    Coil restriction?

    Pretty sure I’ve got some restrictions in distributer tubes. Wonder if the oil additive trane used a few years ago would work? It’s a York d4ce060 a25a
    76* ambient. 194/18 psig. 19*sc 61* sh. When I looked thru the top and saw the compressor I was expecting a evap that was a complete ball of ice not the minimal frost that I found. 1* temp drop on drier so doubt its my issue. Unless it dropped its desiccant bbs. Those pressures and temperatures are after letting thaw out.
    Attached Images Attached Images   

  2. #2
    Join Date
    Nov 2011
    Location
    CO
    Posts
    17,439
    Post Likes
    What's your model number?

    did you weigh the charge?

  3. #3
    Join Date
    Jun 2019
    Location
    Central Illinois
    Posts
    120
    Post Likes
    Thread Starter
    Model number in opening post. Weigh charge ? No that’s what I walked up and found. The suction line was 5.4 * Yes I put a thermometer on it. So it was flooding back bad. But as you can see I only had minor frost on the evap. Top and bottom. Only took about 15 minutes to thaw out. Thought maybe more dirt on evap than it looks but could look right thru it with filter door open letting sunlight in.

  4. #4
    Join Date
    May 2003
    Location
    Charleston SC
    Posts
    172
    Post Likes
    You don't have floodback with 61* superheat.
    Coolairman

  5. Likes BBeerme liked this post.
  6. #5
    Join Date
    Sep 2019
    Location
    New York
    Posts
    203
    Post Likes
    I would add a LB or so of gas and see what happens, see if SH continues to go up... or if it goes down, see if low side goes up, see if SC goes up .. See if high side goes up..

    Before anything I would make sure both coils spic and span..and not just by eyeballing it.

  7. #6
    Join Date
    Mar 2015
    Location
    Medford, N.Y.
    Posts
    10,203
    Post Likes
    Quote Originally Posted by coolairman View Post
    You don't have floodback with 61* superheat.
    Coolairman
    What refrigerant?

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •