Thread: 80% Humidity in brand new home, is my unit undersized?

  1. #1
    Join Date
    Jul 2020
    Posts
    2
    Post Likes

    80% Humidity in brand new home, is my unit undersized?

    Hi there! I have a brand new two level 2960 sq ft home with a split system and a conditioned crawl space. I live in the Raleigh, NC area. Each day around 3 PM, my home begins heating up pretty badly. I understand that this can be normal, and temperature wise we are maxing out at around 75 degrees according to the thermostat, but I have taken the temp of my kids rooms and they were at 80 degrees. I understand some of that can be normal, but our humidity in this home is really high. In the morning, our temperature can hit 69 degrees, but the humidity is at 60%. Yesterday in my upstairs area, at 8PM, the thermostat said 74 degrees and the humidity was 80%. This made the upstairs extremely humid and unbearable. The weather yesterday outside was around 95 degrees with around 50-55% humidity.

    I am concerned because the humidity is causing some extra nail pops and drywall issues, plus it is terrible for sleep! I understand this level of air quality is also really bad for health, and great for mold and fungus.

    As I said, we have a 2960 sq ft home with a conditioned crawl space. We have a Lennox 3-ton 14 SEER system, model 14ACXS036-230A**. This whole system seems like it just cannot keep up with this house. The temperature difference between the returns and the vents is 8-10 degrees. We have the wrightsoft load calculation summary, but many of the numbers are 0, or set to N/A. It also is incorrect about there being a fireplace, and there is no calculations for the ducts or the crawlspace.

    What I would really like to know is, does any of this sound normal? Can this much humidity in the home be a normal function of a properly sized or functioning system? Can a 3-ton system actually cool a 2960 sq ft home properly?

    Should I get another load calculation done for the home?

    I really appreciate an help you all can provide, I am just not sure what is normal or not!

  2. #2
    Join Date
    Jan 2012
    Location
    Missouri, USA
    Posts
    3,963
    Post Likes
    Wow, that sounds pretty bad for new construction. I would call the installers back out for a check up. Maybe they installed it during the winter and never came back to setup the system properly for summer.

  3. Likes dieseldude, ELS liked this post.
  4. #3
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    13,329
    Post Likes
    Quote Originally Posted by ddyraw View Post

    Hi there! I have a brand new two level 2960 sq ft home with a split system and a conditioned crawl space.

    I live in the Raleigh, NC area.

    Each day around 3 PM, my home begins heating up pretty badly. I understand that this can be normal, and temperature wise we are maxing out at around 75 degrees according to the thermostat, but I have taken the temp of my kids rooms and they were at 80 degrees. I understand some of that can be normal, but our humidity in this home is really high.

    In the morning, our temperature can hit 69 degrees, but the humidity is at 60%.
    Yesterday in my upstairs area,
    at 8PM, the thermostat said 74 degrees and the humidity was 80%.

    This made the upstairs extremely humid and unbearable. The weather yesterday outside was around 95 degrees with around 50-55% humidity.

    I am concerned because the humidity is causing some extra nail pops and drywall issues, plus it is terrible for sleep! I understand this level of air quality is also really bad for health, and great for mold and fungus.

    As I said, we have a 2960 sq ft home with a conditioned crawl space. We have a Lennox 3-ton 14 SEER system, model 14ACXS036-230A**. This whole system seems like it just cannot keep up with this house.

    The temperature difference between the
    returns and the vents is 8-10 degrees.


    We have the Wrightsoft load calculation summary, but many of the numbers are 0, or set to N/A.
    It also is incorrect about there being a fireplace, and there is no calculations for the ducts or the crawlspace.

    What I would really like to know is, does any of this sound normal?
    Can this much humidity in the home be a normal function of a properly sized or functioning system?
    Can a 3-ton system actually cool a 2960 sq ft home properly?

    Should I get another load calculation done for the home?

    I really appreciate an help you all can provide, I am just not sure what is normal or not!
    Differential temperature (DT) 8'F to 10'F from the Air Handler outlet to the first diffuser [ vent ]
    indicates a Failed A/C system.
    _____________ DT should be ~ 21'F !!

    Crawl space being conditioned is Rather ODD.
    _____ Sounds like you may be conditioning the OutDoors.
    Designer Dan __ It's Not Rocket Science, But It is SCIENCE with Some Art. _ _ KEEP IT SIMPLE & SINCERE ___ __ www.mysimplifiedhvac.com ___ __ Define the Building Envelope & Perform a Detailed Load Calc: It's ALL About Windows & Make-up Air Requirements. Know Your Equipment Capabilities

  5. #4
    Join Date
    Jul 2020
    Posts
    2
    Post Likes
    Thread Starter
    Thanks for the quick responses Dan and ksefan! This definitely seems concerning!

    I was told that the crawl space received conditioned air to reduce humidity in the crawl space. Kind of ironic considering there is massive humidity upstairs, LOL.

    So if I put a temperature gauge at a Air return, then measure at the first vent, that is a valid test? I was told it was not by the company, even though during my inspection, the inspector noted that the DT was 10'F. Hopefully I can post pictures soon, so I can share the load calcs!

    Is there anytime a functioning a/c system should allow 80% humidity?

  6. #5
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    13,329
    Post Likes
    Quote Originally Posted by ddyraw View Post
    Thanks for the quick responses Dan and ksefan! This definitely seems concerning!

    I was told that the crawl space received conditioned air to reduce humidity in the crawl space. Kind of ironic considering there is massive humidity upstairs, LOL.

    So if I put a temperature gauge at a Air return, then measure at the first vent, that is a valid test?

    I was told it was not by the company, even though during my inspection, the inspector noted that the DT was 10'F. Hopefully I can post pictures soon, so I can share the load calcs!

    Is there anytime a functioning a/c system should allow 80% humidity?
    NO. I presume you don't have five windows open.
    Send me your Manual J calculation [ PDF ].

    MY Gmail address: racingdan11

    Assistance: Https://www.mysimplifiedhvac.com

    You are in need of a different HVAC/ Mechanical contractor.!
    I will let you know.
    Designer Dan __ It's Not Rocket Science, But It is SCIENCE with Some Art. _ _ KEEP IT SIMPLE & SINCERE ___ __ www.mysimplifiedhvac.com ___ __ Define the Building Envelope & Perform a Detailed Load Calc: It's ALL About Windows & Make-up Air Requirements. Know Your Equipment Capabilities

  7. #6
    Join Date
    Aug 2002
    Location
    Southold, NY
    Posts
    47,730
    Post Likes
    Quote Originally Posted by ddyraw View Post
    Thanks for the quick responses Dan and ksefan! This definitely seems concerning!

    I was told that the crawl space received conditioned air to reduce humidity in the crawl space. Kind of ironic considering there is massive humidity upstairs, LOL.

    So if I put a temperature gauge at a Air return, then measure at the first vent, that is a valid test? I was told it was not by the company, even though during my inspection, the inspector noted that the DT was 10'F. Hopefully I can post pictures soon, so I can share the load calcs!

    Is there anytime a functioning a/c system should allow 80% humidity?
    What inspection?

  8. #7
    Join Date
    Jan 2012
    Location
    Broomall, PA
    Posts
    4,743
    Post Likes
    3 tons seems light for 3000sq ft in NC
    If I do a job in 30 minutes it's because I spent 30 years learning how to do that in 30 minutes. You owe me for the years, not the minutes.

    Helpful Calcs, tips, tricks on my YouTube channel: https://www.youtube.com/channel/UCgm...TUTAdKmqRiTDEg

  9. Likes Mr Bill, stumpdigger liked this post.
  10. #8
    Join Date
    Dec 2002
    Location
    Houston,Texas
    Posts
    23,010
    Post Likes
    Quote Originally Posted by STEVEusaPA View Post
    3 tons seems light for 3000sq ft in NC
    You think? It certainly would be in Houston.


    Sent from my iPhone using Tapatalk
    __________________________________________________ _______________________
    “Experience is a hard teacher because she gives the test first, the lesson afterwards" ~ Vernon Law

    "It's what you learn after you know it all that counts." ~ John Wooden

    "When the teachers become unteachable we're all in trouble" ~ Mr. Bill

    "Remember "Pro" is only a name, it's not always a mindset determined to do everything correctly" ~ Mr. Bill




  11. Likes stumpdigger liked this post.
  12. #9
    Join Date
    Aug 2009
    Location
    Beatrice, NE
    Posts
    22,112
    Post Likes
    You have several problems some related others not. Let's start with the home, you say it was new, how new? When a house is built it soaks up moisture. Any rain that comes falls on open wood, that wood gets wet and sometimes does not have a chance to dry before the sheet rock goes on. Then you have the sheet rock, the mud that is used to finish the seams puts off a lot of moisture. One other part of the construction to consider is the insulation. If the insulation gets wet or is wet it takes a long time for that to dry as it is covered by the sheeting on the outside and sheet rock on the inside. You say the crawl space is conditioned but is it sealed? To seal a crawl space the dirt floor has to be covered with a heavy plastic sheet with all the seams sealed as well as where it meets the walls, posts, etc. or it has to be concrete with all openings sealed. The walls must be insulated as well as the rim joist and there should be no openings to the outside.

    If you just started up the A/C for the first summer it is fitting all the moisture in the house from being built as well as all the moisture that you are putting in the house by living there. With the humidity you are talking your system may be overwhelmed right now and will just take a while to get the moisture out.

    Then there is ventilation. Most codes require so much fresh air into a structure. Your may be bringing in fresh air directly from outside with no control. 2900 Sq Ft of space will need quite a bit of fresh air to achieve the required air exchanges. Add to this the air required as make up for exhaust fans, clothes drier, water heater venting, range exhaust, etc and if there is no control you may be over ventilating the house.

    The 10 degree delta T is not accurate if measured at the registers. A better test is at the inlet and outlet of the equipment. We will see what Dan comes up with but I would doubt that 3 T is over sized at just under 1000 Sq FT/T but it would depend on how tight/well insulated it is.

  13. #10
    Join Date
    Mar 2016
    Location
    Dayton Oh
    Posts
    6,632
    Post Likes
    Quote Originally Posted by Mr Bill View Post
    You think? It certainly would be in Houston.


    Sent from my iPhone using Tapatalk
    Would be just right new construction my area.


    Sent from my iPhone using Tapatalk

  14. #11
    Join Date
    Dec 2002
    Location
    Houston,Texas
    Posts
    23,010
    Post Likes
    Quote Originally Posted by jbhenergy View Post
    Would be just right new construction my area.


    Sent from my iPhone using Tapatalk
    I understand, the temperature and humidity levels in different towns all across the country are a little different, and some have a huge contrast in these differences. This is why some like me here in the Deep South, freak out when we hear 2-tons on 2500 sq.ft. Heck we would have a 5- ton on 3000 sq.ft. here.


    Sent from my iPhone using Tapatalk
    __________________________________________________ _______________________
    “Experience is a hard teacher because she gives the test first, the lesson afterwards" ~ Vernon Law

    "It's what you learn after you know it all that counts." ~ John Wooden

    "When the teachers become unteachable we're all in trouble" ~ Mr. Bill

    "Remember "Pro" is only a name, it's not always a mindset determined to do everything correctly" ~ Mr. Bill




  15. #12
    Join Date
    Nov 2004
    Location
    SW FL
    Posts
    13,329
    Post Likes
    Quote Originally Posted by STEVEusaPA View Post
    3 tons seems light for 3000 sq ft in NC
    Raleigh NC is a predominantly heating climate.
    HDD: 3,208 Design Temp. 24.2'F 99%
    Heating Degree Days

    CDD: 1,685 Design Temp. 92.5'F / 75.0'F 1%
    --- --- ---
    1,000 SQ ft / ton is a possibility for some NEW Construction
    > R-20 Walls
    R-48 Ceiling
    SHGC < 0.23. U-factor < 0.3
    A.C.H. Natural < 0.2


    What construction quality that is actually pertinent to this residence remains a mystery.
    Designer Dan __ It's Not Rocket Science, But It is SCIENCE with Some Art. _ _ KEEP IT SIMPLE & SINCERE ___ __ www.mysimplifiedhvac.com ___ __ Define the Building Envelope & Perform a Detailed Load Calc: It's ALL About Windows & Make-up Air Requirements. Know Your Equipment Capabilities

  16. Likes ELS liked this post.
  17. #13
    Join Date
    Jun 2003
    Location
    Madison, WI/Cape Coral, FL
    Posts
    12,042
    Post Likes
    Get the a/c contractor back in. If sized right, the a/c will cool the space to the desired temp and %rH.
    The a/c is adjusted to the correct air flow which will remove enough moisture that at 75^F, 50%RH will be the result. If unable to get to down to 75^F, you need a bigger a/c. You fix the a/c or make it bigger. Now it is big enough to get down to 75^F, but the %RH is +50%RH. You slow the a/c air to increase the latent cooling or moisture removal. You a/c contractor know how to do this. If not, lawyer knows how to sue the a/c contractor.
    You will need some dehumidification to maintain <50%RH during evenings and during rainy days.
    Sound easy enough.
    Keep us posted.
    Regards Teddy Bear
    Bear Rules: Keep our home <50% RH summer, controls mites/mold and very comfortable.
    Provide 60-100 cfm of fresh air when occupied to purge indoor pollutants and keep window dry during cold weather. T-stat setup/setback +8 hrs. saves energy
    Use +Merv 10 air filter. -Don't forget the "Golden Rule"

  18. Likes ELS liked this post.
  19. #14
    Join Date
    Jun 2020
    Location
    BAIRD, TX
    Posts
    1,475
    Post Likes
    Quote Originally Posted by STEVEusaPA View Post
    3 tons seems light for 3000sq ft in NC
    I have a two ton in my house, 866 sq'. My neighbor has a 3000 sq' house with 2 condensing units, at least 7 tons in Chicago land.
    " The more I learn the more I realize how much I don't know"

  20. #15
    Join Date
    Aug 2009
    Location
    Beatrice, NE
    Posts
    22,112
    Post Likes
    First we need to know how is the 3000 Sq Ft figured. I have just under 2000 Sg Ft in my house on the main floor but then I have a full basement which gives a total of nearly 4000 Sq Ft but it is considered a 2000 Sq Ft house. I have a 2 T 2 Stg Hp in my house and it will keep the house at set point 10 degrees over design. Design is 75/93 and the load came out just over 18k. So a well built house in NC should be fairly close at 1000 ft/T

Quick Reply Quick Reply

Register Now

Please enter the name by which you would like to log-in and be known on this site.

Please enter a password for your user account. Note that passwords are case-sensitive.

Please enter a valid email address for yourself.

Log-in

Tags for this Thread

Posting Permissions

  • You may post new threads
  • You may post replies
  • You may not post attachments
  • You may not edit your posts
  •