    Quote Originally Posted by WCZ1 View Post
    If you mean generally for comfort then around 70
    Okay, the load calc has to be done with that as the indoor design temp.

    A 3 ton unit, moving 1200 CFM, will lose almost 5,000 BTUs of sensible capacity at 70°F indoor temp, compared to maintaining 75°F indoor temp.

  2. #22
    Join Date
    Oct 2020
    Posts
    10
    Post Likes
    Thread Starter
    So just to make sure I follow then I would need to move to the 4 ton to get closer to a unit that sensibly can reach 70 ? Thanks


    Quote Originally Posted by beenthere View Post
    Okay, the load calc has to be done with that as the indoor design temp.

    A 3 ton unit, moving 1200 CFM, will lose almost 5,000 BTUs of sensible capacity at 70°F indoor temp, compared to maintaining 75°F indoor temp.

  3. #23
    Join Date
    Jan 2004
    Location
    PA
    Posts
    80,602
    Post Likes
    Quote Originally Posted by WCZ1 View Post
    So just to make sure I follow then I would need to move to the 4 ton to get closer to a unit that sensibly can reach 70 ? Thanks
    Not really. 3.5 ton would meet the sensible load 70 indoor and your areas design outdoor.

  4. #24
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    13,331
    Post Likes
    Quote Originally Posted by WCZ1 View Post
    If you mean generally for comfort then around 70
    Around = +5'F / -0'F ?

    ASHRAE 1% DESIGN CONDTIONS
    __ 88.3'F /58.4'F
    What is the resultant S.H.R. for the specific equipment selected?
    _____ __ __ __ __ 0.76 or 0.90 ?



    1. Winter: 70'F
    2. Summer: ______ 'F

    3. Elevation: ______ Feet

    4. Check ALL details of BUILDING THERMAL ENVELOPE
    __ Re-Read and address Post # 18

    5, Manual J Calc

    6. Perform Manual S considering the Indoor Temperature & Elevation
    _ [ Concurrent Deratings ]

    7. Perform Manual D

    --- All duct lengths and fittings need to be included.
    Designer Dan __ It's Not Rocket Science, But It is SCIENCE with Some Art. _ _ KEEP IT SIMPLE & SINCERE ___ __ www.mysimplifiedhvac.com ___ __ Define the Building Envelope & Perform a Detailed Load Calc: It's ALL About Windows & Make-up Air Requirements. Know Your Equipment Capabilities

Page 2 of 2 FirstFirst 12

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •