    Recently replaced screw compressor for York YCAV chiller, worried about timing on checking rotation? Can anyone inform me on how long I have to check rotation? System is VFD drive and can be shut down at system switch but takes a few seconds.

  2. #2
    Join Date
    Dec 2014
    Location
    New Mexico
    Posts
    2,028
    Post Likes
    If you matched wire for wire at the compressor terminals should not be a problem. If unsure match the wiring diagram for wire numbers.
    You have a minute or two to shut it down.


    Sent from my iPhone using Tapatalk

  3. Likes dieseldude liked this post.
  4. #3
    Join Date
    Jul 2015
    Location
    Bracebridge On Canada
    Posts
    13
    Post Likes
    Thread Starter
    Yes system compressor wires were matched and identified upon replacement. If not correct, net oil pressure should not increase ?

  5. #4
    Join Date
    Dec 2014
    Location
    New Mexico
    Posts
    2,028
    Post Likes
    Yes correct


    Sent from my iPhone using Tapatalk

  6. Likes Lab26 liked this post.
  7. #5
    Join Date
    Apr 2020
    Location
    va
    Posts
    10,300
    Post Likes
    Use a phase sequence meter on the drive output wiring.

    Will only run a few seconds-2-3 minutes without lubrication before severe damage. Discharge check location also has a bearing on time.

  8. Likes Lab26 liked this post.
  9. #6
    Join Date
    Apr 2016
    Location
    Maryland
    Posts
    341
    Post Likes
    I always pump some oil into the suction prior to start to prevent a " DRY START " never lost one on start up
    Last edited by CHILLERSVCMAN; 09-25-2020 at 03:18 PM. Reason: more info

  10. #7
    Join Date
    Dec 2014
    Location
    New Mexico
    Posts
    2,028
    Post Likes
    You could close the oil line isolation valve and pump oil into the oil filter cover plate. A quart should do it fill the filter cavity and push down the oil passages into the bearings. A quart could be pulled out after the system settles down. Who knows could be pulling back a lot of oil with the new compressor.


    Sent from my iPhone using Tapatalk

+ Reply to Thread

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •