings check out okay, disconnect the leads to the motor and re-apply voltage. If the breaker still trips, the issue lies within the module or the supply circuit.

    Curious, what is the make/model of the unit? I have only came across these on high end euro style units (GEA). Generally very reliable, but also dead expensive.
    Attached Images Attached Images  

  6. #6
    Join Date
    Dec 2014
    Posts
    3,331
    Post Likes
    I cant remember for sure but I thought Seresco had some trouble shooting procedure for those. Possibly.

    Sent from my SM-G950U using Tapatalk

  7. #7
    Join Date
    Dec 2014
    Location
    New Mexico
    Posts
    1,070
    Post Likes
    They look like condenser fan motors I have had to change on MRI chillers mounted in a semi-trailer. I think it was a Northern Air set up. They sent out the whole assembly, that thing weighed at ton to pull up on top of the trailer.


    Sent from my iPhone using Tapatalk

  8. #8
    Join Date
    Feb 2005
    Location
    Florida
    Posts
    1,423
    Post Likes
    Thread Starter
    95lbs

  9. #9
    Join Date
    Nov 2011
    Location
    CO
    Posts
    8,099
    Post Likes
    can you even buy separate parts (motor/module) for those?

    I always figured it would be all or nothing.

  10. #10
    Join Date
    Nov 2004
    Location
    up in the hizzy
    Posts
    3,665
    Post Likes
    Quote Originally Posted by 71CHOPS View Post
    can you even buy separate parts (motor/module) for those?

    I always figured it would be all or nothing.
    I changed a few and had to buy the whole thing including the blades, once waited for 2 months to get a replacement, ran the chiller with a large fan from HFT strapped to the condenser.