  1. #1
    Join Date
    Sep 2020
    Posts
    2
    Post Likes

    Confused New system not dehumidifying

    New system installed 7/10/20 (specs below). One of the main concerns I had prior to purchase was indoor humidity and was told this system would work be great.

    Thus far that hasn't been our experience. The installer has been back twice to investigate. They agree the humidity should never reach the levels it is (+70% when set at 56%) and that it and the temperature should remain relatively static given the variable speed. During the 2nd trip the installer felt the answer was to use the Ecobbe thermostat's "overcool" feature where it allows the system to run up to 3 degrees lower than the desired temperature IF the system hasn't reached the desired humidity level. Well, we're just cold now. :-(

    My assumption is either:
    - The dehumidification isn't working and/or working as well as it should
    - The system isn't running at a low enough fan speed to allow the system to run longer to dehumidify but not freeze us out

    Here's what's been installed:
    - Carrier® Performance™ - 3.5 Ton 16 SEER Air Conditioning Condenser
    - Model: 24apb642a003
    - Product: 24apb642a0030010
    - 24 = AC / Product Series
    - A = RES AC / Product Family
    - P = Performance Series / Tier
    - B = Puron / Major Series
    - 6 = 16 SEER / SEER
    - 42 = 3.5 Ton / Cooling Capacity
    - A = Standard / Grille Variations
    - 0 = Not Defined / Open
    - 0 = Not Defined / Open
    - 3 = 208/230-1 / Voltage
    - Carrier 3.5 Ton Evaporator N Coil Cased Horizontal Painted 21" Width (Aluminum)
    - Model CNPHP4321ALAEAAA
    - C = Coil Product
    - N = N Coil Type
    - P = Puron® Refrigerant TXV Refrigerant Type
    - H = Horizontal Coil Configuration
    - P = Painted Cabinet Finish
    - 43 = 3.5 Ton Unit Capacity
    - 21 = 21" in (533 mm) Cabinet Width
    - A = 1st Revision Level
    - L = Aluminum Tubing Design
    - A = Basic Variations
    - Carrier Carrier® Performance™ - 80% AFUE 90000 Btuh 4-Way Multipoise Induced-Combustion Gas Furnace, 2-Stage, Variable-Speed
    - Model: 58TP0A090V211120

    Name:  humidity.png
Views: 1210
Size:  178.2 KB
    Here's a graph showing humidity quickly decreasing when the system is running...and then quickly increasing when it's not:
    - Blue rectangles: when the system is running
    - White line: indoor humidity level
    - Green: outdoor humidity

    Name:  temp.png
Views: 1172
Size:  162.7 KB
    Here's a graph showing the system consistently "overcooling" past the desired temperature:
    - Blue rectangles: when the system is running
    - Blue line: desired (cool) temp
    - White line: indoor temperature
    - Green: outdoor temperature

  2. #2
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    13,331
    Post Likes
    Quote Originally Posted by cjs226 View Post
    New system installed 7/10/20 (specs below). One of the main concerns I had prior to purchase was indoor humidity and was told this system would work be great.

    Thus far that hasn't been our experience. The installer has been back twice to investigate. They agree the humidity should never reach the levels it is (+70% when set at 56%) and that it and the temperature should remain relatively static given the variable speed.

    During the 2nd trip the installer felt the answer was to
    use the Ecobbe thermostat's "overcool" feature
    where it allows the system to run up to 3 degrees lower than the desired temperature
    IF the system hasn't reached the desired humidity level.

    Well, we're just cold now. :-(

    My assumption is either:
    - The dehumidification isn't working and/or working as well as it should
    - The system isn't running at a low enough fan speed to allow the system to run longer to dehumidify but not freeze us out

    - Carrier Carrier® Performance™ - 80% AFUE 90000 Btuh 4-Way Multipoise Induced-Combustion Gas Furnace, 2-Stage, Variable-Speed
    - Model: 58TP0A090V211120

    Name:  humidity.png
Views: 1210
Size:  178.2 KB
    Here's a graph showing humidity quickly decreasing when the system is running...and then quickly increasing when it's not:
    - Blue rectangles: when the system is running
    - White line: indoor humidity level
    - Green: outdoor humidity

    Set the thermostat to 76'F

    + Report back in 3 days

    What is the SUPPLY AIR Temperature?
    Designer Dan __ It's Not Rocket Science, But It is SCIENCE with Some Art. _ _ KEEP IT SIMPLE & SINCERE ___ __ www.mysimplifiedhvac.com ___ __ Define the Building Envelope & Perform a Detailed Load Calc: It's ALL About Windows & Make-up Air Requirements. Know Your Equipment Capabilities

  3. #3
    Join Date
    Jun 2003
    Location
    Madison, WI/Cape Coral, FL
    Posts
    12,042
    Post Likes
    Fan, auto or on?

    Need Supply temp/%RH is critical in commenting on the a/c's function!!!s

    During the design outdoor load conditions, like 92^F, 50%RH, a 70^F dew point, cooling load, a properly functioning and setup a/c should be able to maintain 75^F, <50%RH, a 55^F dew point.

    During the hottest part of the day, you are in a part load condition at 88^F, 40%RH, a 60^F dew point outside. Even at this part load condition, the a/c should run enough to maintain 50% without over-cooling.

    During the evenings, the a/c will not run enough maintain 50%RH even with over-cooling.

    Here is how to start, Get the a/c checked for function. The amount of refrigerant and function what the tech checks. Next adjust the air flow through the cooling coil to improve the moisture removed by the cooling coil. We need cold air supply with <50^F DEW point at the supply of the a/c for a minimum of 50% of the time, 40-40 mins. per hour to remove +2 lbs.per ton per hour of cooling. This is critical. The supply should be like 55^F, 80%RH, a 50^F dew point.

    Do not expect any dehumidification from your a/c during low/no sensible cooling load conditions. you will get dehumidification only during significant sensible cooling loads. With your current setup, you need over-drying during high sensible cooling to carry you through the evenings and rainy days be comfortable.

    Many living in green grass regions are adding a small whole house dehumidifier to remove moisture during evenings/rainy days and high outdoor dew point plus the moisture from the occupants.

    You must get your a/c setup ideally before considering adding a dehumidifier. Adding a dehumidifier to a defective a/c is not a solution. The a/c must be able do its part during peak sensible/latent cooling loads.

    Your thoughts. My comments are intended to help your a/c tech guide lines on setting up the a/c function properly. Supply the temp/%RH at the supply for more feed back from me.

    Regards Teddy Bear
    Bear Rules: Keep our home <50% RH summer, controls mites/mold and very comfortable.
    Provide 60-100 cfm of fresh air when occupied to purge indoor pollutants and keep window dry during cold weather. T-stat setup/setback +8 hrs. saves energy
    Use +Merv 10 air filter. -Don't forget the "Golden Rule"

  4. #4
    Join Date
    Sep 2020
    Posts
    2
    Post Likes
    Thread Starter
    Quote Originally Posted by teddy bear View Post
    Need Supply temp/%RH is critical in commenting on the a/c's function!!!s
    Where should I measure supply temp and relative humidity? While I don't know much HVAC, I am a home automation geek and can setup a sensor or 3 to monitor such things.

  5. #5
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,745
    Post Likes
    RH gets measured at the return.
    Delta T closet supply and return

    With a set point near the outside air temp how much run time do you expect?

  6. #6
    Join Date
    Jun 2003
    Location
    Madison, WI/Cape Coral, FL
    Posts
    12,042
    Post Likes
    Quote Originally Posted by cjs226 View Post
    Where should I measure supply temp and relative humidity? While I don't know much HVAC, I am a home automation geek and can setup a sensor or 3 to monitor such things.
    Measure temp/%RH at the closest supply to the a/c. Would be nice to measure temp/%RH any return grill.

    Regards Teddy Bear
    Bear Rules: Keep our home <50% RH summer, controls mites/mold and very comfortable.
    Provide 60-100 cfm of fresh air when occupied to purge indoor pollutants and keep window dry during cold weather. T-stat setup/setback +8 hrs. saves energy
    Use +Merv 10 air filter. -Don't forget the "Golden Rule"

  7. #7
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    13,331
    Post Likes
    Quote Originally Posted by pecmsg View Post
    RH gets measured at the return.
    Delta T closest supply and return

    With a set point near the outside air temp how much run time do you expect?
    Supply Air AT the air handler Outlet.

    Relative Humidity would likely be 84% to 93%
    Designer Dan __ It's Not Rocket Science, But It is SCIENCE with Some Art. _ _ KEEP IT SIMPLE & SINCERE ___ __ www.mysimplifiedhvac.com ___ __ Define the Building Envelope & Perform a Detailed Load Calc: It's ALL About Windows & Make-up Air Requirements. Know Your Equipment Capabilities

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Tags for this Thread

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •