    Less than 24v effect?

    Good evening guys, my question is, how sensitive are the Johnson controllers at a >24v output from a xformer? My last call today, was a server room no cool, it was a york unit, first thing I noticed was the xformer was wired for 230, but was really 209. Could the >24v have any effect on the control voltage side? I rewired it for 208, and my controls guy was like everything seems to be doing what it should

    Sent from my SM-A516U using Tapatalk

  2. #2
    Join Date
    Jan 2010
    Location
    Sea to Sky
    Posts
    4,153
    Post Likes
    If you meant less than 24 volts...the yes I have seen control systems go haywire with low voltage.

    Sent from my SM-G965W using Tapatalk

  3. Likes Matt Woodbridge liked this post.
  4. #3
    Join Date
    Jul 2020
    Location
    San Diego, CA
    Posts
    205
    Post Likes
    Thread Starter
    Quote Originally Posted by BALloyd View Post
    If you meant less than 24 volts...the yes I have seen control systems go haywire with low voltage.

    Sent from my SM-G965W using Tapatalk
    Yes that is what I meant, but the control voltage was at 22.6. But thank you for your knowledge.

    Sent from my SM-A516U using Tapatalk

  5. #4
    Join Date
    Apr 2014
    Posts
    616
    Post Likes
    Quote Originally Posted by Matt Woodbridge View Post
    Yes that is what I meant, but the control voltage was at 22.6. But thank you for your knowledge.

    Sent from my SM-A516U using Tapatalk
    18 volts or less and you are screwed. 22.5 shouldn’t be an issue, but 24-27 is better

  6. Likes Matt Woodbridge liked this post.
  7. #5
    Join Date
    Jul 2020
    Location
    San Diego, CA
    Posts
    205
    Post Likes
    Thread Starter
    Quote Originally Posted by JCIman View Post
    18 volts or less and you are screwed. 22.5 shouldn’t be an issue, but 24-27 is better
    Thank you my man, im going back in the a.m. to take another look at it

    Sent from my SM-A516U using Tapatalk

  8. #6
    Join Date
    May 2009
    Location
    SC
    Posts
    2,439
    Post Likes
    Just check out the cut sheet for the device in question. Most give a valid range like 18-30vAC.

  9. Likes Matt Woodbridge liked this post.
  10. #7
    Join Date
    Feb 2005
    Location
    Edmonton, AB Canada
    Posts
    840
    Post Likes
    Good day Matt,

    Just doing an off the cuff calculation, the primary miswiring would have reduced the output voltage by about 10% ... which is very close to what you measured (22.6VAC). Also on a side note... a 24VAC output transformer is the output voltage at the maximum rate current of the transformer. So... if you use a larger VA rated transformer than what you actually need then output voltage will be larger than 24VAC. As a consequence if you are measuring 24VAC on a 24VAC rated transformer then you are at the transformer's maximum power output... and so the resulting output voltage can droop if your load increases for some reason. I usually spec at least 50% what I need to be on the safe side and if the transformer size is too big, etc then maybe I will allow only a 25% increase.

    Cheers,

    Sam

  11. Likes Matt Woodbridge liked this post.
  12. #8
    Join Date
    Sep 2013
    Posts
    403
    Post Likes
    Had a Honeywell spyder today that we couldn’t download. Long wire run and 5-6 vavs on the circuit. Two vavs within 10’ would accept the download this one wouldn’t. Swapped controllers etc. Ended up being voltage drop had 24.5 at xfmer and 22.4 at vav. Temporary xfmer and then it would download.


    Sent from my iPhone using Tapatalk

  13. Likes Matt Woodbridge liked this post.
  14. #9
    Join Date
    Jul 2020
    Location
    San Diego, CA
    Posts
    205
    Post Likes
    Thread Starter
    Quote Originally Posted by bigguy158 View Post
    Had a Honeywell spyder today that we couldn’t download. Long wire run and 5-6 vavs on the circuit. Two vavs within 10’ would accept the download this one wouldn’t. Swapped controllers etc. Ended up being voltage drop had 24.5 at xfmer and 22.4 at vav. Temporary xfmer and then it would download.


    Sent from my iPhone using Tapatalk
    I'm glad you made it work bro, thats awesome

    Sent from my SM-A516U using Tapatalk

  15. #10
    Join Date
    Apr 2020
    Location
    Garner NC
    Posts
    1,552
    Post Likes
    I see it all the time on RTUs, I swap the high voltage wire from the 230 to the 208v terminal wiring(some older transformers showed 200v terminals and it works the same) to get 24-26v ...I see plenty of problems of anything below 22v when all the contactors and relays activate . In some cases it gets below 20v and contactors / relays chatter then fail..

    Don’t feel bad, some units have been misdiagnosed For over 10 years because other parts swappers don’t notice the obvious of checking for the correct voltage output first..

  16. Likes stanbyyourword, Matt Woodbridge liked this post.
  17. #11
    Join Date
    May 2013
    Location
    Luxembourg
    Posts
    216
    Post Likes
    In good old Europe electronic devices usually work correctly, if the supply voltage is between 90% and 110% of the nominal value.

  18. Likes Matt Woodbridge liked this post.
  19. #12
    Join Date
    Jul 2002
    Posts
    1,327
    Post Likes
    I've seen low voltage problems too. I sometimes wish transformers put out 25 volts. Kind of like a car system is called 12 volts but the engine really puts out 14.

  20. Likes Matt Woodbridge liked this post.
  21. #13
    Join Date
    Jul 2020
    Location
    San Diego, CA
    Posts
    205
    Post Likes
    Thread Starter
    Quote Originally Posted by incontrol View Post
    I've seen low voltage problems too. I sometimes wish transformers put out 25 volts. Kind of like a car system is called 12 volts but the engine really puts out 14.
    Yes I usually like to see about 26, but it is what it is

    Sent from my SM-A516U using Tapatalk

  22. #14
    Join Date
    Apr 2020
    Location
    Garner NC
    Posts
    1,552
    Post Likes
    It depends on your incoming high voltage...I have seen 490v put out 27v where 460 has 24.5v ....215v put out 26v where 208v has 24v . You get the idea...but the voltage also drops under use and how many components are energized at the time...
    Some buildings can have 245v incoming with nothing running but drop to 232v with everything running...

    You could have a weak transformer or bad coils on the relays/contactors/ corroded connections giving a higher resistance pulling the voltage lower..I’m fine seeing 23v , I recheck everything at 22v or lower with everything energized ...

  23. Likes Matt Woodbridge liked this post.
  24. #15
    Join Date
    Jul 2020
    Location
    San Diego, CA
    Posts
    205
    Post Likes
    Thread Starter
    Quote Originally Posted by Unlimited1 View Post
    It depends on your incoming high voltage...I have seen 490v put out 27v where 460 has 24.5v ....215v put out 26v where 208v has 24v . You get the idea...but the voltage also drops under use and how many components are energized at the time...
    Some buildings can have 245v incoming with nothing running but drop to 232v with everything running...

    You could have a weak transformer or bad coils on the relays/contactors/ corroded connections giving a higher resistance pulling the voltage lower..I’m fine seeing 23v , I recheck everything at 22v or lower with everything energized ...
    Yes for sure, 22 is usually good? My old boss would always say look for 25+

    Sent from my SM-A516U using Tapatalk

  25. #16
    Join Date
    Apr 2020
    Location
    Garner NC
    Posts
    1,552
    Post Likes
    Quote Originally Posted by Matt Woodbridge View Post
    Yes for sure, 22 is usually good? My old boss would always say look for 25+

    Sent from my SM-A516U using Tapatalk
    My meter is high end and very accurate . A lot of cheaper meters don’t give the same results..as mentioned I look for problems at 22v and below. Incoming high voltage can have corroded connections.. I always use a good known Multi tap test transformer That I got from an older unit that was replaced and recheck...However if you have 22v and everything is working good, it is what it is...