  1. #1
    Join Date
    Sep 2020
    Posts
    8
    Post Likes

    Commercial WeilMclain

    I have a brand new WeilMclain 4 section cast iron 240,000MBH and the pilot will light but the gas valve chatters when it rectifies flame then shuts off. This is a commercial boiler in a residential setting. I have confirmed my gas pressures are within range. Is this a bad valve out of the box? Poor burner ground? Or control issue? Any feedback is appreciated. Thanks!

  2. #2
    Join Date
    Jan 2008
    Location
    New Jersey
    Posts
    201
    Post Likes
    What type of gas valve/valves, burner and ignition system does this system utilize? If you a model number that will help.

    Sent from my ASUS_P00J using Tapatalk

  3. #3
    Join Date
    Sep 2020
    Posts
    8
    Post Likes
    Thread Starter
    Quote Originally Posted by chander View Post
    What type of gas valve/valves, burner and ignition system does this system utilize? If you a model number that will help.

    Sent from my ASUS_P00J using Tapatalk
    This is a natural gas, 1 in and 1 out 7000DERHC-S7C spark ignition

  4. #4
    Join Date
    Sep 2020
    Posts
    8
    Post Likes
    Thread Starter
    Keep in mind, this boiler ran fine with no issue for 2 weeks before the chatter started

  5. #5
    Join Date
    Sep 2020
    Posts
    8
    Post Likes
    Thread Starter
    Intermittent pilot

  6. #6
    Join Date
    Sep 2020
    Posts
    8
    Post Likes
    Thread Starter
    Gas pressure 7.3 in and 3.2 out

  7. #7
    Join Date
    Jan 2008
    Location
    New Jersey
    Posts
    201
    Post Likes
    Do you have a solid 24v at the valve when it opens?

    Sent from my ASUS_P00J using Tapatalk

  8. #8
    Join Date
    Nov 2004
    Location
    up in the hizzy
    Posts
    3,665
    Post Likes
    Call a service technician, boiler have the potential to go kaboom, dont play with it if you dont know what you are doing!
    There is not better place for the working men than the union! 100% UA the only HVAC union!

  9. Likes icy78, CHILLERSVCMAN liked this post.
  10. #9
    Join Date
    Mar 2015
    Location
    Medford, N.Y.
    Posts
    7,300
    Post Likes
    What is factory spec for the manifold gas press? 3.2? 3.5? Was the gas press verified during startup and run?

  11. #10
    Join Date
    Sep 2020
    Posts
    8
    Post Likes
    Thread Starter
    Quote Originally Posted by valdelocc View Post
    Call a service technician, boiler have the potential to go kaboom, dont play with it if you dont know what you are doing!
    I am the service tech as well as the installer. I found that the zone board was replaced by another company the previous year and when all zones called I would lose 24v intermittently to the valve due to an undersized transformer. Thanks to everyone for their input and guidance