    Confused Heat Pump Output Calculation - Help!!!

    Hi,
    Does anyone here know how to calculate heat pump system ouput? Let's say I want to swap heat exchanger to more effective one, or refrigerant to less harmful one. How do I calculate overall performance of the system based on components, before actually swapping and taking physical measurements? I understand, that performance varies by temperature difference, but let's assume it's constant, controlled environment.

    If anyone can help, I would be glad

  2. #2
    Join Date
    Apr 2020
    Location
    va
    Posts
    208
    Post Likes
    Check with mfg data easiest.

    Fairly easy to calculate capacity in heat mode, more difficult in cooling mode (must have wet bulb and heat content tables).

  3. #3
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    28,824
    Post Likes
    Less harmful refrigerant?
    CO2
    LP
    Ammonia

  4. Likes paulchri liked this post.
  5. #4
    Join Date
    Mar 2016
    Location
    Dayton Oh
    Posts
    2,674
    Post Likes
    Entering air db exiting air db. Convert both to ethapy. Use constant to multiple.

    Papers out their on. Done it before very easy if you have the right tools.


    Sent from my iPhone using Tapatalk

  6. #5
    Join Date
    Jul 2013
    Location
    Richmond, VA
    Posts
    5,255
    Post Likes
    You need the return wet bulb and dry bulb temperatures, supply wet bulb and dry bulb temperatures, and actual CFM (not an assumption). Find the enthalpy of each the return and supply using a psychrometric chart or calculator, then use the following formula:

    (CFM * 4.5) / (Return enthalpy - Supply enthalpy) = BTU/hr
    Everything Im going to say today are my conclusions and my opinions, my opinions are based on my education, my training, my experience. Different people have different experiences, so they have different opinions and I make no claim that my opinion has its origin in the mind greatness. - Paul Harrell

  7. #6
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    10,311
    Post Likes
    How do I calculate overall performance of the system based on components,


    NOT-TOO-SIMPLE
    ________ REFRIGERATION CYCLE

    https://www.sciencedirect.com/scienc...81006474000024

    https://www.sciencedirect.com/scienc...81006474000255
    Designer Dan
    It's Not Rocket Science, But It is SCIENCE with "Some Art". ___ ___ K EEP I T S IMPLE & S INCERE

    Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities

  8. #7
    Join Date
    Aug 2020
    Posts
    2
    Post Likes
    Thread Starter
    Thanks for information

    Also, is it possible to get higher COP than compressor COP rating? Or the compressor COP is the most you can get from the system?