    Using RTU as Make-up air

    One of my clients just moved into a building and the WH keeps going out

    I light pilot , crank her up , look at the flames and they are blowing all over the place

    Put my hand near the top of WH and air is blowing out of the flu like crazy

    Go open the back door , flames are perfect , no more air coming out of flu

    The hood only has Natural Draft

    Im thinking of slowing down the Hood Fan speed , and open the fresh air vent on RTU

    But ... how much can I open the fresh air without upsetting the AC performance ?

  2. #2
    Join Date
    Feb 2016
    Location
    Louisburg Kansas
    Posts
    5,824
    Post Likes
    You have to know the heating and cooling capacity of the RTU to know how much OA it can handle. The other way is to experiment by opening the OA damper enough to solve your problem and monitor the performance.
    No man can be both ignorant and free.
    Thomas Jefferson

  3. #3
    Join Date
    Apr 2003
    Location
    Maple Grove, MN
    Posts
    5,136
    Post Likes
    It doesn't matter how much it affects the operation of the air conditioning. Leaving the space in a negative with that water heater could kill somebody. How big is the exhaust hood? Are we talking about a restaurant? Do they not have a make-up air unit?
    If at First You Don't Succeed, Skydiving Is Not for You.

  4. Likes jbhenergy, dieseldude liked this post.
  5. #4
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    14,048
    Post Likes
    Thread Starter
    Its an old ass mom n pop place , natural draft make up hood is like 8ft ...grease type

  6. #5
    Join Date
    Feb 2016
    Location
    Louisburg Kansas
    Posts
    5,824
    Post Likes
    Can you add a supply fan to the hood? That's the best solution if workable.
    No man can be both ignorant and free.
    Thomas Jefferson

  7. #6
    Join Date
    Nov 2011
    Location
    CO
    Posts
    17,438
    Post Likes
    Or just add outside airnfeom somewhere....cut a vent in the closet door, leave some doors open, etc. But it needs fixed.

  8. #7
    Join Date
    Apr 2010
    Location
    California
    Posts
    717
    Post Likes
    "]You should NEVER Try To Balance or Adjust, a Buildings Airflow System, using a Hot Water Heaters Pilot Light Flame as a Go-NoGo Gauge. That Pilot should function in a plus or minus range of Static Pressure Conditions for safety sake.


    LZ....

  9. #8
    Join Date
    Feb 2016
    Location
    Louisburg Kansas
    Posts
    5,824
    Post Likes
    The make-up air should be close enough to the range that adding a supply fan should ease the negative pressure without impacting comfort conditions very much if any. The supply airflow should be slightly less than the exhaust. It should then be possible to adjust the RTU OA to provide a slightly positive building without over loading the RTU.
    No man can be both ignorant and free.
    Thomas Jefferson

  10. #9
    Join Date
    Apr 2010
    Location
    California
    Posts
    717
    Post Likes
    WHOOPS, I See Now OP was Talking about High Fire, as apposed to Pilot. My Bad, But the Same Message Applies.!


    LZ...

  11. Likes WAYNE3298 liked this post.
  12. #10
    Join Date
    Feb 2016
    Location
    Louisburg Kansas
    Posts
    5,824
    Post Likes
    Agree Izenglish it depends on how negative the building is. It sounds like the negative is excessive but a hood supply fan will lower the negative enough to allow the RTU to make the building positive which it should be.
    No man can be both ignorant and free.
    Thomas Jefferson

  13. #11
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    14,048
    Post Likes
    Thread Starter
    Found a crawlspace type vent 8x16 blocked off , and its actually in the same room as the WH

    Pulled the cover off and the air suddenly came blowing in like a fan was on !

    Looked at the flames and they are much better , but there is STILL enough air coming through the Flu to blow out the pilot once in while during times its satisfied

    Im gonna head there now and try slowing down the Hood fan , and give the RTU about 20 percent OA

    After that he's gotta call someone in who knows what the hell he's doing lol

    I know of a place that shut down their make up system ... and then opened all the RTU to 100 percent OA

    They have to change air filters weekly because they are near a desert in California , and the AC units suction pressure is high like you would imagine ... how crazy is that ...

  14. #12
    Join Date
    Apr 2003
    Location
    Maple Grove, MN
    Posts
    5,136
    Post Likes
    Quote Originally Posted by Snapperhead View Post
    Found a crawlspace type vent 8x16 blocked off , and its actually in the same room as the WH

    Pulled the cover off and the air suddenly came blowing in like a fan was on !

    Looked at the flames and they are much better , but there is STILL enough air coming through the Flu to blow out the pilot once in while during times its satisfied

    Im gonna head there now and try slowing down the Hood fan , and give the RTU about 20 percent OA

    After that he's gotta call someone in who knows what the hell he's doing lol

    I know of a place that shut down their make up system ... and then opened all the RTU to 100 percent OA

    They have to change air filters weekly because they are near a desert in California , and the AC units suction pressure is high like you would imagine ... how crazy is that ...
    What's a "natural draft make up hood"? I'm glad you fixed that combustion air vent. Also look for a dirty screen on the intake of whatever they're using for make up air. I also agree that opening the economizer a little bit is a good idea as well. Sounds like you're on the right track.
    If at First You Don't Succeed, Skydiving Is Not for You.

  15. #13
    Join Date
    Feb 2016
    Location
    Louisburg Kansas
    Posts
    5,824
    Post Likes
    A natural draft hood has a makeup air source but no fan on it.
    No man can be both ignorant and free.
    Thomas Jefferson

  16. #14
    Join Date
    Mar 2015
    Location
    Medford, N.Y.
    Posts
    10,203
    Post Likes
    The regular RTU being converted into a makeup air unit? I think that you are limited to the CFM that the Economizer will/would allow under the normal 15-20% fresh air open position.

  17. #15
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    14,048
    Post Likes
    Thread Starter
    Yeah I went there this morning and saw the OA vent is very small , like 8x8 , and it was set at 10 percent on this 5 ton unit

    Even if I open it completely it would be pissing in the wind

    The other system is a split unit.

    I slowed down the hood 2 turns on the motor sheave , had to put 1 inch smaller belt , and its like I didn't even touch it

    When you flip on the switch for hood , the filters go " clang" up against the rack

  18. #16
    Join Date
    May 2019
    Posts
    397
    Post Likes
    We had a cobbled up restaurant mechanical room with a whole house exhaust fan in it because on WIF and WIC cond units in the room.

    Water heater pilots out every day.

    Put in a Cyclone power vented commercial water heater with combustion air piped in from outside, solved the 2 problems of pilots and adequate supply of hot water.

    Amazingly the AO Smith tank is still going strong since 2005.

  19. #17
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    14,048
    Post Likes
    Thread Starter
    Yeah I was entertaining that idea yesterday , or even go electric

    I think its 75 gallons

    He's gonna cry when he finds out the cost of those in power vent ...

  20. #18
    Join Date
    May 2004
    Location
    Salt Lake City/Tooele
    Posts
    9,679
    Post Likes
    Our engineers use RTU units as MUA units all the time. Most are 100% OA, they oversize the cooling capacity and restrict the RA inlet, with a RAWAL APR control installed, they work just surprisingly well. Probably thirty of forty RTU units of all manufactures, some thirty years old are pulling 100% OA are out where I work and they all are doing fine.

    Example, last month, I installed a new base model Daikin 5ton cool only unit, restrictive OA inlet plate installed in place of return air duct, about 2 to 2.5 tons of air aloud based on opening, brazed in a Rawal kit, adjusted charge. Had to revisit the unit and adjust the hot gas a tinch, but even on the record 105° day we had last week, that unit had no issues maintaining a perfect SAT to the building.

  21. Likes ksefan liked this post.
  22. #19
    Join Date
    Sep 2002
    Location
    Virginia
    Posts
    14,048
    Post Likes
    Thread Starter
    I cant imagine being on the Humid ass East Coast that would fly very well ....

  23. #20
    Join Date
    May 2004
    Location
    Salt Lake City/Tooele
    Posts
    9,679
    Post Likes
    Quote Originally Posted by Snapperhead View Post
    I cant imagine being on the Humid ass East Coast that would fly very well ....
    That is why I rely on the engineers.

+ Reply to Thread
Page 1 of 2 12 LastLast

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •