    New HVAC system

    Hey Sirs!
    I decided to select the TRANE HVAC 16 SEER System to replace my existing 08/05/2005 Manufactured 10 SEER Carrier system. My 2006 SFH is built in Northern Virginia, finished with two levels (3,560 Sq.ft) and I plan on adding a finished basement (800 Sq.ft) in future. Is it worth the money to move from 2.0 ton to 2.5 ton for Attic and 3.0 ton to 3.5 ton for Basement? Will the current Air Ducts handle air flow with an increment of 1/2 ton? Did any one claim the home insurance to cover the old HVAC replacement costs? Any advantage with the TRANE over Carrier brand. Appreciate valuable suggestions! Please comment on any mismatch Trane system pair.

    Attic: Old Carrier System
    Air Handler: FA4BNF024010 - Serial # 3105A73519 (2 TON)
    Heat Pump : 38YCC024340 Serial # 4205E30813 (2 TON)
    Heater: 10KW

    Basement: Old Carrier System
    Furnace: 58MCA080---1--16 Serial # 3205A06152
    Furnace Coil: CD5AXA036017 Serial # 2805X89729
    Air Conditioner: Model 38CKC024 Serial # Faded


    Attic: New Trane System:

    Option 1: 2.0 Ton
    1. Heat Pump: 4TWR6024H1000A
    2. Air Handler: TEM6A0B24H21+TDR
    3. Heater: BAYHTR1510BRKC
    4. Slim Fit Filter Rack: BAYSF1185AA
    5. Thermostat: TCONT824AS52DBXL824

    Option 2 - 2.5 Ton:
    1. Heat Pump: 4TWR6030H1000A
    2. Air Handler: TEM6A0B30H21+TDR
    3. Heater: BAYHTR1510BRKC
    4. Slim Fit Filter Rack: BAYSF1185AA


    Basement: New Trane System:

    Option 1: 3.0 Ton:
    1. Furnace: S9X1B080U4PSB
    2. AC: Condenser: 4TTR6036J1000A
    3. Evaporator Coil: 4PXCCU42BS3HAA
    4. Thermostat: TCONT824AS52DB XL824

    Option 2: 3.5 Ton:
    1. Furnace: S9X1B080U4PSB
    2. AC: Condenser: 4TTX6042J1000A
    3. Evaporator Coil: 4PXCBU42BS3HAA
    4. Thermostat: TCONT824AS52DB XL824

  2. #2
    Join Date
    May 2018
    Location
    Elizabethtown, PA
    Posts
    169
    Post Likes
    Bigger is better doesn't work with HVAC equipment. When buying shoes, do you buy a pair a couple sizes larger because bigger is better? No, you buy the size that fits you. You need the the equipment that is sized correctly for your home.

  3. #3
    Join Date
    Apr 2020
    Location
    Garner NC
    Posts
    1,017
    Post Likes
    you would need to see how much humidity is in the air/foundation and foundation walls in your basement..and make sure it is water tight.you should already have a geothermal temp. the basement will not need much except dehumidification with excess humidity if its not water tight. the cooler return air from the basement could possibly assist you cooling load upstairs...some basements could have 12' ceilings and others are 6'...you home load calculations will tell you what you need...without it you are just guessing at this point...

    do it the right way...have the load calculation done..then return with that info..

  4. #4
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    10,320
    Post Likes
    2006 Single Family Home in Northern VA

    Clarification needed
    1. Basement: 800 Sq Feet ____ Heat Only + Dehumidifier
    2. __ First Floor: 2,100 Sq Feet _ 3.0 Ton
    3. Second Floor: 1,460 Sq Feet _ 2.0 Ton


    Total Window Area < 460 Sq Feet
    Windows: Double Pane & Tinted


    OR ___________
    Designer Dan
    It's Not Rocket Science, But It is SCIENCE with "Some Art". ___ ___ K EEP I T S IMPLE & S INCERE

    Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities

  5. #5
    Join Date
    Jul 2020
    Posts
    4
    Post Likes
    Thread Starter
    Hey Dan SW FL,

    Appreciate your reply regarding my HVAC replacement!

    My current home has a total finished Area of 3,560 Sq. Ft.

    First Floor: 1597.5 Sq. ft

    Second Floor: 1963 Sq. ft

    Two Car Garage: 525 Sq. ft

    Unfinished Basement Area: 1597.5 Sq. ft: Eight Ceiling Steel Registers with 10-Inch x 4-Inch Duct Openings.

    Your experienced inputs will greatly help me to finalize the Trane HVAC Unit.

    I would really appreciate if you could comment on my prospective Trane Models Capacity as I mentioned in the post.

    Thx
    NOVA Resident, VA

  6. #6
    Join Date
    Jul 2020
    Posts
    4
    Post Likes
    Thread Starter
    Thanks for your reply.

  7. #7
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    10,320
    Post Likes
    Quote Originally Posted by padmakar_kodali View Post
    Hey Dan SW FL,

    Appreciate your reply regarding my HVAC replacement!

    My current home has a total
    Finished Area of 3,560 Sq. Ft.
    ----- First Level: 1,600 Sq. Feet
    ---- Main Floor: 1,960 Sq. Feet

    Unfinished Basement Area:
    1597.5 Sq. ft: Eight Ceiling Steel Registers with 10-Inch x 4-Inch Duct Openings.

    Your experienced inputs will greatly help me to finalize the Trane HVAC Unit.

    I would really appreciate if you could comment on my
    prospective Trane Models Capacity as I mentioned in the post.

    Thx
    NOVA Resident, VA
    NOVA is not a city that I can find in Virginia.

    ZIP _ _ _ _ _


    First level is a basement which implies it is fully underground IMO. To be confirmed.

    A fully underground level probably does not have any windows. To be confirmed.

    An Air Conditioned/ Heated basement with eight diffusers ( registers) and a separate A/C system is not " UNfinished. "
    .. i.e. __ Block wall with R-13 insulation? or _ _ ?

    Choice between Hybrid System(s), Heat Pump and/or Furnace
    depends on the locale / climate, natural gas and electric rates along with the
    ACCA Manual J & S calculations.

    Furnace may be selected for main level
    and not selected for the basement.
    Heat strips may be selected if electric rate is < $0.11 / kw-hour
    and natural gas is > $1.00 / therm.

    Number of windows on Main Level
    or total square feet of glass
    North
    South
    East
    West

    ___ Double Pane __ ?
    ___ Triple Pane __ ?
    ___ Tinted ______ ? SHGC _0. _ _ ?

    Assistance:
    _______ https://www.mysimplifiedhvac.com
    Designer Dan
    It's Not Rocket Science, But It is SCIENCE with "Some Art". ___ ___ K EEP I T S IMPLE & S INCERE

    Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities

  8. #8
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    10,320
    Post Likes
    PARTIAL Operating Cost
    __ Comparison

    Main Level 1,960 Sq Feet
    ___ Example: .. ~ 36,000 BTU/HR
    __________ someWhere in VA

    $0.108 / kw-hour __________ $ 865 heating _ 4,340 Heating Degree Days
    $1.16 / N. Gas Therm ______ $1,326
    Attached Images Attached Images   
    Designer Dan
    It's Not Rocket Science, But It is SCIENCE with "Some Art". ___ ___ K EEP I T S IMPLE & S INCERE

    Define the Building Envelope and Perform a Detailed Load Calc: It's ALL About Windows and Make-up Air Requirements. Know Your Equipment Capabilities