    Recently replaced screw compressor for York YCAV chiller, worried about timing on checking rotation? Can anyone inform me on how long I have to check rotation? System is VFD drive and can be shut down at system switch but takes a few seconds.

  2. #2
    Join Date
    Dec 2014
    Location
    New Mexico
    Posts
    1,067
    Post Likes
    If you matched wire for wire at the compressor terminals should not be a problem. If unsure match the wiring diagram for wire numbers.
    You have a minute or two to shut it down.


    Sent from my iPhone using Tapatalk

  3. Likes dieseldude liked this post.
  4. #3
    Join Date
    Jul 2015
    Location
    Bracebridge On Canada
    Posts
    2
    Post Likes
    Thread Starter
    Yes system compressor wires were matched and identified upon replacement. If not correct, net oil pressure should not increase ?

  5. #4
    Join Date
    Dec 2014
    Location
    New Mexico
    Posts
    1,067
    Post Likes
    Yes correct


    Sent from my iPhone using Tapatalk

  6. Likes Lab26 liked this post.
  7. #5
    Join Date
    Apr 2020
    Location
    va
    Posts
    641
    Post Likes
    Use a phase sequence meter on the drive output wiring.

    Will only run a few seconds-2-3 minutes without lubrication before severe damage. Discharge check location also has a bearing on time.

  8. Likes Lab26 liked this post.
  9. #6
    Join Date
    Apr 2016
    Location
    Maryland
    Posts
    338
    Post Likes
    I always pump some oil into the suction prior to start to prevent a " DRY START " never lost one on start up
    Last edited by CHILLERSVCMAN; 09-25-2020 at 03:18 PM. Reason: more info

  10. #7
    Join Date
    Dec 2014
    Location
    New Mexico
    Posts
    1,067
    Post Likes
    You could close the oil line isolation valve and pump oil into the oil filter cover plate. A quart should do it fill the filter cavity and push down the oil passages into the bearings. A quart could be pulled out after the system settles down. Who knows could be pulling back a lot of oil with the new compressor.