Thread: Cvhf with (negative) -63F evap approach. Help!

  1. #1
    Join Date
    Oct 2020
    Posts
    8
    Post Likes

    Cvhf with (negative) -63F evap approach. Help!

    First time posting here. I have a CVHF570. I'm having trouble making sense of this -63F evap approach temp. Set point is 42F. Evap leaving is 41.9F. Entering is 44.4F (I know my delta is to close). Sat refrigerant temp is 105.7F and evap pressure is 8.5psig. I CAN NOT MAKE SENSE OF THIS FOR SOME REASON. I know I'm missing something somewhere.

  2. #2
    Join Date
    Aug 2006
    Location
    Mixing oil and fire with a big spoon.
    Posts
    8,082
    Post Likes
    the math is correct for R123. clearly, your temperature sensor is faulty. i recommend calling a qualified contractor to take care of your machine.
    "Right" is not the same as "Wise".

    Don't step on my favorite part of the Constitution just to point out your favorite part.

    Just because you can measure it, doesn't mean it is important. Just because you can't measure it, doesn't mean it isn't important.

  3. Likes CHILLERSVCMAN, supertek65 liked this post.
  4. #3
    Join Date
    Jan 2015
    Location
    Somewhere making cold water
    Posts
    370
    Post Likes
    You need some help, please call a service professional before you put yourself in a compromising situation.


    Sent from my iPhone using Tapatalk

  5. Likes CHILLERSVCMAN liked this post.
  6. #4
    Join Date
    Oct 2020
    Posts
    8
    Post Likes
    Thread Starter
    Time out. Maybe I should of worded it better. I needed help to verify it's my temp sensor. I am a professional and I know what I'm doing. I've got 15 yrs doing this, with the last 3 yrs on low pressure machines. I'm still learning. Try not to bust my chops to bad guys.

  7. #5
    Join Date
    Oct 2020
    Posts
    8
    Post Likes
    Thread Starter
    Right! I've done the math. I was just having a hard time convincing myself it's a temp sensor. I dont know why. The obvious ones are the ones I always try to prove to not be the problem. I dont know why I do that. But thanks for helping me in a assuming way.

  8. #6
    Join Date
    Mar 2004
    Location
    ottawa canada
    Posts
    4,011
    Post Likes
    I think someone is just goofin around
    The toy chest is officially full ... I got a new toy..... 2007 Aston Martin V8 Vantage and yes it still gives me goosebumps
    You bend em" I"ll mend em" !!!!!!!
    I"m not a service tech, I’m retired ….I used to be a thermodynamic transfer analyst & strategic system sustainability specialist
    In the new big shop , greasin', oilin' . tweakin' n shinin' !!

  9. Likes stanbyyourword liked this post.
  10. #7
    Join Date
    Apr 2020
    Location
    va
    Posts
    10,300
    Post Likes
    Looks like to me you have the condenser and evaporator mixed up.

  11. #8
    Join Date
    Oct 2020
    Posts
    8
    Post Likes
    Thread Starter
    Quote Originally Posted by ehsx View Post
    Looks like to me you have the condenser and evaporator mixed up.
    Ha! Yeah, no. I'm not sure 42 degree condenser water is even possible down here where I'm at.

  12. #9
    Join Date
    Apr 2020
    Location
    va
    Posts
    10,300
    Post Likes
    Quote Originally Posted by Im_just_goofin View Post
    Ha! Yeah, no. I'm not sure 42 degree condenser water is even possible down here where I'm at.
    Saturated temp and pressure are condenser.
    41.9 & 44.4 are evap

    If R-123 evap should be in vac with sat <40

  13. #10
    Join Date
    Jun 2003
    Location
    in a tree looking in your window
    Posts
    2,088
    Post Likes
    My money says it's an adaptiview panel, wait until he tries to install it

  14. #11
    Join Date
    Jan 2015
    Location
    Somewhere making cold water
    Posts
    370
    Post Likes
    Quote Originally Posted by ehsx View Post
    Saturated temp and pressure are condenser.
    41.9 & 44.4 are evap

    If R-123 evap should be in vac with sat <40
    Quote Originally Posted by Im_just_goofin View Post
    Time out. Maybe I should of worded it better. I needed help to verify it's my temp sensor. I am a professional and I know what I'm doing. I've got 15 yrs doing this, with the last 3 yrs on low pressure machines. I'm still learning. Try not to bust my chops to bad guys.
    Clue..... cup of ice water


    Sent from my iPhone using Tapatalk

  15. Likes dieseldude liked this post.
  16. #12
    Join Date
    Oct 2020
    Posts
    8
    Post Likes
    Thread Starter
    It was my sat evap sensor. Like I said I dont know why I even second guessed myself. Thanks all for making me feel dumb lol. Yeah chillrdude definitely the adaptive view was bad too. Good thing I've done a few tu upgrades in my past. But hey there's always a know it all in every bunch they say. Keep up that sarcasm, that stuff really helps to build confidence in the guys still learning.

  17. #13
    Join Date
    Nov 2008
    Posts
    499
    Post Likes
    tracer tu panel upgrades......so you work for Trane

  18. #14
    Join Date
    Jun 2003
    Location
    in a tree looking in your window
    Posts
    2,088
    Post Likes
    Quote Originally Posted by Im_just_goofin View Post
    It was my sat evap sensor. Like I said I dont know why I even second guessed myself. Thanks all for making me feel dumb lol. Yeah chillrdude definitely the adaptive view was bad too. Good thing I've done a few tu upgrades in my past. But hey there's always a know it all in every bunch they say. Keep up that sarcasm, that stuff really helps to build confidence in the guys still learning.
    I do what I can, I'll be here all week. My comment had to with the sensor needing to be bound to the controller and not plug and play which leads to the always fun TU software debate that rages here forever (right Healey) anyway you come on here with your first post and ask a question that makes you sound like a building maintenance man then get butt hurt when we question your level of experience, at least you clarified that you have a whole 3 years doing low pressure chillers and TU upgrades, welcome to the forum.

  19. #15
    Join Date
    Oct 2020
    Posts
    8
    Post Likes
    Thread Starter
    Lol what gave it away. Not any more. I made the wonderous decision to leave and go to JCI. Not a bad gig. The local here isn't what it is north of here. But still ok.

  20. #16
    Join Date
    Oct 2020
    Posts
    8
    Post Likes
    Thread Starter
    I realized once the replies came in, how it sounded and looked. No hard feelings this way. 3 years isn't a lot when it comes to most. Screws, recips, and the god awful scroll machines is my strong point. Centrifugal mechanics are the 1%ers lol. I'm getting there. I'll trade my plethora of knowledge about york machines for centrifugal as needed. Not saying much I know but hey I'm here for you guys if needed too. Butt doesn't hurt anymore now. Chillrdude I'll buy you a beer next time.

  21. #17
    Join Date
    Jun 2003
    Location
    in a tree looking in your window
    Posts
    2,088
    Post Likes
    Quote Originally Posted by Im_just_goofin View Post
    I realized once the replies came in, how it sounded and looked. No hard feelings this way. 3 years isn't a lot when it comes to most. Screws, recips, and the god awful scroll machines is my strong point. Centrifugal mechanics are the 1%ers lol. I'm getting there. I'll trade my plethora of knowledge about york machines for centrifugal as needed. Not saying much I know but hey I'm here for you guys if needed too. Butt doesn't hurt anymore now. Chillrdude I'll buy you a beer next time.
    Cool I was really waiting for you to come back to us asking about TU software, I love how that topic triggers Healey

  22. #18
    Join Date
    Oct 2020
    Posts
    8
    Post Likes
    Thread Starter
    Lol I hear you. Nah I have TU, tracer, rover, blah blah blah. So click bind BEFORE you highlight the LLID with a magnet!! Got it!! Lmao. You was gonna rip me wasnt you. Ha!

  23. #19
    Join Date
    Jul 2007
    Location
    The Hot South
    Posts
    2,413
    Post Likes
    You can now bind devices from the front panel with the current CT. firmware.
    The 2nd most important amendment is to protect the 1st....

    Free Air Conditioner Sizing Chart

  24. #20
    Poodle Head Mikey's Avatar
    Poodle Head Mikey is offline Membership Chair/ARP Committee / Professional Member*
    Join Date
    Sep 2002
    Location
    I try to stay as far away from myself as I can.
    Posts
    37,825
    Post Likes
    I suspect that your sensor is just goofin too. <g>
    ------------------
    Quote Originally Posted by Im_just_goofin View Post
    First time posting here. I have a CVHF570. I'm having trouble making sense of this -63F evap approach temp. Set point is 42F. Evap leaving is 41.9F. Entering is 44.4F (I know my delta is to close). Sat refrigerant temp is 105.7F and evap pressure is 8.5psig. I CAN NOT MAKE SENSE OF THIS FOR SOME REASON. I know I'm missing something somewhere.
    PHM
    --------

    When faced with the choice between changing one's mind, and proving that there is no need to do so, most tend to get busy on the proof.

+ Reply to Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.