    Question Condensation Drainage Problem

    Hi.

    My home has 2 HVAC's with coils from Allstyle Coil Company, model FMSP. One one of the units, the bottom pan keeps filling up, stopping the unit. Obviously, it is not draining properly. The draining pipe on both units are connected to the same drain PVC pipe. I've attached some photos.

    Any suggestions on correcting the problem greatly appreciated.

    Thanks
    Attached Images Attached Images

  2. #2
    Join Date
    Apr 2020
    Location
    va
    Posts
    488
    Post Likes
    The lower pan & switch is a back-up in case the coil pan or top drain plugs...

  3. #3
    Join Date
    Aug 2020
    Posts
    2
    Post Likes
    Thread Starter
    Well, yes. I understand that. The top drain, as you called it, is obviously not draining properly. Hence it’s likely backed up. I guess I need to take apart the pvc assembly to find the clog. I was just wondering if there is an easier way.

    Thanks for your suggestion.

  4. #4
    Join Date
    Jan 2008
    Location
    New Jersey
    Posts
    182
    Post Likes
    If you remove the coil access cover, you can try to use a shop vac to suck the clog out of the trap and pipe.

    Sent from my ASUS_P00J using Tapatalk