    Quote Originally Posted by pecmsg View Post
    CCH is still cheap insurance?
    Good point! So is a pump down imo.
    “Happiness can be found, even in the darkest of times, if one only remembers to turn on the light.”
    "Ha! Memory is RAM!"

  2. #42
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,726
    Post Likes
    Quote Originally Posted by Bombboy90 View Post
    I was taught in school years ago one major benefit to walk in cooler pump down was to prevent refrigerant leakage during the off cycle if the evap has a leak from say, tomato or onion acid eating at the coil. I know most coils are coated but leaks find a way...

    Among the other points listed, I never really thought of it to prevent liquid slugging. Makes sense really, and also bbeerme makes a point, solenoid is off no liquid in the compressor, no reason for a CCH thus saving $
    CCH is still cheap insurance?

    The CCH is only good during the off cycle. While running the motor windings keep the oil warm.

  3. #43
    Join Date
    Apr 2003
    Location
    Maple Grove, MN
    Posts
    5,135
    Post Likes
    Quote Originally Posted by pecmsg View Post
    CCH is still cheap insurance?

    The CCH is only good during the off cycle. While running the motor windings keep the oil warm.
    Yeah, when its -20°F that CCH is a good thing to have

  4. #44
    Join Date
    Jan 2019
    Location
    EU
    Posts
    76
    Post Likes
    Quote Originally Posted by TechmanTerry View Post
    Why is that?
    Installers don't have the knowledge, or perhaps they don't want to bother with pump-down set up.

  5. #45
    Join Date
    Feb 2006
    Location
    Austin, Texas
    Posts
    543
    Post Likes
    So all yÂ’all did yo homework and found out a properly operating system without a pump down will not cause a flooded start, no slugging. In fact the tev will close on the off cycle. The tev will not feed in the off cycle! All the liquid refrigerant in the Evap will evaporate. As to migration in the cold parts of the world the crankcase heater takes care of that..
    And as to those 100 foot suction run at -20 ambient refer to the basis refrigerant textbooks and the pt chart how the vapor condenses to liquid. Tev are the most mis-understood component of the refrigeration system!
    FYI in the 45 years I have been working, the only time I found a busted crank was due to a defecting tev flooding. We always breakdown those semi hermetic for a Look see and a few hermetic compressors as well, just for fun.

  6. #46
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,726
    Post Likes
    Quote Originally Posted by rickl View Post
    So all yÂ’all did yo homework and found out a properly operating system without a pump down will not cause a flooded start, no slugging. In fact the tev will close on the off cycle. The tev will not feed in the off cycle! All the liquid refrigerant in the Evap will evaporate. As to migration in the cold parts of the world the crankcase heater takes care of that..
    And as to those 100 foot suction run at -20 ambient refer to the basis refrigerant textbooks and the pt chart how the vapor condenses to liquid. Tev are the most mis-understood component of the refrigeration system!
    FYI in the 45 years I have been working, the only time I found a busted crank was due to a defecting tev flooding. We always breakdown those semi hermetic for a Look see and a few hermetic compressors as well, just for fun.
    If that’s how you feel fine!

  7. Likes WT70 liked this post.
  8. #47
    Join Date
    Oct 2011
    Location
    Harrisburg, NC
    Posts
    2,034
    Post Likes
    Quote Originally Posted by rickl View Post
    FYI in the 45 years I have been working, the only time I found a busted crank was due to a defecting tev flooding. We always breakdown those semi hermetic for a Look see and a few hermetic compressors as well, just for fun.
    We do the same a lot of times, when we have time from all the service calls to tear it down.

    One busted crank in 45 years? Go buy yourself a lottery ticket.


    Sent from my iPhone using Tapatalk

    I can't fix it if it won't stay broke..

  9. #48
    Join Date
    Aug 2008
    Location
    Hibbing, MN
    Posts
    1,301
    Post Likes
    Quote Originally Posted by BBeerme View Post
    Typo ?
    Bad grammar. I meant that migration of refrigerant is not possible if you’re pumped down.
    If God didn't want us to eat animals... He wouldn't have made them out of MEAT.

  10. #49
    Join Date
    Oct 2011
    Location
    Harrisburg, NC
    Posts
    2,034
    Post Likes
    Directly from a Sporlan rep....





    Sent from my iPhone using Tapatalk

    I can't fix it if it won't stay broke..

  11. #50
    Join Date
    May 2014
    Location
    Bay Area California
    Posts
    43,452
    Post Likes
    Very rare to see a busted crank. I've probably never seen one.

    Most likely scenario is the clearance at either end of the connecting rod, piston/rings, or valves.
    I do a triple evac with nitro to remove non condensables.

  12. #51
    Join Date
    Oct 2011
    Location
    Harrisburg, NC
    Posts
    2,034
    Post Likes
    Quote Originally Posted by BBeerme View Post
    Very rare to see a busted crank. I've probably never seen one.

    Most likely scenario is the clearance at either end of the connecting rod, piston/rings, or valves.
    Oil slugging on racks will tear a compressor up.

    Wait. Ha. Pistons and rods, I guess I’ve only had a crank bust when it hit the rod that came off when oil went thru the heads.


    Sent from my iPhone using Tapatalk

    I can't fix it if it won't stay broke..

  13. #52
    Join Date
    May 2014
    Location
    Bay Area California
    Posts
    43,452
    Post Likes
    Yeah, cranks do get severely damaged, but bust? Like in two pieces? VERY rare.
    I do a triple evac with nitro to remove non condensables.

  14. #53
    Join Date
    Mar 2013
    Location
    Treasure coast, FL
    Posts
    11,466
    Post Likes
    Quote Originally Posted by BadDaddy420 View Post
    Directly from a Sporlan rep....





    Sent from my iPhone using Tapatalk
    Are you confusing evaporator pressure with inlet (liquid line) pressure??

    Sent from my Moto Z (2) using Tapatalk

  15. #54
    Join Date
    May 2014
    Location
    Bay Area California
    Posts
    43,452
    Post Likes
    Have to get Remanworld to weigh in on this one, he's the authority here. Not sure I got his username correct.


    Quote Originally Posted by BBeerme View Post
    Yeah, cranks do get severely damaged, but bust? Like in two pieces? VERY rare.
    I do a triple evac with nitro to remove non condensables.

  16. #55
    Join Date
    Oct 2011
    Location
    Harrisburg, NC
    Posts
    2,034
    Post Likes
    Quote Originally Posted by shellkamp View Post
    Are you confusing evaporator pressure with inlet (liquid line) pressure??

    Sent from my Moto Z (2) using Tapatalk
    Liquid pressure goes down in off cycle, suction would rise.


    Sent from my iPhone using Tapatalk

    I can't fix it if it won't stay broke..

  17. #56
    Join Date
    Mar 2013
    Location
    Treasure coast, FL
    Posts
    11,466
    Post Likes
    Quote Originally Posted by BadDaddy420 View Post
    Liquid pressure goes down in off cycle, suction would rise.


    Sent from my iPhone using Tapatalk
    What are you trying to say???

    To be clear, all I said was that on non-balanced port valves, the inlet (liquid pressure) acts as an opening force on the valve. The difference in pressure between the liquid line and the outlet of the TXV will aggravate this condition.



    Sent from my Moto Z (2) using Tapatalk

  18. #57
    Join Date
    Oct 2011
    Location
    Harrisburg, NC
    Posts
    2,034
    Post Likes
    Quote Originally Posted by shellkamp View Post
    What are you trying to say???

    To be clear, all I said was that on non-balanced port valves, the inlet (liquid pressure) acts as an opening force on the valve. The difference in pressure between the liquid line and the outlet of the TXV will aggravate this condition.



    Sent from my Moto Z (2) using Tapatalk
    Rickl stated “valve closes in off cycle”, which a lot said this doesn’t happen. So I wanted a true answer myself.

    I honestly thought the power element would overcome the spring, but it doesn’t.

    According to Sporlan Rep, the valve closes. I asked him because what better way to get the proper answer than ask the people that make the valves.

    The liquid pressure actually does push down on the metering needle, during operation it helps keep movement of the TEV smooth.

    Internal EQ valves uses the pressure on the outlet of the TEV for the pressure under the power element through an internal port. External uses the pressure from the suction line on the outlet of the evaporator.

    In off cycle, suction pressure rises, pushes against the power element, along with the spring to overcome power element force, closing the valve.

    That’s not to say it doesn’t fully close until pressures equalize, and worn out valves may bleed by, but a TEV closes on off cycle.


    Sent from my iPhone using Tapatalk

    I can't fix it if it won't stay broke..

  19. #58
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,726
    Post Likes
    Correct but that can take several minutes while the valve is still beating refrigerant into the evaporator. That refrigerant condenses into a liquid
    Depending on the operating conditions it could be a little or a lot

  20. #59
    Join Date
    Oct 2011
    Location
    Harrisburg, NC
    Posts
    2,034
    Post Likes
    Quote Originally Posted by pecmsg View Post
    Correct but that can take several minutes while the valve is still beating refrigerant into the evaporator. That refrigerant condenses into a liquid
    Depending on the operating conditions it could be a little or a lot
    Exactly. But it does close. The time it takes to close throws most of us as we see the pressures equalize.

    I’m still a proponent of pump down. But on smaller systems and cap tube systems how often do we see that except for True equipment I think.


    Sent from my iPhone using Tapatalk

    I can't fix it if it won't stay broke..

+ Reply to Thread
Page 3 of 3 FirstFirst 123

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •