Results 1 to 16 of 16
Thread: TXV Stuck Open?
    Aug 2008
    Hibbing, MN
    TXV Stuck Open?
    Just replaced compressor in a Federal open deli case. R404a, receiver, TXV, sight glass, no pump down, no other valves. Pretty basic system. Evacuated to 150 microns, weigh in charge. Start up. All sound great, but liquid line is hot to the touch and suction line and compressor dome are very cold. No gauges hooked up at this point.
    I figured, it just started up, it’ll settle in. Started putting my gear back in the van, and when I cam back in, the unit was off on high pressure cut out. Condenser is perfectly clean, and fan is running the right direction and moving good air. Gauge up and find high side pressure around 380. Sub cooling is 35 and superheat is almost zero.
    Remove about 1 or 2 lbs of refrigerant and get high side down to 310 (120F) and superheat goes up to 30.
    On a system with a TXV and receiver, adding or removing a pound or two of refrigerant should not have this much effect. Right? I’m thinking that I might have a TXV that is stuck open. In 35 years, I don’t think I’ve ever seen a valve fail open. I see them fail closed quite often.
    Any thoughts?
    If God didn't want us to eat animals... He wouldn't have made them out of MEAT.
    Oct 2011
    Harrisburg, NC
    Quote Originally Posted by GenesisRefrig View Post
    Any thoughts?
    Someone pull the dime trick on the power element?
    It’s a known “emergency repair” for a bad power element to get the valve to open, take power element off, put a dime in it and reinstall until next business day. Sometimes get forgotten.
    I can't fix it if it won't stay broke..
    Austin, Texas
    Forget the dime thing that will not work. Replace the valve and be done with it.
    Sent from my SM-T387AA using Tapatalk
    Oct 2011
    Harrisburg, NC
    Quote Originally Posted by rickl View Post
    I was suggesting that it’s possible it WAS done possibly because that particular person didn’t have a power element on his truck at the time and forgot about it, this causing the valve to be wide open and noticeable now that it has a new compressor.
    Austin, Texas
    OK cool. Your right on that. I never done the dime thing. We carried the sporlan tex kits on the truck.
    Aug 2008
    Hibbing, MN
    I’m planning on going back, and replacing the valve, then putting a full charge in on Monday. Right now we’ve got a partial charge and bubbles in the sight glass. If I find a dime, I’ll post a pic.
    Austin, Texas
    I wish somebody would try the dime thing. I don’t believe it has ever been done. Wouldn’t the power element leak where it is threaded to the valve. Or flood the system. I don’t think a good power element diaphragm moves the thickness of a dime!
    Just don’t believe it will work and never found a dime,
    Southold, NY
    Done it twice. Gave time to get a replacement head.
    Oct 2011
    Harrisburg, NC
    I’ve done it once, and a friend of mine was running a call recently, sent me a pic of one he found that no one knew how long it had been in there.
    Aug 2008
    Hibbing, MN
    Thinking about the dime trick, now I’m even more skeptical about changing the TXV. Because with a dime, the system runs semi-normally. Can anyone think of another reason I’d have high head, And low (no) superheat.
    Dec 2014
    I tried the dime thing once but it definitely was flooding back and I couldn't leave it like that. So I used shim material and tried a couple THINnesses lol and it worked out well for overnight.
    Sent from my SM-G950U using Tapatalk
    I did the dime trick once ... 10 oclock at night with cooler full of food
    The dime wasnt letting enough juice in , so I used a thicker washer
    It definitely doesnt work right , but it works good enough for the night
    I assume the juice is moving so fast through the system it doesnt have enough time to reject heat ....
  14. #14
    Aug 2013
    Omaha
    Did this federal case have a tecumseh condensing unit and compressor?
    I dont like those tecumseh condensing units because the run their condensers real small so they'll fit in areas but that causes high head pressure.
    I've had a federal case like this and the Expansion valve liked to floodback. Had a receiver too and it ran real high head in a 73F ambient.
    Still kinda fighting it
    Sent from my SM-G975U using Tapatalk
  15. #15
    Aug 2008
    Hibbing, MN
    Quote Originally Posted by UmmScott View Post
    You’ve been to my job site! That’s it exactly.
  16. #16
    Jul 2000
    Guayaquil, EC
    What is the Tecumseh condensing unit's model number?
    Go to Tecumseh Boxload page, select Condensing Unit Data Sheets and scroll down the dropdown menu to find the model. It'll give you what the condensing temperature should be.
    https://boxload.tecumseh.com/