    Sizing Backup Heat Commercial

    I have sized an Allied 5 Ton HP ML14XP1-060-233 (Customer has 3 phase) If I am putting in bas backup does anyone spec it for the entire load or less? 80 or 90 ? Not sure if the 90 would make sense given it is for backup and but we should spec it for the entire space if the heat pump will not be working at all. (Region 3)

  2. #2
    Join Date
    Jan 2004
    Location
    PA
    Posts
    79,291
    Post Likes
    Gas back up makes it dual fuel. Since the heat pump can't run while the gas heat is, the gas heat must be sized for the full load.
    Contractor locator map

    How-to-apply-for-Professional

    How many times must one fix something before it is fixed?

  3. #3
    Join Date
    Jan 2015
    Location
    Bellevue, Washington, United States
    Posts
    1,677
    Post Likes
    Quote Originally Posted by beenthere View Post
    Gas back up makes it dual fuel. Since the heat pump can't run while the gas heat is, the gas heat must be sized for the full load.
    X2